Default No bushings in the panel

All the branch wiring left the panel (Sylvania) through the bottom knock out, with no bushing. Would you call this out as a defect?
Stu
Reply With Quote
  #2  
Old 2/20/07, 9:49 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

Yes.
Reply With Quote
  #3  
Old 2/20/07, 10:11 PM
sspradling sspradling is offline
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 227
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

Thanks, Ben. I should know this, but I'm stumbling around for wording. Any suggestions?
Stu
Reply With Quote
  #4  
Old 2/20/07, 10:52 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

Quote:
Originally Posted by sspradling
All the branch wiring left the panel (Sylvania) through the bottom knock out, with no bushing.
I don't understand this description at all.
Reply With Quote
  #5  
Old 2/20/07, 11:40 PM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: No bushings in the panel

Maybe something like, " Wiring at main panel lacked proper bushings and/or wire clamps, this applicaiton is incorrect and we suggest repair"



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #6  
Old 2/21/07, 1:00 AM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,091
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

Missing service panel protective knock out grommets, (Unsafe Condition - wiring, cable, conductors, whatever are subject to physical damage as a result of same).
Reply With Quote
  #7  
Old 2/21/07, 7:56 AM
sspradling sspradling is offline
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 227
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

Thanks Tim. Thanks Will. Sorry Speedman.
Stu
Reply With Quote
  #8  
Old 2/21/07, 8:44 AM
jwortham1 jwortham1 is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Bolingbrook, IL
Posts: 721
Default Re: No bushings in the panel

"There is wiring entering the panel without the proper protective bushings. Wiring that enters the panel should be solidly anchored and protected where it enters the panel by a bushing to prevent the sharp edges of the panel box from damaging the wiring and creating an equipment/safety hazard. Recommend installation of the proper connectors by a licensed electrical contractor. "



Jeffrey Wortham
ANS Inspections, Inc.
www.ansinspections.com
630.276.8440
638 Langford Drive
Bolingbrook, IL 60440
NACHI ID:04050181
Reply With Quote
  #9  
Old 2/21/07, 9:04 AM
sspradling sspradling is offline
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 227
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

Nice, Jeffrey. Thanks to all that understood what I was talking about. If I could just figure out the darn photo upload....I resized the photos of this to 640x480, and it was still 111kb. Oh well, some changes aren't really better, but that's another thread somewhere else. Have a great week, guys!
Stu
Reply With Quote
  #10  
Old 2/21/07, 10:17 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

Resize them to 500 x whatever it works everytime....
Reply With Quote
  #11  
Old 2/21/07, 11:58 AM
wforsyth's Avatar
wforsyth wforsyth is offline
Active Poster
 
Join Date: Feb 2006
Location: Brinnon, Wa
Posts: 7,860
Please Note: wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

When you say the bottom knock out, are you referring to the one in the base of the panel, or the bottom knockout in the front of the panel? I got a really goofy image and can't picture it as well.

Thanks.
Reply With Quote
  #12  
Old 2/21/07, 3:54 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: No bushings in the panel

Quote:
Originally Posted by wforsyth
When you say the bottom knock out, are you referring to the one in the base of the panel, or the bottom knockout in the front of the panel? I got a really goofy image and can't picture it as well.

Thanks.
The front would be an open breaker slot. He's talking about panel knock outs with out wire protection clamps/ bushings to hold the wire comming through the panel and also protects them from damage.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #13  
Old 2/21/07, 3:57 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: No bushings in the panel

Like this picture
Attached Thumbnails
no-bushings-panel-100_1459.jpg  



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #14  
Old 2/21/07, 4:00 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No bushings in the panel

Pictures would be helpful.....but when he says
Quote:
branch wiring left the panel
Pretty good sign he DOESN'T mean the front knockout, bottom, middle or otherwise.
Attached Thumbnails
no-bushings-panel-worthlesswithoutpics.gif  
Reply With Quote
  #15  
Old 2/21/07, 6:13 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: No bushings in the panel

Quote:
Originally Posted by tneumann
Pictures would be helpful.....but when he says

Pretty good sign he DOESN'T mean the front knockout, bottom, middle or otherwise.
He probably dosnt know that "Sylvania" could also be a Zinsco too



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts