I inspected a new home that had a very odd service grounding configuration, with the primary grounding wire connected to a copper clamp on iron rebar sticking out of basement floor.
Not only does a piece of rebar sticking about a foot out of the basement floor appear to be a potential hazard, but the use of a copper clamp to connect to an iron bar screams of temporary grounding while the yard (which was basically dirt and weeds) is being sorted out. I've inspected many new houses -- not many lately, being in the Detroit area -- but have not seen anything quite like this. Thoughts, anyone? |
| Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Ufer?
"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission Last edited by dandersen; 8/13/11 at 9:55 PM.. |
|
#3
|
|||
|
|||
|
I'm aware of Ufer grounding connections, but the copper connector to iron and potentially hazardous rod sticking out of the floor seemed odd, for the reasons I mentioned.
Last edited by fbartlo; 8/13/11 at 10:19 PM.. |
|
#4
|
||||
|
||||
|
a number of bronze alloy clamps are designed for direct burial and suited for direct rebar contact/connection
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#5
|
|||
|
|||
|
Do those bronze connectors look just like copper clamps, and are not such connections supposed to be buried or at least enclosed by some sort of panel if they are to be accessible?
|
|
#6
|
||||
|
||||
|
Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#7
|
|||
|
|||
|
Thanks for the link, Jeffrey. So my instincts were correct, after all. Maybe it is a temporary rig.
|
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Why would you think that it was a temporary connection to the CEE? Looks like a hazard if you fell on it, but most likely it's electrically code compliant. |
|
#9
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
I see no reason to think that is temporary either. It matches the one pic in the link in Hansens article. As long as there is still 20' of rebar in the footing the top of the rebar could be cut off.
|
|
#10
|
|||
|
|||
|
What size is the wire? Looks to small to be a service ground.
|
|
#11
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Could be, the OP doesn't mention the size of the service entrance conductors. For copper the minimum size would be #8 for a typical 100 amp service but that would require physical protection so my guess is that it's a #6 GEC which would be OK for a typical 150 amp service. A copper #4 is the largest GEC required to a CEE. |
|
#12
|
|||
|
|||
|
Conductor was 6 gauge copper for 150A service. Based on the info in Jeff's link, the features that "felt" wrong were wrong, even if it is effective for electrical grounding purposes, which it did appear to be.
|
|
#13
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Then it was properly sized. |
| Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
What features are you saying are wrong?
|
|
#15
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Good question. #6 Cu to a CEE for a typical 150 amp service would be code compliant.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| something else to chew on | john bubber | Structural Inspections | 706 | 4/25/12 7:13 AM |
| Poly being applied to Basement walls | dvalley | Interior Inspections | 40 | 11/24/09 10:49 PM |
| VIDEO--Bowed Basement Wall, Cracks etc | john bubber | Structural Inspections | 75 | 7/21/08 5:25 PM |
| Where do I put the Aquarium? | mcyr | Structural Inspections | 3 | 11/6/07 3:05 PM |