  #1  
Old 1/26/08, 3:07 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default No trip Zinsco

Had an odd one late last night 1961 Zinsco 20 A circuit was in a tripped position upon arrival, but still energized, it would not reset to the ON position or turn off. Labeling was long gone so I couldn't identify exactly what it was servicing.

Besides the obvious RR any ideas on why this occurred or what may have caused it?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 8:21 PM..
Reply With Quote
  #2  
Old 1/26/08, 4:14 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: No trip Zinsco

Nope
Reply With Quote
  #3  
Old 1/26/08, 9:28 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No trip Zinsco

I'll bet the the bus bar behind it is melted and the breaker is fused to it.
Reply With Quote
  #4  
Old 1/26/08, 10:47 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: No trip Zinsco

Quote:
Originally Posted by wsiegel
I'll bet the the bus bar behind it is melted and the breaker is fused to it.
Not specifically at this breaker location but the 3 above it that appeared functional and unaffected were or starting too.

This panel is being replaced in the very near future, like today!

Anyone needing these pics to make a point to client, broker or realtor...feel free to use them, credit me or not, it's way too important



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 8:21 PM..
Reply With Quote
  #5  
Old 1/26/08, 11:47 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: No trip Zinsco

This is one of the problems with Zinsco. Unfortunately, it's not uncommon. It has nothing to do with the bus bars or the connection to the breaker. It's, quite simply, a deficient breaker.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 1/26/08, 11:54 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: No trip Zinsco

Quote:
Originally Posted by jpope
This is one of the problems with Zinsco. Unfortunately, it's not uncommon. It has nothing to do with the bus bars or the connection to the breaker. It's, quite simply, a deficient breaker.
Man, I've been waiting for you to show up

I mused if anyone knows it will be my buddy, The Pope

Thanks for the reply



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #7  
Old 1/26/08, 2:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: No trip Zinsco

Any time. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 1/26/08, 2:38 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No trip Zinsco

http://www.inspect-ny.com/electric/Zinsco.htm

I didn't see your specific scenario mentioned here, but there is an allegation(?) of the circuit not being deactivated when the breaker is turned off.
Reply With Quote
  #9  
Old 1/26/08, 2:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: No trip Zinsco

I have personally seen this "specific scenario" on many occasions. It is a common problem with Zinsco breakers.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 1/26/08, 3:00 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No trip Zinsco

I have inspected well over 100 Zinsco panels and have not noticed that issue in the past. I will certainly watch more closely for it from now on.

Thanks for the heads up.
Reply With Quote
  #11  
Old 1/26/08, 9:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: No trip Zinsco

As many as we have in CA, I'm sure it won't be long before you notice this condition. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 1/26/08, 9:30 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: No trip Zinsco

Quote:
Originally Posted by badair
Not specifically at this breaker location but the 3 above it that appeared functional and unaffected were or starting too.

This panel is being replaced in the very near future, like today!

Anyone needing these pics to make a point to client, broker or realtor...feel free to use them, credit me or not, it's way too important
Those are some damn good pictures Barry.....
Reply With Quote
  #13  
Old 1/26/08, 9:40 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: No trip Zinsco

Quote:
Originally Posted by jpope
I have personally seen this "specific scenario" on many occasions. It is a common problem with Zinsco breakers.
What do you put in your report Senor' Zinsco.........

It's odd you have never posted any of the problems you have come across with these gems........................

...........................

Quote:
many
Oh that made me laugh....!!......

I really do miss your exciting pictures, but I remember your under duress at the present time.....
Reply With Quote
  #14  
Old 1/26/08, 10:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: No trip Zinsco

Stay tuned. More will be revealed. This case is really starting to "heat-up", if ya know what I mean



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 1/27/08, 11:29 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No trip Zinsco

That is not only a great set of pictures, but explains well the situation you came across..

I would just like to add that this situation (a breaker tripping and still in the closed position) is not subject just to zinsco/fedpacific type breakers. I have been in the industry a few years, and I have come across this many times with all brands of CBers.
Just a ..."be careful" post.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"Magnetrip" by Zinsco rspriggs Electrical Inspections 8 12/4/07 10:44 PM
Zinsco cbuell Electrical Inspections 4 1/4/07 3:31 PM
Yes, to trip or not to trip kshepard Electrical Inspections 8 5/25/06 10:14 PM
GFCI trip or not to trip abishop Electrical Inspections 11 5/24/06 6:43 PM


All times are GMT -4. The time now is 3:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts