Default Number of Romex wires in one hole

Guys need some quick help. How many romex wires can be in one 1 1/2 in hole in a wood top plate. I have a circuit panel inside a garage, new construction, with the hole at the top plate completely stuffed with 12/2 romex. I have attempted to add the picture, but don't think it went through.
Reply With Quote
  #2  
Old 10/6/07, 3:55 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,295
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

There is no limit. Some might say this is bundling, but I seriously doubt the wires are tightly grouped together for more than 24" in this instance.
Reply With Quote
  #3  
Old 10/6/07, 4:03 PM
Russell E. Napper Russell E. Napper is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Bulverde, TX
Posts: 33
Default Re: Number of Romex wires in one hole

thanks
Reply With Quote
  #4  
Old 10/6/07, 6:43 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

As many as you can without damaging the jackets of the cables.
Reply With Quote
  #5  
Old 10/6/07, 8:38 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,054
Default Re: Number of Romex wires in one hole

Spock: An illogical approach to electricity does have its advantages on occasion, Captain.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #6  
Old 10/6/07, 8:55 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Number of Romex wires in one hole

You need to address derating issues when stuffing holes with cables.

tom
Reply With Quote
  #7  
Old 10/6/07, 9:33 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,295
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

Quote:
Originally Posted by tdietrich1
You need to address derating issues when stuffing holes with cables.

tom
Care to support this claim?
Reply With Quote
  #8  
Old 10/6/07, 10:36 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

Quote:
Originally Posted by tdietrich1
You need to address derating issues when stuffing holes with cables.

tom
Electrical Myth #47
Reply With Quote
  #9  
Old 10/7/07, 12:24 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,795
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

You only need to derate if they stuff insulation in that hole 334.80. Do you have an energy code?
Reply With Quote
  #10  
Old 10/7/07, 9:04 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Number of Romex wires in one hole

Quote:
Originally Posted by Marc D. Shunk
Electrical Myth #47
Not around here(NE Pa) I've been getting word from other electricians that fire inspectors are looking at not just top and bottom plates, but studs and joists. So when drilling hole and running wires, we break our runs up to minimize bundling, and how many #14's and #12's go through holes. We can get the order to fire caulk every hole, as they want. The Myth is that this is coming from California, I think it's being lobbied by fire caulk makers.

tom
Reply With Quote
  #11  
Old 10/7/07, 9:41 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

Quote:
Originally Posted by tdietrich1
Not around here(NE Pa) I've been getting word from other electricians that fire inspectors are looking at not just top and bottom plates, but studs and joists.
Hey, I'm in PA too, and we all work out of the same set of rules. Bundling is not bundling until it's for 24 inches or more. I'd appeal the red tag for multiple cables in a top or bottom plate in a heartbeat, and I'd have to win. The code text is very clear on that matter.
Reply With Quote
  #12  
Old 10/7/07, 10:19 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Number of Romex wires in one hole

Quote:
Originally Posted by Marc D. Shunk
The code text is very clear on that matter.
So is 90.4

So now just incase, I drill an extra hole everytime I get to 9 cc's 14# and 12# and 6 for #10.

tom
Reply With Quote
  #13  
Old 10/7/07, 10:39 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

Quote:
Originally Posted by tdietrich1
So is 90.4
90.4 isn't permission to make stuff up.
Reply With Quote
  #14  
Old 10/7/07, 10:48 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,295
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

Quote:
Originally Posted by Marc D. Shunk
90.4 isn't permission to make stuff up.
You better beileve it!
Reply With Quote
  #15  
Old 10/7/07, 10:57 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,295
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

The rule about derating cables through firestopped holes is new in 2005. This is ONLY for holes that are (or to be) firestopped.

So here again we are caught with the "when was the hosue built" problem and "what code was it under when it was built".
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
HVAC age tspeerstra General Inspection Discussion 11 3/7/12 8:25 AM
September Inspection Slow Down?!?!?!.... jwatts1 Miscellaneous Discussion for Inspectors 13 9/20/07 5:47 PM
Need Help With an age of a Bryant bbishop1 Inspecting HVAC Systems 4 11/27/06 12:27 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM

All times are GMT -4. The time now is 9:15 AM.
no new posts