Does anyone know if a smoke alarm/dectector that is 20 feet above the floor "has" to have battery backup? My 80 year old, home alone, lady client doesn't like changing the battery this high up.
Reply With Quote
  #2  
Old 3/6/07, 12:01 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nose bleed smoke alarm/detectors

Quote:
Originally Posted by cbuell
Does anyone know if a smoke alarm/dectector that is 20 feet above the floor "has" to have battery backup? My 80 year old, home alone, lady client doesn't like changing the battery this high up.
Simple fix buy a new one and mount it lower down .
Roy Cooke
Reply With Quote
  #3  
Old 3/6/07, 12:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nose bleed smoke alarm/detectors

Must it have a battery? Only if the IRC applies to that dwelling. It seems that your choices are battery only, or commercial voltage with battery backup.

R313.2 In new construction, the required smoke alarms shall recieve their primary power from the building wiring when such wiring is served from a commercial source, and when primary power is interrupted, shall recieve power from a battery. Wiring shall be permanent and without a disconnecting switch other than those required for overcurrent protection. Smoke alarms shall be permitted to be battery operated when installed in buildings without commercial power or in buildings that undergo alterations, repairs, or additions regulated by Section R313.1.1

Smoke alarms are available with a remote battery source, such as those as the ADT type low voltage fire alarm systems that run to a central panel with a large battery backup for the whole system.
Reply With Quote
  #4  
Old 3/6/07, 12:11 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nose bleed smoke alarm/detectors

It just dawned on me that many local fire departments will come out and change the smoke detector batteries for older folks as a community service. They even provide the batteries. Maybe this person should just keep the non-emergency number for the fire house handy, and they can come out every once in a while and square her away?

I'm a little worried about the proposal to mount the detector lower, as the detectors are to be mounted within (12" ?) of the ceiling to function as they are intended.
Reply With Quote
  #5  
Old 3/6/07, 12:44 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Nose bleed smoke alarm/detectors

Quote:
Originally Posted by Marc D. Shunk
I'm a little worried about the proposal to mount the detector lower, as the detectors are to be mounted within (12" ?) of the ceiling to function as they are intended.
Me too. I see quite a few vauted ceilings and the detectors are mounted quite high. 12-15 ft is not uncommon.
Reply With Quote
  #6  
Old 3/6/07, 12:49 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: Nose bleed smoke alarm/detectors

The lithium batteries in low-drain detectors are good for 10 years - at which point you ought to change out the detector anyway.

http://www.amazon.com/Ultra-Battery-.../dp/B00004W3ZE

What makes ME crazy (I live in a house with cathedral ceilings) is trying to figure out which detector is producing a low-battery warning "beep" - "there outta' be a law" requiring an LED to come and stay on when a low batter conditions is detected.

Last edited by mthomas2; 3/6/07 at 12:56 PM..
Reply With Quote
  #7  
Old 3/6/07, 12:51 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nose bleed smoke alarm/detectors

Quote:
Originally Posted by Marc D. Shunk
It just dawned on me that many local fire departments will come out and change the smoke detector batteries for older folks as a community service. They even provide the batteries. Maybe this person should just keep the non-emergency number for the fire house handy, and they can come out every once in a while and square her away?

I'm a little worried about the proposal to mount the detector lower, as the detectors are to be mounted within (12" ?) of the ceiling to function as they are intended.
Good call Roy

http://www.usfa.dhs.gov/downloads/pyfff/smkalarm.html
If an alarm is mounted on an exterior wall or a ceiling below an unheated attic that is poorly insulated
(the surface gets noticeably cold in the winter and warm in the summer), the temperature difference
can prevent smoke from getting to the alarm. Placing the alarm on an inside wall avoids the problem.
In desert climates where evaporative coolers are being used, mount smoke alarms on walls 12 inches below the ceiling.
These coolers add moisture that can cause the smoke to drop.
Older adults may have difficulty reaching alarms on the ceiling to change batteries.
If hard-wired alarms are impractical, wall mounting 12 inches down should be considered.
Reply With Quote
  #8  
Old 3/6/07, 1:08 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: Nose bleed smoke alarm/detectors

The 12" requirement is modified for sloped or peaked ceilings:

http://www.brkelectronics.com/downlo...to_install.pdf
Reply With Quote
  #9  
Old 3/6/07, 1:19 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: Nose bleed smoke alarm/detectors

Hum... now this is cool: a smoke alarm you can silence (including low-battery alert) using most TV remotes:

http://www.firstalert.com/manuals/M08_0071_002E%20(SA302_HD)WEB.pdf
Reply With Quote
  #10  
Old 3/6/07, 1:45 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nose bleed smoke alarm/detectors

If there is any "code" on smoke detector mounting, it is in NFPA 72, The National Fire Alarm Code.

There's lots of information in ther about mounting heights and spacings of heat detectors, but oddly, very darned little about smoke detectors. The guidance basically given in NFPA 72 with regard to smoke detector placement is:
-Don't install them in areas below 32°F, over 100°F, over 93% humidity, and in places with more than 300 ft/min air velocity.
-In large rooms, space them no more than 30 feet apart.
-Follow manufacturer's instructions.


Reply With Quote
  #11  
Old 3/6/07, 3:21 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Nose bleed smoke alarm/detectors

My "Free Smoke Detector Installation" program offers battery operated smoke detectors that have 10 year batteries. So no battery changing, just smoke detector changing in 10 years.

tom
Reply With Quote
  #12  
Old 3/6/07, 4:47 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nose bleed smoke alarm/detectors

I have argued with IAEI guys about this for years. They will say NFPA72 requires the detector up in the tray or on the ceiling of a vaulted ceiling near the peak, in spite of the fact that this is never going to be accessible to the homeowner.
It can cost up to $100 to get these batteries replaced and as often as not they will just have the guy take the detector down and put a blank cover over the hole. Now, in the effort to squeeze the last .01% of effectiveness out of the detector they have created a situation where they will likely end up with zero.
If I was an HI I would point out detectors that are not accessible as an issue they have to consider. That battery will die (if it has one in the first place) and it will be a pain to replace. Bear in mind, more people are killed and injured every year from falls than fires.
Reply With Quote
  #13  
Old 3/6/07, 4:49 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nose bleed smoke alarm/detectors

BTW I would call a smoke detector in a tray with a fan as a defect
Reply With Quote
  #14  
Old 3/7/07, 7:17 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Nose bleed smoke alarm/detectors

Quote:
Originally Posted by Greg Fretwell
BTW I would call a smoke detector in a tray with a fan as a defect
Greg,

Do you have a photo example of this specific configuration?

If you can't post here please email: adairinspex@adairinspection.com



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #15  
Old 3/7/07, 9:21 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,751
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Nose bleed smoke alarm/detectors

Hi to all,

while we're on this subject, this weekend the clocks move forward, many authorities suggest checking alarms and replacing batteries at this time.

It's also a good excuse to email your former clients with a timely reminder.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Escape, Fire & Smoke Alarms badair Interior 14 1/28/08 8:21 AM
QOD for 1/22/07 (Smoke Detectors) jbowman Question of the Day 9 4/14/07 9:33 AM
2 questions staylor5 Electrical 9 3/23/07 11:40 PM
smoke detectors in bedrooms bgraham Electrical 3 1/27/07 2:19 PM


All times are GMT -4. The time now is 5:06 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts