Default Odd grounding with copper clamp on iron rebar sticking out of basement floor

I inspected a new home that had a very odd service grounding configuration, with the primary grounding wire connected to a copper clamp on iron rebar sticking out of basement floor.

Not only does a piece of rebar sticking about a foot out of the basement floor appear to be a potential hazard, but the use of a copper clamp to connect to an iron bar screams of temporary grounding while the yard (which was basically dirt and weeds) is being sorted out.

I've inspected many new houses -- not many lately, being in the Detroit area -- but have not seen anything quite like this. Thoughts, anyone?
Attached Thumbnails
odd-grounding-copper-clamp-iron-rebar-sticking-out-basement-floor-pic-008_8_1.jpg   odd-grounding-copper-clamp-iron-rebar-sticking-out-basement-floor-pic-010_10_1.jpg  
Reply With Quote
Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/13/11, 9:52 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

Ufer?



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 8/13/11 at 9:55 PM..
Reply With Quote
  #3  
Old 8/13/11, 10:12 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

I'm aware of Ufer grounding connections, but the copper connector to iron and potentially hazardous rod sticking out of the floor seemed odd, for the reasons I mentioned.

Last edited by fbartlo; 8/13/11 at 10:19 PM..
Reply With Quote
  #4  
Old 8/13/11, 10:23 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

a number of bronze alloy clamps are designed for direct burial and suited for direct rebar contact/connection



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #5  
Old 8/13/11, 10:25 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

Do those bronze connectors look just like copper clamps, and are not such connections supposed to be buried or at least enclosed by some sort of panel if they are to be accessible?
Reply With Quote
  #6  
Old 8/13/11, 10:27 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

http://www.creia.org/files/public/gr...ode_locked.pdf
Reply With Quote
  #7  
Old 8/13/11, 11:23 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

Thanks for the link, Jeffrey. So my instincts were correct, after all. Maybe it is a temporary rig.
Reply With Quote
  #8  
Old 8/14/11, 9:11 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

Quote:
Originally Posted by fbartlo View Post
Thanks for the link, Jeffrey. So my instincts were correct, after all. Maybe it is a temporary rig.

Why would you think that it was a temporary connection to the CEE? Looks like a hazard if you fell on it, but most likely it's electrically code compliant.
Reply With Quote
  #9  
Old 8/14/11, 9:46 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

I see no reason to think that is temporary either. It matches the one pic in the link in Hansens article. As long as there is still 20' of rebar in the footing the top of the rebar could be cut off.
Reply With Quote
  #10  
Old 8/14/11, 11:46 AM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

What size is the wire? Looks to small to be a service ground.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #11  
Old 8/14/11, 12:36 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

Quote:
Originally Posted by rernst1 View Post
What size is the wire? Looks to small to be a service ground.

Could be, the OP doesn't mention the size of the service entrance conductors. For copper the minimum size would be #8 for a typical 100 amp service but that would require physical protection so my guess is that it's a #6 GEC which would be OK for a typical 150 amp service. A copper #4 is the largest GEC required to a CEE.
Reply With Quote
  #12  
Old 8/26/11, 4:41 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

Conductor was 6 gauge copper for 150A service. Based on the info in Jeff's link, the features that "felt" wrong were wrong, even if it is effective for electrical grounding purposes, which it did appear to be.
Reply With Quote
  #13  
Old 8/26/11, 4:58 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

Quote:
Originally Posted by fbartlo View Post
Conductor was 6 gauge copper for 150A service. Based on the info in Jeff's link, the features that "felt" wrong were wrong, even if it is effective for electrical grounding purposes, which it did appear to be.

Then it was properly sized.
Reply With Quote
Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/26/11, 8:08 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

What features are you saying are wrong?
Reply With Quote
  #15  
Old 8/26/11, 8:14 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Odd grounding with copper clamp on iron rebar sticking out of basement floor

Quote:
Originally Posted by Jim Port View Post
What features are you saying are wrong?
Good question. #6 Cu to a CEE for a typical 150 amp service would be code compliant.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
something else to chew on john bubber Structural Inspections 706 4/25/12 7:13 AM
Poly being applied to Basement walls dvalley Interior Inspections 40 11/24/09 10:49 PM
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural Inspections 75 7/21/08 5:25 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM


All times are GMT -4. The time now is 7:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts