Just need clarification here:
Of course with being a female, I get challenged all of the time, today on a final inspection for a city based company, a new panel box was installed in the basement, 4 feet off ground, secured to the wall fine.the electric company has not yet connected to the meter or to the pole, no inspection stickers on new panel box, OF COURSE the gentleman whose company installed the panel box says they have been inspected by the city and passed, I requested the permits pulled and paperwork for final sign off and electrical license # from installer. There was no door cover present, the woman who lives in the house stated no children live there, the gentleman stated that the panel is not recessed and no cover needs to be present, is this true on a new panel box install?
Reply With Quote
  #2  
Old 7/13/06, 11:29 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

IF IF

I understand your question a panel cover must be installed.

Is that your question?
Reply With Quote
  #3  
Old 7/13/06, 11:36 PM
Laura Line Laura Line is offline
New User
 
Join Date: Feb 2004
Posts: 13
Please Note: Laura Line is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

The panel box was covered but no door present to open that latches over the circuit breaker area, is that required? a panel cover door?
Reply With Quote
  #4  
Old 7/13/06, 11:44 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Newly installed panel box

Laura,

The breakers within that panel MUST be accessible in order to turn them off in the event of a electrical issue. I do not believe and I am not with my NEC right now....but I do not believe the Distribution panel can be installed in this manner...now a AUX gutter or the like with no OCPD and so on that would be only accessed by qualified individuals fine....but not a service panel with OCPD's located inside.

I will look into more detail on this when I am back in the office, Mike may have more information on this already ready on hand.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 7/13/06, 11:48 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

Good question.

At first I have to say no requirement (because I can not site it) but I do not believe that. BECAUSE

This is the first time that I have heard this question.

Just question it.

PS I do not have a code reference Now.
Reply With Quote
  #6  
Old 7/13/06, 11:53 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

"Mike may have more information on this already ready on hand."

Thanx Paul

A picture may help.

As you can tell Paul and I do not want to tell you something unless we have the code reference.
Reply With Quote
  #7  
Old 7/13/06, 11:53 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Newly installed panel box

I will give it a FULL LOOK SEE when I am back in the office..I am on the handheld now out of town.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 7/13/06, 11:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Newly installed panel box

Mike, Agreed.....I dont like the idea of it........and it SOUNDS fishy...and it may be a good proposal for additional NEC's IF it is not their.....now we know they can be locked out in commerical settings.....because of usually an 'Authority" person has access...

But in a residential that has a CODE that likes to see things like (6) disconnect rules and 6 throws and such...seems not having access to the OCPD's in a HURRY would be...well.......potentially problematic...what do ya thing fella?



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 7/13/06, 11:57 PM
Laura Line Laura Line is offline
New User
 
Join Date: Feb 2004
Posts: 13
Please Note: Laura Line is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

thanks for your help
I wanted to be sure before I send the follow up items before I sign off. He has ripped off the client, they charged and are to be paid from the city $3695.00, (older row home)they installed a new 100 amp service panel box and service cable and repaired a circuit to outlets that were not working in house. They were to update service (old 60 amp service glass fuse panel) and wiring through house and ground outlets plus new wiring as needed. They did not rewire anything, and there are still 2 prong outlets present, she was running extension cord after extension cord for fans. (not to mention, installed a new furnace-high effiency generic brand for $3900.00 no A/C unit just a furnace, the ductwork was already there) Just a shame that some people rip others off.

I have not seen a newly installed panel box without a cover door???
Reply With Quote
  #10  
Old 7/14/06, 12:00 AM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

Paul

I would turn it down.

From my memory not the code, readily accessible?

Too damn dark to go to the truck and get my code books.
Reply With Quote
  #11  
Old 7/14/06, 12:03 AM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

Give us your location.

Someone here will help you.
Reply With Quote
  #12  
Old 7/14/06, 12:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Newly installed panel box

Ok.....double check me Mike........I may be STREECHING it a bit.....

Off memory....check out Art 240.24 I believe which should state the OCPD SHALL BE readily accessible unless certain options are met...and I dont think any of them apply here....check that for me....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 7/14/06, 12:07 AM
Laura Line Laura Line is offline
New User
 
Join Date: Feb 2004
Posts: 13
Please Note: Laura Line is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

I am in Baltimore, I will not send anything about that til tomorrow afternoon, no problem, I appreciate the help

I did question it, but have not seen yes or no
Reply With Quote
  #14  
Old 7/14/06, 12:13 AM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Newly installed panel box

Paul

I have an easy out here. As the AHJ I say NO.
Reply With Quote
  #15  
Old 7/14/06, 12:21 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Newly installed panel box

As a Part-Time fill in AHJ and ICC Residential Electrical Inspector, NEC Consultant, F-15 Fighter Pilot, Dragon Slayer, Mentor to Donald Trump ...lol....I also say NO as well....There....you got (2) NO's...lol

Ok..Ok......so I don't slay Dragons.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:24 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts