Homeowner put new 40 amp double oven in and was wired to a #10 and 30 amp breaker. Never used both ovens at the same time so never had a problem. Told him he needed #8 and 40 amp breaker. Homeowner had electrician come out and electrician said since kitchen was upstairs, to difficult to run new wire and he should just put in a 35 amp breaker and all would be good. Common sense tells me no, but with electrician saying this, thought I would throw it out to the sparkys for clarification.
|
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
240.4 Protection of Conductors. (D) Small Conductors. Unless specifically permitted in 240.4(E) through (G), the overcurrent protection shall not exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG, and 30 amperes for 10 AWG copper; or 15 amperes for 12 AWG and 25 amperes for 10 AWG aluminum and copperclad aluminum after any correction factors for ambient temperature and number of conductors have been applied. But I am not a "Sparky." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Whether it is too difficult or not the proper size circuit using #8 CU should be run. There is no allowance for "too difficult" in the Code. Also, the instructions provided need to be followed.
I agree with Jeff. |
|
#4
|
|||
|
|||
|
Thanks guys. I knew but with a licensed electrician doing something wrong and being liable for his work threw me into questioning if I was missing something. This was my 15th mock, still learning. Thanks again.
|
|
#5
|
||||
|
||||
|
What does the paper work or the label on the stove require? If it says 40 amp, tell him to argue with the manufactuer.
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Without the rating of the oven it's hard to say for sure if this is an NEC violation or not. But with the information given it sounds as if it violates this code section:
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Wall Oven Recall | jevans | Interior Inspections | 0 | 12/20/08 3:39 PM |
| Moisture Management | mcyr | Exterior Inspections | 15 | 9/8/08 12:11 PM |
| VIDEO--Bowed Basement Wall, Cracks etc | john bubber | Structural Inspections | 75 | 7/21/08 5:25 PM |
| 980 Questions/Answers to the NHIE....Free! | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 50 | 4/20/08 1:26 AM |
| Newbie here with a slab "standards" question | Robert Young, #3 | Structural Inspections | 17 | 4/10/07 10:48 AM |