Default NON insulated Ground wire

Need help with the writeup.

So far.
the equipment grounding conductor
Unshielded or non insulated, non color code panel ground wire showing erosion.
SUSPECT GROUNDING CONDUCTOR DEFICIENCY;
To small for 200 amp.
8awg.
Deficiencies; Erosion, galvanized metal contact ( metal staple ) out side the panel.
Uninsulated ground panel wire.
Corrosion .
Electrical panel ground wire are designed to provide a path that will trip a breaker in the event of a shortage. This path is made possible through the main bonding jumper.
Galvanized metallic staples on copper strand-wire grounding conductor into plywood base.
Signs of open exterior access into the plastic conduit. Dead wasps.
Unused breaker fuses at the panels inclosure's bottom.
non-insulated-ground-wire-brian-peddar-098.jpg

non-insulated-ground-wire-aa4.jpg



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/11/12, 11:18 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NON insulated Ground wire

Not sure about in Canada but under the NEC that would likely be a GEC (or grounding electrode conductor) not an EGC. It would be permitted to be bare, and if it were going to a ground rod the maximum size required would be a #6. Also there is nothing wrong with spare breakers in the panel. One other note the GEC's purpose is not for the opening of an OCPD during a fault condition.
Reply With Quote
  #3  
Old 1/11/12, 11:55 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: NON insulated Ground wire

Quote:
Originally Posted by Robert Meier View Post
...the maximum size required would be a #6.
There is no required maximum. The minimum required is #6.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 1/12/12, 12:02 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: NON insulated Ground wire

grounding electrode conductor My mistake.
Taken from side notes.
Yes #6 awg.
I thought the panel was to be void of excess components or conductive materials.


Did you see the corrosion?
Ground strand wire corrosion over 30% corroded.
Electrical tape except where it comes out the panel.


Copper in contact with galvanized staples.
Electrolysis is not spontaneous. It requires an external source of energy.
Galvanic corrosion?

12 dead wasps in the bottom of the panel. Noted.
Drip loop fine and masthead weather proof.

non-insulated-ground-wire-aa6.jpg



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 1/12/12 at 12:11 AM..
Reply With Quote
  #5  
Old 1/12/12, 6:38 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: NON insulated Ground wire

Quote:
Originally Posted by ryoung7 View Post
Need help with the writeup.
Quote:
Originally Posted by ryoung7 View Post

So far.
the equipment grounding conductor
This is the grounding electrode conductor

Quote:
Originally Posted by ryoung7 View Post
Unshielded or non insulated, non color code panel ground wire showing erosion.
Quote:
Originally Posted by ryoung7 View Post
SUSPECT GROUNDING CONDUCTOR DEFICIENCY;
It is not required to be insulated and it is not required to be color coded
Quote:
Originally Posted by ryoung7 View Post
To small for 200 amp.
Quote:
Originally Posted by ryoung7 View Post
8awg.
It is larger than 8 and looks like it is plenty large enough
Quote:
Originally Posted by ryoung7 View Post
Deficiencies; Erosion, galvanized metal contact ( metal staple ) out side the panel.
Quote:
Originally Posted by ryoung7 View Post
Uninsulated ground panel wire.
Corrosion .
again it is not required to be insulated and the use of metal staples if fine. The corrosion in no way makes it deficient

Quote:
Originally Posted by ryoung7 View Post
Electrical panel ground wire are designed to provide a path that will trip a breaker in the event of a shortage.
This is not true. The grounding electrode plays no role in the operation of the overcurrent devices. The grounding electrode system is installed for four reasons and four reasons only. 1- lightning. 2- power surges. 3- unintentional contact with higher voltage lines. 4- to keep everything stable


Quote:
Originally Posted by ryoung7 View Post
This path is made possible through the main bonding jumper.
This is true. During a fault the faulted current travels on the equipment grounding conductor back to the service equipment, through the main bonding conductor, to the neutral and back to the source which causes a high current draw that opens the overcurrent device


Quote:
Originally Posted by ryoung7 View Post
Galvanized metallic staples on copper strand-wire grounding conductor into plywood base.
there is nothing wrong with the staples holding the conductor

Quote:
Originally Posted by ryoung7 View Post
Signs of open exterior access into the plastic conduit. Dead wasps.
Quote:
Originally Posted by ryoung7 View Post
Unused breaker fuses at the panels inclosure's bottom.
Can’t see any plastic conduit in the picture so can’t comment but as to the bugs that is going to happen. I have even found rats and snakes in the panel.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #6  
Old 1/12/12, 8:19 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NON insulated Ground wire

Quote:
Originally Posted by jfunderburk View Post
There is no required maximum. The minimum required is #6.
A GEC to a rod is not required to be larger than a #6. You can install a larger one if you wish but the NEC will not require you to do so.

Last edited by Jim Port; 1/12/12 at 9:18 AM.. Reason: clarity
Reply With Quote
  #7  
Old 1/12/12, 8:24 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NON insulated Ground wire

Quote:
Originally Posted by jfunderburk View Post
There is no required maximum. The minimum required is #6.
For a typical 200 amp service the GEC, sized according to T250.66, is #4 Cu. However as I stated in post #2 the largest GEC required to a ground rod is #6 Cu. If the conductor in question is going to a water pipe then a #6 would be too small.
Reply With Quote
  #8  
Old 1/12/12, 9:10 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: NON insulated Ground wire

Thank you. Mr.Whitt
Thank you everyone.
Yes not my strong suite.
I must educate more..
I thank you all.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #9  
Old 1/12/12, 9:39 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: NON insulated Ground wire

Originally Posted by ryoung7
Electrical panel ground wire are designed to provide a path that will trip a breaker in the event of a shortage.

This is not true. The grounding electrode plays no role in the operation of the overcurrent devices. The grounding electrode system is installed for four reasons and four reasons only. 1- lightning. 2- power surges. 3- unintentional contact with higher voltage lines. 4- to keep everything stable
Off a website dedicated to residential electrical educational information.
They quote and link to NEC material.
Will not go there agin.

A
Uninsulated ground panel wire.
Corrosion .

again it is not required ( I understand ) to be insulated and the use of metal staples if fine. The corrosion in no way makes it deficient.

The ground is corroded, by 1/3 its thickness in areas between the staples.
Signs of corrosion ( various degrees ) throughout the exposed viable wiring.

Copper in contact with
Ferrous alloy
Did not test ground for current. Should have.

Hypotheses: Electrolysis is not spontaneous. It requires an external source of energy.The screws triggered my tickers at a low setting.
Galvanic corrosion? moisture, temperature, and the level of pollution.
There is no sacrificial anode. The weakest metal will degrade.
Couples of copper and aluminum or copper and steel can lead to severe galvanic corrosion (see also Galvanic Series of Metals in Seawater or Galvanic Corrosion Chart).


Non-Ferrous They are not magnetic and are usually more resistant to corrosion
So leave out the Ferrous alloy contact.
Any recommendations or hypotheses to the corrosion.






montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #10  
Old 1/12/12, 11:23 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: NON insulated Ground wire

Quote:
Originally Posted by ryoung7 View Post
Thank you. Mr.Whitt
Thank you everyone.
Yes not my strong suite.
I must educate more..
I thank you all.
My dear friend it is Mike. Mr. Whitt was my dad



Mike Whitt
Contractor/Instructor
Reply With Quote
  #11  
Old 1/12/12, 11:35 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: NON insulated Ground wire

Quote:
Originally Posted by ryoung7 View Post
Any recommendations or hypotheses to the corrosion.
A ground rod is required to be 8 feet long and the entire length of the rod is required to be in contact with earth. Think about what is taking place at this connection.

What you see on the conductor in the picture has to do with what it is exposed to not the fact that metal staples is coming in contact with the copper. I have saw solid copper stapled to the bottom of floor joist that had a green color but once outside looked brand new. It all depends on the chemicals that it is exposed to. Forget about all this hype concerning galvanic reaction.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #12  
Old 1/12/12, 11:55 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: NON insulated Ground wire

OK Joseph.
Permission to address you by your first name.

Hype should not be used nor is it being implied.

Null Hypotheses drawing to fact is my only quest.

The recommendation is done.

The amount of corrosion in such a short, confined space.
Safety!!
That is all!!
non-insulated-ground-wire-aa7.jpg
non-insulated-ground-wire-aa10.jpg
non-insulated-ground-wire-aa11.jpg
Click image for larger version

Name:	aa7.jpg
Views:	51
Size:	67.3 KB
ID:	51419
Attached Thumbnails
non-insulated-ground-wire-aa8.jpg   non-insulated-ground-wire-aa9.jpg  



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #13  
Old 1/12/12, 11:59 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NON insulated Ground wire

That one photo looks like PVC male adapters are used instead of cable connectors.
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/12/12, 5:45 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: NON insulated Ground wire

Quote:
Originally Posted by ryoung7 View Post
OK Joseph.
Permission to address you by your first name.
Look at my signature line. My Mom called me by my middle name “Micheal” or “mike” for short.

If you feel in your heart that it needs pointing out then by all means please call it out but don’t be upset should an electrician come along and say that nothing is wrong with the conductor.

The first thing we should think about is just what the job of that conductor is. It is not a current carrying conductor. Its sole purpose is to allow lightning a path to travel or in the event of a power surge (not a spike) or should a high voltage line come in contact with the service drop and to keep the level of the service at the same point to earth at the building as it is at the transformer.

The electrical system will work just as well without that conductor as it will with it in place. Its sole purpose is those four outlined above.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #15  
Old 1/12/12, 9:07 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: NON insulated Ground wire

http://electronics.howstuffworks.com...-protector.htm

  • When the increase lasts three nanoseconds (billionths of a second) or more, it's called a surge.
  • When it only lasts for one or two nanoseconds, it's called a spike.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM


All times are GMT -4. The time now is 7:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts