When the NEC is addressing line surges it is addressing the switching of grids which can cause a surge of voltage of several thousand volts that have been known to last for several sine waves. Lightning striking a substation or transmission lines can cause surges on our services that last as long as the visible flash that surge protectors such as the plug-in strip type cannot stop. This type of surge will need a surge arrester installed at the service in order to be of benefit to the user although the plug-in type will afford some protection

Smaller surges such as motors in AC units, air handlers, well pumps and the like is not what is being addressed by the NEC. These surges will be very short lived, in the nanosecond time period and the voltage level will be less than a thousand volts. These surges are similar to spikes and the plug-in surge strips are designed to stop these.

It is high voltage types of line surges that have someone using uncategorized testing equipment getting hurt. All voltage testers used at a service should be a category IV at 600 volts. Meters that have no category rating should never be used for anything larger than electronic circuits. This information can be found in NFPA 70E.



Mike Whitt
Contractor/Instructor
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 1/12/12, 11:25 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: NON insulated Ground wire

Thanks, Mike.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM


All times are GMT -4. The time now is 7:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts