Default Re: Number of Romex wires in one hole

Good points Speedy,

I'm addressing both worse case, if I get hounded by the fire inspector, and then by the electrical inspector, so commenting specific on my work.

However, the OP says New Construction, Russel is in Texas (they adopted the 2005 NEC about the same time we [Pa]), through a TOP Plate(so fire caulking[or other method] should be required if not by fire codes, the NEC implied), so 334.80 seems to apply here(in this post).

Seems the term "bundling" is open for discussion, it was mentioned a distance was required, but I was instructed by an inspector, the actual text for derating[related 310] is 'bundled more than 24"' if just 'bundled' is mentioned, no distance is implied. So any bundling is bundling [related to 334], therefore bound by a hole in wood is bundling.

tom

Last edited by tdietrich1; 10/7/07 at 11:11 AM..
Reply With Quote
  #17  
Old 10/8/07, 8:44 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Number of Romex wires in one hole

Ironically enough when you do get involved with the derating of the NM Cable for the examples you all are giving....and end up using 90 degree for derating it in most cases with 14 AWG and 12 AWG wont effect the ampacity.

Basically if we had (4) 14-2 NM Cables thru the firestop....(4) current carry conductors so apply 310.15(b)(2)(a) and 80% would still be fine....for 15A breaker.....without getting too detailed in it...so really it is not nearly an issue as other factors.....

For example...how many inspectors make electricians adjust the ampacity in areas where the attics get VERY HOT........again without doing the math would it matter much on smaller NM Cable....probably not.


Where more than two NM cables containing two or
more current-carrying conductors are bundled together and
pass through wood framing that is to be fire- or draftstopped
using thermal insulation or sealing foam, the allowable
ampacity of each conductor shall be adjusted in
accordance with Table 310.15(B)(2)(a).

Now...I really dont like how this is written........I had one argument a 14-2 contains only (1) current carry conductor and because how that reads it says...more than (2) NM Cables containing two or more current-carry conductors.....but a 14-2 only has (1) current carry conductor.....lol....I know...I know......but thats how debates get going.



Paul W. Abernathy

Last edited by pabernathy; 10/8/07 at 8:53 AM..
Reply With Quote
  #18  
Old 10/8/07, 11:54 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

In residential you really don't have that much firestopping, it is mostly draft stopping. That is why I asked about your "energy code". Generally the only fire rated assembly in R3 is a ceiling over a garage if there is living space above. Some local codes also want 1hr between a garage and the rooms next to it but that is not how the IRC/Florida Building Codes read. It is assumed draft stopping also slows the spread of fire products and thus does slow the spread of fire. If this is that spray in foam YMMV since it is flammable. They are taking a long hard look at that in Florida as we speak.
For the purposes of 334.80 it is a distinction without a difference. If the hole has insulation in it you must look at derating. It really just gets back to the original question. How many wires are in one hole. This pretty much tells the installer not to jam all the Romex in one big hole. Drill several smaller ones.
Reply With Quote
  #19  
Old 10/9/07, 1:32 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Number of Romex wires in one hole

Here in Pima County, Arizona fire caulking is now required on all top plate penetrations for residential. And yes, de rating in these holes is being enforced. We are buying smaller bits and drilling more holes.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
HVAC age tspeerstra General Inspection Discussion 11 3/7/12 8:25 AM
September Inspection Slow Down?!?!?!.... jwatts1 Miscellaneous Discussion for Inspectors 13 9/20/07 5:47 PM
Need Help With an age of a Bryant bbishop1 Inspecting HVAC Systems 4 11/27/06 12:27 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM


All times are GMT -4. The time now is 3:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts