Default No Ground Rod - Sure Test Says Wiring OK

I came across a house yesterday that had no ground rod, just the grounding conductor hanging from the house. The house was about 3 years old and was occupied. Hmm, didn't think the power company would put in a meter without a grounding rod.

I looked around the garage (where the panel was located) for a box where a UFER connection might be but found nothing. Exposed plumbing didn't have any bonding either. So I am thinking the system is not grounded. FWIW, the electric service was provided via buried laterals.

Since there was no visible means of grounding, I called it out for an electrician.

For grins and giggles I whipped out my Sure Test, it indicated "Wiring OK".

Now I am wondering was the Sure Test wrong? I would think that it would have indicated a "No Ground" condition or is it not that smart?

Any ideas?



Andrew Way
Keystone Residential Inspection Services PLLC
www.keystoneinspections.com
Reply With Quote
  #2  
Old 6/17/06, 11:59 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Ground Rod - Sure Test Says Wiring OK

The wiring system is grounded at the utility transformer as well.
Reply With Quote
  #3  
Old 6/17/06, 12:50 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Ground Rod - Sure Test Says Wiring OK

All the suretest, or any other plug in tester, will tell you is that the equipment grounding conductor is bonded to the neutral.
It really takes a lightning strike nearby to test the ground electrode conductor connectoin and surge protector bonding. The impedance there is the square root of the number of electrical devices destroyed.
Reply With Quote
  #4  
Old 6/17/06, 12:59 PM
Jeffrey D. Clark's Avatar
Jeffrey D. Clark Jeffrey D. Clark is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 645
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Ground Rod - Sure Test Says Wiring OK

A ground rod is usually a supplemental grounding electrode. The system should either be connected to the incoming metal water piping (within 5' of the entrance to the house) or connected to building steel (if present and effectively grounded) or foundation steel (rebar, connected by approved methods). A ground rod by itself is usually not an effective grounding method.
Reply With Quote
  #5  
Old 6/18/06, 9:30 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 834
Send a message via Skype™ to pbolliger
Default Re: No Ground Rod - Sure Test Says Wiring OK

Quote:
Originally Posted by jclark1
A ground rod is usually a supplemental grounding electrode. The system should either be connected to the incoming metal water piping (within 5' of the entrance to the house) or connected to building steel (if present and effectively grounded) or foundation steel (rebar, connected by approved methods). A ground rod by itself is usually not an effective grounding method.

James,
Is this a state thing / local thing where you are at?

What does" effectively grounded" for a wood frame house mean?
A ufer ground?
"Water pipe must be supplemented (not sole electrode) IRC 3508.1.1
NEC 250-50C (from code check)

I work in the Chicago area where a cold water pipe is used without a Grounding Electrode in old buildings BUT here lies the problem. Water pipes corrode at especially at fittings plus many old buildings used soft lead water pipes. A poor grounding electrode if you ask me.


I would argue that a grounding electrode IS an effective grounding method. But I will defer to the board sparkies for futher comment.
Reply With Quote
  #6  
Old 6/18/06, 10:13 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: No Ground Rod - Sure Test Says Wiring OK

Sure Test is not pcycic - draw out a schematic and you will see how Sure Test can be fooled -- As you can see the house ground is just a figure of speech electrically. Remember that the neutral and the "ground" are bonded at some point. Normally at the main breaker panel.

rlb
Reply With Quote
  #7  
Old 6/19/06, 12:34 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: No Ground Rod - Sure Test Says Wiring OK

Many of the power company techs will recommend a 2nd rod that is located at least 5 feet from the foundation. This is usually after a nearby lightning strike that trips most of the breakers in the panel. The magnetic fields produced by the strike will still trip breakers with one rod that may be in fairly loose soil. I often recommend a 2nd rod on homes that are waterfront due to the frequent lighting there.
Reply With Quote
  #8  
Old 6/19/06, 1:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: No Ground Rod - Sure Test Says Wiring OK

Quote:
Originally Posted by pbolliger
James,
Is this a state thing / local thing where you are at?

What does" effectively grounded" for a wood frame house mean?
A ufer ground?
"Water pipe must be supplemented (not sole electrode) IRC 3508.1.1
NEC 250-50C (from code check)

I work in the Chicago area where a cold water pipe is used without a Grounding Electrode in old buildings BUT here lies the problem. Water pipes corrode at especially at fittings plus many old buildings used soft lead water pipes. A poor grounding electrode if you ask me.


I would argue that a grounding electrode IS an effective grounding method. But I will defer to the board sparkies for futher comment.

Hey Brother......since that nice old grounding electrode is only 25 ohms or less to ground........chances are it is not greatly effective as it pertains to the house voltage.....really only their for trans and lightning issues...since as you stated at the main panel disconnect they are bonded together anyway with the grounded conductor back to the Trans.....so this is why the SureTest will still give a reading...without the rod connection.

On a related note....I guess.....lol

This is why many are electrocuted at pole lights to parking lots in some cities...they run a grounding electrode down to a ground rod thinking that meets the NEC...and it does in terms of technicals...However it is not safe because a poor 25 ohms cant aid in clearing a fault if is becomes a issue and well....death happens.

Do the math....120V and 25 OHMS resistance.......only 4.8 amps draw....sure is not going to trip anything.....so it can't clear the fault...you touch...you become a path and well......get smoked....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 6/19/06, 2:51 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,700
Default Re: No Ground Rod - Sure Test Says Wiring OK

So what is the scoop?

Does a Service Panel need bonding to a ground rod?
I see a lot of Service Panels not bonded to the meter box because plastic conduit attaches the two panels without a bond wire. Only a service ground available?
Reply With Quote
  #10  
Old 6/19/06, 6:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: No Ground Rod - Sure Test Says Wiring OK

David,

The NEC says the service can be attached to the GEC at the Meter, Panel or actually the Messenger wire......kinda depends on the AHJ and POCO in the area...as in my area we have one county that likes the GEC into the Panel and the other county likes it into the Meter Can.......go figure.

Yes, if you are using a supplimental ground rod it needs to be connected...but it will not stop the function of the system if it is not...just you will have no protection from Trans Volt or Lightning Issues.

Now if the Ground Rod is the ONLY source of the GE....it still would need to be connected.

In older homes you may only see a waterpipe connection....I still always suggest a supplimental when I do these inspections....kinda the more is better approach.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 6/19/06, 6:14 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: No Ground Rod - Sure Test Says Wiring OK

Good info, Paul.

Thanks
Reply With Quote
  #12  
Old 6/19/06, 6:21 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: No Ground Rod - Sure Test Says Wiring OK

Sorry I was kinda rushing it Larry....you know me I would have given more detail but I am trying to get some touchups ready to fly to Denver tomorrow.

Multi-tasking as we speak...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 6/19/06, 6:24 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: No Ground Rod - Sure Test Says Wiring OK

Quote:
Originally Posted by pabernathy
Sorry I was kinda rushing it Larry....
No appology needed...I really did mean Thanks.
Reply With Quote
  #14  
Old 6/21/06, 9:42 AM
Andrew Way Andrew Way is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Aledo, TX
Posts: 232
Default Re: No Ground Rod - Sure Test Says Wiring OK

All,
Sorry for getting back to this so late. Fortunately I have been busy. I had a feeling the SureTest was giving the OK due to the bonding back at the panel, just wanted to be sure.

Thanks for all the replies, especially the technical aspects provided by our electrician friends.



Andrew Way
Keystone Residential Inspection Services PLLC
www.keystoneinspections.com
Reply With Quote
  #15  
Old 6/21/06, 9:44 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: No Ground Rod - Sure Test Says Wiring OK

Andrew,

No problem fella....anytime you need something answered...you just post away my friend.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
bbbb mcyr Structural 1 8/19/07 11:26 PM
K&T splice. egarcia1 Electrical 13 2/3/07 7:36 AM


All times are GMT -4. The time now is 11:26 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts