Default No AFCI In New Home

The house was built in Feb. 2006 and has never been occupied. There are no AFCI's for the bedrooms. The house resides in Cherokee Co., OK which has no electrical inspector. Cherokee Co. follows what the state of OK has adopted, which has adopted NEC 2005. Do I need to put there are no AFCI's for the bedroom circuits in my report?
Reply With Quote
  #2  
Old 1/22/07, 11:31 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,649
Default Re: No AFCI In New Home

Quote:
Originally Posted by rgant
Do I need to put there are no AFCI's for the bedroom circuits in my report?
You can certainly recommend them as an additional safety factor that is now "standard" in most new homes...avoiding any reference to "code".
Reply With Quote
  #3  
Old 1/22/07, 11:33 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No AFCI In New Home

Quote:
Originally Posted by rgant
The house was built in Feb. 2006 and has never been occupied. There are no AFCI's for the bedrooms. The house resides in Cherokee Co., OK which has no electrical inspector. Cherokee Co. follows what the state of OK has adopted, which has adopted NEC 2005. Do I need to put there are no AFCI's for the bedroom circuits in my report?
You bet CRichardsA all the way . You can not be wrong on saftey.
Roy Cooke .....How About gfci are they OK
Reply With Quote
  #4  
Old 1/22/07, 11:39 AM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No AFCI In New Home

Ahh,,,and herein lies the rub.
How do we do it without citing the dirty word...CODE ? As we are not code inspectors or enforcers.
No help , I know .
What a predicament.
I might say that current studies prove that installation of AFCI's greatly reduce the chance of an electrical fire should an arc occur.No code mentioned .
Or you could always defer to an electrician.

Cheremie
Reply With Quote
  #5  
Old 1/22/07, 12:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: No AFCI In New Home

How about simply stating that under normal construction in todays safety standards world, AFCI's are required by the minimum standards of the NFPA and should be present in new construction.

Amazing how I did a Seminar in Atlanta,GA and all the HI's wanted was CODE.....simply amazing......anyway I see nothing wrong with using an section of the NEC as a reference in such a regard as their is no formal inspection process in your county......Still makes it SAFER by the mandate of the board who determine these things and help formulate the NEC.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 1/22/07, 1:41 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No AFCI In New Home

I think the jury is still out about how much AFCIs actually add to safety.
Without quoting code I am not sure how you would talk about this. It has to be noted, a number of AHJs specifically removed the AFCI requirement in their amendments.
You can always report anything you want but I am not sure it is a defect if the AHJ doesn't call it a violation. There are guys in Chicago who call Romex a defect.
Reply With Quote
  #7  
Old 1/22/07, 1:46 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: No AFCI In New Home

One could "recommend bedroom AFCI's for enhanced safety" and leave it to them to decide.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #8  
Old 1/22/07, 1:52 PM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: No AFCI In New Home

What was the date that AFCIs became required?
Reply With Quote
  #9  
Old 1/22/07, 2:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: No AFCI In New Home

Regardless...the AFCI safety debate is not out to jury in MY mind....I happen to have seen plenty of documentation and demonstrations that I believe in them and in my mind they are much like the early days of the GFCI....However, I do not believe they need to be beyond the bedroom so personally I like the way the NEC is written now in regards to them......not the way the 2008 is moving.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 1/22/07, 3:12 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No AFCI In New Home

You can't confuse the AFCI with the GFCI, even if they are only one letter apart. The GFCI has a specified performance standard. The AFCI is more smoke and mirrors than any defined function. Certainly Cuttler Hammer has done a great marketing job in selling them but they do not protect against one of the worst kind of arcing faults, the loose connection.
This is more a case of a product looking for a market than a market need fulfilled by a product. They promised us "arc fault protection" and only delivered a product that will detect a fault that the O/C device will usually clear, a short. The place where a retrofit would really make sense would be aluminum wire, but, alas, this will not detect those faults.
Reply With Quote
  #11  
Old 1/22/07, 3:46 PM
rgant rgant is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Catoosa, OK
Posts: 13
Default Re: No AFCI In New Home

Thanks for all the input, I knew not to mention the evil CODE word and that there is alot of debate about its use ans intention. I will mention it as a current new construction safety standard that is required by the NFPA, and should be present for new home construction.
Reply With Quote
  #12  
Old 1/22/07, 4:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: No AFCI In New Home

Quote:
Originally Posted by Greg Fretwell
You can't confuse the AFCI with the GFCI, even if they are only one letter apart. The GFCI has a specified performance standard. The AFCI is more smoke and mirrors than any defined function. Certainly Cuttler Hammer has done a great marketing job in selling them but they do not protect against one of the worst kind of arcing faults, the loose connection.
This is more a case of a product looking for a market than a market need fulfilled by a product. They promised us "arc fault protection" and only delivered a product that will detect a fault that the O/C device will usually clear, a short. The place where a retrofit would really make sense would be aluminum wire, but, alas, this will not detect those faults.
Greg,

Not confusing the letters fella...lol....I just happen ( along with Mike Holt and many others ) to believe the AFCI is a move in the right direction.....let me have my opinion in it fella...lol....

With so many home fires that happen...I am all for the advancement of technology and even if we argue LOBBYISTS have put this in place....just happen to feel it is a step in the right direction for safety...and CT also has them now for both Par. and Ser arcs......

I will let you KNOW more about it when I get back from touring their plant hopefully in a few weeks....I will ask the hard questions fella....

Here is a rather nice article on the subject of do AFCI's work : http://www.pfeiffereng.com/The%20Arc...nterrupter.pdf

I happen to agree with the guy in that I believe it is a step forward...my association to it like the GFCI was based on the remarks that came out when the first GFCI came out....everyone is a skeptic until it proves to save lives and if a life is being saved for a 30-50 buck breaker....I have no problem with it.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 1/22/07 at 4:16 PM..
Reply With Quote
  #13  
Old 1/22/07, 9:00 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: No AFCI In New Home

You can recommend AFCI's installed, but before you make the statement that they ARE required, check with your state's position.

I was told, NJ and NY adopted current versions of the NEC, but have amended the AFCI's as optional.

tom
Reply With Quote
  #14  
Old 1/22/07, 9:37 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: No AFCI In New Home

What do you expect from a state that has no state licensing anyway....tells me they can't come together to agree on anything..much less AFCI's.

And the only person who said REQUIRED is wesley....and Wesley the statement on AFCI's was effective in 2002.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 1/22/07, 10:43 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No AFCI In New Home

It may be a step in the right direction but it is a crime to put something in the law that does not exist. These should be optional and let the customer decide if they want to Beta Test a device under development in their home.
This landed in the ROP for the 99 code before Cutler Hammer could even define what an arc signature was. They are still fine tuning that definition. They still can't detect a series arc. The fact is that most of the protection from these things comes from the ground fault protection anyway. AFCIs only detect shorts that spike up to about 70a and most short circuit faults will be phase to ground. The GFCI will see that and also detect a neutral to ground fault. The only advantage over a garden variety GFCI is the rare chance that you would have a phase to neutral fault inside a wall that doesn't trip the breaker. How does that happen? How often?
I have seen statistical analysis that says we are paying about 2 billion dollars per fire that *might* be prevented if these things work as advertised..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing & Legal Issues 249 1/15/09 5:49 PM
American Home Inspection Service Area jmckenna1 Misc. Discussion 3 9/4/06 8:23 PM
Misinformed CAHPI member? rwand1 Canadian Inspectors 1 8/1/06 10:39 PM


All times are GMT -4. The time now is 1:51 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts