  #1  
Old 3/7/06, 9:00 PM
ecox1's Avatar
ecox1 ecox1 is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Hampton, VA
Posts: 268
Send a message via Yahoo to ecox1
Default No main disconnect

Today I found this no main disconnect on main panel box. What do you guys have to say about this.
Attached Thumbnails
no-main-disconnect-elect.-panel-no-main.jpg   no-main-disconnect-picture-015-small-.jpg.jpg
Views:	121
Size:	37.3 KB
ID:	1875  
Reply With Quote
  #2  
Old 3/7/06, 9:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: No main disconnect

A split bus. Six or less throws completely disconnects the service. No problem there.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 3/7/06, 9:13 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No main disconnect

Double tap upper left.

I don't like the double pole breaker feeding off down to (what appears to be the same buss bar?

No main disconnect.

What is the multi strand aluminum looking wire right side of box?
Reply With Quote
  #4  
Old 3/7/06, 9:16 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No main disconnect

Also, and I am guessing and going solely on the photo, but..
The middle left bridged breaker (60 amp) appears to have undersized wire for 60 amp breaker?
Reply With Quote
  #5  
Old 3/7/06, 9:17 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: No main disconnect

Agree with Jeff, six throw rule okay.
Agree with Ray, double tap upper left.

Middle breaker right hand side (40 or 50 amp) double pole tie to neutral appears a tad burnt...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #6  
Old 3/7/06, 9:17 PM
Harvey Gordon's Avatar
Harvey Gordon Harvey Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 249
Default Re: No main disconnect

Jeff,

I have always respected your posts and advice..but how do you come up with Six or Less here?





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #7  
Old 3/7/06, 9:18 PM
ecox1's Avatar
ecox1 ecox1 is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Hampton, VA
Posts: 268
Send a message via Yahoo to ecox1
Default Re: No main disconnect

Quote:
Originally Posted by rwand1
Also, and I am guessing and going solely on the photo, but..
The middle left bridged breaker (60 amp) appears to have undersized wire for 60 amp breaker?
Those wires are aluminium branch wires. I recommend to have this evaluated by an electrician.
Reply With Quote
  #8  
Old 3/7/06, 9:24 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No main disconnect

Earl

I assume they are the ground wires? I see copper going under terminal screws of breaker, were does the aluminum fit into the picture. Work with me, I am going by a photo, my eyes are dim I cannot see....
Reply With Quote
  #9  
Old 3/7/06, 9:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: No main disconnect

Quote:
Originally Posted by hgordon
I have always respected your posts and advice..but how do you come up with Six or Less here?
A breaker at the lower-right of the upper bus, feeds the entire lower bus (one throw) - two double-pole breakers above that - and three double poles to the left side - six throws total.

It's possible that the double tapped breaker is not tied together, but I can't tell for sure.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 3/7/06, 9:27 PM
Harvey Gordon's Avatar
Harvey Gordon Harvey Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 249
Default Re: No main disconnect

Like I said...you da man!





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #11  
Old 3/7/06, 9:27 PM
ecox1's Avatar
ecox1 ecox1 is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Hampton, VA
Posts: 268
Send a message via Yahoo to ecox1
Default Re: No main disconnect

Quote:
Originally Posted by rwand1
Earl

I assume they are the ground wires? I see copper going under terminal screws of breaker, were does the aluminum fit into the picture. Work with me, I am going by a photo, my eyes are dim I cannot see....
Right side upper middle and left side upper middle 60 amp douple throw
Reply With Quote
  #12  
Old 3/7/06, 9:28 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No main disconnect

Jeff is correct!
Reply With Quote
  #13  
Old 3/7/06, 9:29 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: No main disconnect

Quote:
Originally Posted by jpope
A breaker at the lower-right of the upper bus, feeds the entire lower bus (one throw) - two double-pole breakers above that - and three double poles to the left side - six throws total.

It's possible that the double tapped breaker is not tied together, but I can't tell for sure.
Agreed.

hard to make out the left side of the panel from the photo.

Configuration is for 6 throws which is acceptable.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #14  
Old 3/7/06, 9:32 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,612
Default Re: No main disconnect

Quote:
Originally Posted by ecox1
Today I found this no main disconnect on main panel box. What do you guys have to say about this.
I am a retired sparky and do not get into code.... period.
.
............ my call would be!
Main panel (Immediate Further evaluation by qualified person.)
I think there is too many concerns to start and list them all.
It is wrong and must be fixed .

Roy Cooke . Royshomeinspection.com.....
Reply With Quote
  #15  
Old 3/7/06, 9:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: No main disconnect

Stranded AL is not a problem.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM
Tenant access to main disconnect in apartment bldg? lhoffman Electrical Inspections 4 9/1/06 11:54 AM
No main disconnect? mboyett Electrical Inspections 25 8/6/06 11:53 PM
Disconnect and Main panel srowe Electrical Inspections 10 6/13/06 7:49 PM
Main Disconnect Manufactured Home dbreen Electrical Inspections 1 3/4/06 12:42 PM


All times are GMT -4. The time now is 3:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts