  #1  
Old 8/15/10, 4:29 PM
Scott Donnelly Scott Donnelly is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 22
Default no main breaker

inspected a 100 amp box with no main breaker. It had 8 breakers labeld as "main breaker" to turn off all power to house and one sub panel. The box was full .Is there any soultion short of upgrading to a 200 amp panel box.
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/15/10, 4:31 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: no main breaker

How big is the house?

You may need a bigger service...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 8/15/10, 4:47 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: no main breaker

There is something not right here. There would be no need to have 8 main breakers to shut the power off. I would also ask how the wires from the meter were split to provide power to 8 breakers at the same time. Do you have pics of the panel front and the inside?

There are 100 amp panels available with main breakers and space for typically 20 circuits. I do not know why someone thought you would have to ungrade to a 200 amp panel.

A disconnect could also be installed ahead of the panel. The panel would then need to be feed with a 4 wire feeder and grounds and neutrals isolated.
Reply With Quote
  #4  
Old 8/15/10, 4:54 PM
Scott Donnelly Scott Donnelly is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 22
Default Re: no main breaker

The house is over 3000 sq ft, built in the 20's They are not really main breakers, just labeled that way. One went to a sub panel. ILL post some pics. If memory service me correctly you should not need more then 6 moves to shut off all power?
Reply With Quote
  #5  
Old 8/15/10, 4:56 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: no main breaker

One of the breakers may in fact be the main.

Did you shut it off?
Did you open the panel?
How was it wired?

You guys need to provide some information for these questions.
We can't see it from here. How can we comment about anything?

We don't even know where you work...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 8/15/10, 5:23 PM
Scott Donnelly Scott Donnelly is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 22
Default Re: no main breaker

I attached 2 pics. Yes I shut them off, one at a time. None of them shut off everything. With the use of a voltage detector I was not sure everything was off when all "labeled main breakers" were off.
Attached Thumbnails
no-main-breaker-beckford-ave-princess-anne-103.jpg   no-main-breaker-beckford-ave-princess-anne-104.jpg  
Reply With Quote
  #7  
Old 8/15/10, 5:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: no main breaker

Looks like possibly a split-bus. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 8/15/10, 5:52 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: no main breaker

Looks like a MLO (main lug only panel) to me.
Reply With Quote
  #9  
Old 8/15/10, 5:53 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: no main breaker

Not clear to me.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 8/15/10, 8:04 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: no main breaker

Quote:
Originally Posted by sdonnelly View Post
inspected a 100 amp box with no main breaker. It had 8 breakers labeld as "main breaker" to turn off all power to house and one sub panel.
Was there a disconnect upstream?

And, was this panel pictured wired as a remote distribution panel?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 8/15/10, 8:12 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: no main breaker

I wouldn't assume that a CB labeled with a sticker is actually the MAIN. Anyone could install those stickers not knowing what the word MAIN implies with regards to a service. I've seen electricians with 20 years in the business put the SERVICE DISCONNECT sticker on disconnect switches for motors having no clue what the purpose of that sticker actually is. In my eyes it's pretty clear that the panel has no main.
Reply With Quote
  #12  
Old 8/15/10, 9:08 PM
Scott Donnelly Scott Donnelly is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 22
Default Re: no main breaker

No upstream disconnect and no its not a remote sub panel. There is a sub panel next to it that is fed from here. I agree with the comment about no main breaker. I wrote it up as an unsafe situation needing further evaluation by an electrcian. I'm wondering if there is any fix short of a upgraded service since the box is full.
Reply With Quote
  #13  
Old 8/15/10, 9:17 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: no main breaker

I tried to blow the picture up to see better, but I don't even see 8 breakers labeled MAIN. I do see one two pole labeled Range and another that might say Lighting Main.

All the Square D split buss I have seen had a space between the top and bottom buss halves. But the breaker labeled Lighting Main would make me check to verify it as a split buss.
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/15/10, 9:22 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: no main breaker

Quote:
Originally Posted by Jim Port View Post
I tried to blow the picture up to see better, but I don't even see 8 breakers labeled MAIN. I do see one two pole labeled Range and another that might say Lighting Main.
Your right, there isn't 8 breakers labeled MAIN, and it looks like the one, top right, that is is feeding the sub-panel.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #15  
Old 8/16/10, 8:24 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: no main breaker

You also have grouond and nuetral wires under the same screw.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Federal Electric 100A standalone main breaker -- OK or problematic? fbartlo Electrical Inspections 16 9/6/10 5:17 PM
Arching Causes Main Breaker To Trip? msylvester Electrical Inspections 10 10/22/07 3:57 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM