Here's a 30 year old well built home. Service and meter in the front yard supplies a gutter and 4 sub-panels in the back yard about 75 feet away. No main disconnect on the home side of the meter (there apparently is one on the POCO side, see photo). Gutter supplies the 4 sub-panels and the sub-panels all have Grounds, Neutrals and Chassis bonded. Did I miss something or does this look OK to the sparky's? The home has been well maintained and has had some upgrades over the years and the local electricians have placed their logos on the panels somewhat indicating they approve of everything inside. Thoughts?
Attachment 4929 Attachment 4930

Last edited by mboyett; 4/9/09 at 9:38 PM..
Reply With Quote
  #2  
Old 8/5/06, 8:07 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: No main disconnect?

At that time it seems no one carried 4 conductor cables for feeding subpanels so they used 3 conductors and always thought it was correct.

As long as you have the POCO disconnect switch it should be fine.
Recommend an insulated neutral be ran to each subpanel that has 120V circuits (isolated neutrals) for safety upgrade.
Reply With Quote
  #3  
Old 8/5/06, 8:08 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: No main disconnect?

I'm not for sure but I'm thinking the gutter and panels together could be the service equipment and not load side equipment. Was the GEC/GES there at the gutter?

Paul?...others?...help us out?

Last edited by lkage; 8/5/06 at 8:47 PM..
Reply With Quote
  #4  
Old 8/5/06, 9:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: No main disconnect?

It's simple, if you ask me. Is it "service" equipment, or is it "other" equipment?

The meter and disconnect are the "service" equipment (which are clearly separated from the "other" equipment).

The gutter, which carries the load side feeders (not the service feeders), may very well "bond" the load side panels, but it does not negate the need for isolation of the neutrals (exceptions apply and will, I'm sure, be hammered in by our resident sparkies).

In any event, as Home Inspectors (and thereby, generalists), we should defer for evaluation/repair any time we see load side equipment where neutrals are grounded. Let the sparkies sort it out.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 8/5/06, 9:35 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No main disconnect?

Michael, it looks like the utility enters the meter can from behind thru that utility owned junction box. Then it would leave the meter and enter that big main disconnect. So that would qualify as the house side main.

Most utilities will not allow a disconnect like that before the meter, it would make it too easy to steal power.
Reply With Quote
  #6  
Old 8/5/06, 9:40 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: No main disconnect?

I do have to admit that the panel to the left of the meter with the disconnect was assumed to be POCO equipment feeding the meter (the house is to the right in the photo). I guess it really could be house side and the main disconnect. That would change things some wouldn't it?

Last edited by mboyett; 8/5/06 at 9:48 PM..
Reply With Quote
  #7  
Old 8/5/06, 9:40 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No main disconnect?

Service Equipment. The necessary equipment, usually consisting of a circuit breaker(s) or switch(es) and fuse(s) and their accessories, connected to the load end of service conductors to a building or other structure, or an otherwise designated area, and intended to constitute the main control and cutoff of the supply.

From what I can see in the pictures, I believe that this equipment is in terrible condition, and looks like it has not be maintained for a very long time.

The issues about the neutrals, etc., are not important here. I sincerely believe that the whole system should be evaluated by the Utility Company, the AHJ, and a licensed and qualified electriciian, if any are available.

I would love to be the fly on the wall having this to discuss with knowledgable electricians and inspection authorities on site.
Reply With Quote
  #8  
Old 8/5/06, 9:47 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: No main disconnect?

Joe, I agree that the panel area needed attention. The 91 year old owner died in Feb and his 90 year old widow is selling ($750k Texas dollars or $3M in California dollars) and moving to an assisted living facility in Dallas. The rest of the home looked much better than the panel area. Now, unless I can really identify something that is unsafe or very technically wrong I don't want to simply defer to a sparky because the panels are rusty.
Reply With Quote
  #9  
Old 8/5/06, 11:27 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: No main disconnect?

Quote:
Originally Posted by brian winkle
Michael, it looks like the utility enters the meter can from behind thru that utility owned junction box. Then it would leave the meter and enter that big main disconnect. So that would qualify as the house side main.

Most utilities will not allow a disconnect like that before the meter, it would make it too easy to steal power.

That makes sense...appreciate the lesson.
Reply With Quote
  #10  
Old 8/5/06, 11:58 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: No main disconnect?

I will Larry, once I can confirm that the switch is house side and not POCO side equipment. I think it will take another trip out to the community where the house was to talk to the AHJ there.
Reply With Quote
  #11  
Old 8/6/06, 12:03 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: No main disconnect?

Glad you're following up...assuming can really have an effect.
Reply With Quote
  #12  
Old 8/6/06, 2:09 AM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: No main disconnect?

Quote:
Originally Posted by jpope
It's simple, if you ask me. Is it "service" equipment, or is it "other" equipment?

The meter and disconnect are the "service" equipment (which are clearly separated from the "other" equipment).

The gutter, which carries the load side feeders (not the service feeders), may very well "bond" the load side panels, but it does not negate the need for isolation of the neutrals (exceptions apply and will, I'm sure, be hammered in by our resident sparkies).

In any event, as Home Inspectors (and thereby, generalists), we should defer for evaluation/repair any time we see load side equipment where neutrals are grounded. Let the sparkies sort it out.

Mr. Pope you are the Man. I have seen you go from asking seemingly silly questions .. to making the sparkies look silly.. Thank you for all that you do.
Reply With Quote
  #13  
Old 8/6/06, 1:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: No main disconnect?

Quote:
Originally Posted by tallen
I have seen you go from asking seemingly silly questions ..
Don't remind me. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 8/6/06, 1:48 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No main disconnect?

One thing struck me in the OPs pictures. When they say "less than 6" they mean to disconnect all of the power, not 6 per panel. This installation may be OK but you should have someone looking at it to say that.
Reply With Quote
  #15  
Old 8/6/06, 2:19 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: No main disconnect?

Michael -

Call me a silly boy, but once I saw it sitting on the ground and rusting out I'd have been recommending a licensed and competent electrician for further review and evaluation - for safety, age, condition, moisture, etc.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM
Tenant access to main disconnect in apartment bldg? lhoffman Electrical Inspections 4 9/1/06 11:54 AM
Disconnect and Main panel srowe Electrical Inspections 10 6/13/06 7:49 PM
No main disconnect ecox1 Electrical Inspections 19 3/7/06 9:59 PM
Main Disconnect Manufactured Home dbreen Electrical Inspections 1 3/4/06 12:42 PM


All times are GMT -4. The time now is 7:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts