#1
|
|||
|
|||
|
Hi,
When inspecting a service panel with fuses for the main disconnect, how do you proceed? Can you assume the fuses are appropriate after noting the ratings on the meter/panel? Is it normal to shut off the power to verify the proper fuses? Obviously, assuming is no good, but... Just setting out and this one has been nagging at me. Thanks, Tim |
| Find an InterNACHI certified Kentucky Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Tim take one of the NACHI Electrical courses.
Meanwhile , never shutoff the power to Inspect. Check the conductor sizes,labeling,ground,neutral,and bond. What are the conductors made out of? Aluminum? Copper? None the less you may need to study up some more. For now just note main amp,take a picture or series and upload here for help. |
|
#3
|
||||
|
||||
|
Here is something I got off one of the Members.
Apology for not noting whom. for inspecting an electrical panel Follow InterNACHI Standards of Practice Wear personal safety protection, including glasses and gloves Check adequate workspace Panel must be readily accessible Use proper inspection tools, including magnet handle, insulated screwdriver, and flashlight Check adequate illumination at workspace Measure height of main disconnect Inspect cabinet front cover Check for incorrect type of screws or missing screws at the cabinet front cover Inspect panelboard All disconnects must have specific identification Check for inspection stickers and dates Check for identified filler plates Identify main overcurrent device Determine size of service Safe removal of cabinet front cover No foreign objects or contamination inside cabinet Check entrance conductors and lugs Identification of grounded conductor Check clamps, connectors, and bushings No open knockouts permitted Check for disconnected or loose conductors Inspect main bonding jumper Inspect main grounding electrode conductor (GEC) Check for doubled neutrals Check for doubled hot conductors Identify any breakers that are not permitted by manufacturer No white wires on breakers Test GFCIs and AFCIs No doorbell transformers inside cabinet Check for loose equipment grounding conductor (EGC) Check for ampacity or overfusing defects No melted conductor insulation No rust, corrosion, or water inside cabinet No gaps between cabinet and wallboard greater than 1/8 inch Check multiple cables in connectors Check for damage to wires Check for damage to insulation sheathing Inspect for exposed live wires Check identified handle ties Read the label on the cabinet front cover Identify product name and type of cabinet from label Confirm amps and volts are identified on label Inspect the panelboard diagram Count maximum number of poles from the diagram Confirm location of main bonding jumper Identify twin or ½ breakers In subpanel, confirm the grounds and neutrals are isolated or floating Never leave exposed panelboard unattended Replace cabinet cover correctly |
|
#4
|
|||
|
|||
|
Thanks, Robert. I've taken the electrical course, etc. Just wasn't clear on actual field
SOP where hidden fuses were concerned. That's a good concise list. I'm printing it. Cheers, Tim |
|
#5
|
||||
|
||||
|
Make a good template on your software.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Double Main Panel Question | bboerner | Electrical Inspections | 12 | 11/6/08 10:28 PM |
| Panel Surround / Exposed Wiring Question | thance | Electrical Inspections | 11 | 2/19/08 9:06 PM |
| Panel Question | gmckenzie | Electrical Inspections | 9 | 8/24/07 1:25 AM |
| Federal Pacific 200 Amp Fuse Panel | jhagarty | Electrical Inspections | 2 | 1/24/07 12:12 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |