A receptacle below the bathroom sink in the cabinet (you have to open a cabinet door), would that fall under the exception rule (1) not needed to be GFCI protected since it is not readily accessible ??
#2
The GFCI function is for the person using the appliance plugged in. Can a hair dryer for example be plugged in and reach the sink? I say it should be GFCI protected.
Peter Siposs Absolute Home Inspections Home, Mold, IAQ, Radon, & Lead Based Paint Liberty Lake, WA Serving Eastern WA & Northern ID Nachi# 05100181 peter@absolute-home-inspections.com |
#3
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
What exception? 210.8(A)(1) just says "bathrooms".
All 15 and 20a 120v receptacles in the bathroom must have GFCI protection without exception. (at least as far back as 1975) I think you are confusing other parts of 210.8 that did have exceptions but they don't apply to the bathroom. |
#4
NEC 2002 210.8 (A)
Exception No.1 Receptacles that are not readily accessible. |
#5
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
There are NO exceptions to "210.8(A)(1) Bathrooms". |
#6
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quite a contrast to the post, I don't remember if it was here, where HI wanted GFI protection for dining room receptacle on the other side of a pass thru that was within 6' of the kitchen sink.
#7
Please Note:
He can "want" all he wants. That "request" holds no water.
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel (A)(6) Kitchens — where the receptacles are installed to serve the countertop surfaces |
#8
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Visit the other site for a full explanation of this |
#9
Please Note:
The short answer is the exception you are looking at is to 210.8(A)(2) and does not apply to 210.8(A)(1). Two separate rules.
#10
Thanks Mike
| Thread Tools | |
Similar Threads
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| More GFCI info from U/L | Greg Fretwell | Electrical Inspections | 9 | 12/4/07 8:33 PM |
| GFCI Safety Notice | rcooke | Electrical Inspections | 1 | 10/30/07 12:29 PM |
| The question asked on the new HI Study test here? | jtedesco1 | Electrical Inspections | 28 | 10/4/06 9:31 AM |
| UL Information about Testing of GFCIs | jtedesco1 | Electrical Inspections | 0 | 2/5/06 4:38 PM |