Default New wall oven on 30 amp

Homeowner put new 40 amp double oven in and was wired to a #10 and 30 amp breaker. Never used both ovens at the same time so never had a problem. Told him he needed #8 and 40 amp breaker. Homeowner had electrician come out and electrician said since kitchen was upstairs, to difficult to run new wire and he should just put in a 35 amp breaker and all would be good. Common sense tells me no, but with electrician saying this, thought I would throw it out to the sparkys for clarification.
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/26/10, 1:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: New wall oven on 30 amp

240.4 Protection of Conductors.

(D) Small Conductors.
Unless specifically permitted in 240.4(E) through (G), the overcurrent protection shall not exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG, and 30 amperes for 10 AWG copper; or 15 amperes for 12 AWG and 25 amperes for 10 AWG aluminum and copperclad aluminum after any correction factors for ambient temperature and number of conductors have been applied.

But I am not a "Sparky."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 3/26/10, 1:41 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New wall oven on 30 amp

Whether it is too difficult or not the proper size circuit using #8 CU should be run. There is no allowance for "too difficult" in the Code. Also, the instructions provided need to be followed.

I agree with Jeff.
Reply With Quote
  #4  
Old 3/26/10, 1:50 PM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: New wall oven on 30 amp

Thanks guys. I knew but with a licensed electrician doing something wrong and being liable for his work threw me into questioning if I was missing something. This was my 15th mock, still learning. Thanks again.
Reply With Quote
  #5  
Old 3/26/10, 9:34 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: New wall oven on 30 amp

What does the paper work or the label on the stove require? If it says 40 amp, tell him to argue with the manufactuer.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #6  
Old 3/26/10, 10:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New wall oven on 30 amp

Without the rating of the oven it's hard to say for sure if this is an NEC violation or not. But with the information given it sounds as if it violates this code section:

Quote:
210.19(A)(3) Household Ranges and Cooking Appliances. Branch-circuit conductors supplying household ranges, wall-mounted ovens, counter-mounted cooking units, and other household cooking appliances shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served. For ranges of 8¾ kW or more rating, the minimum branch-circuit rating shall be 40 amperes.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wall Oven Recall jevans Interior Inspections 0 12/20/08 3:39 PM
Moisture Management mcyr Exterior Inspections 15 9/8/08 12:11 PM
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural Inspections 75 7/21/08 5:25 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 10:48 AM


All times are GMT -4. The time now is 7:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts