Default Odd grounding question.

The electrical panel had no bonding and no ground connection (inside). Also with one exception there were zero ground wires in the panel. However ALL the circuits in the home tested that they were grounded.

Here's what I found... Each three wire did go to the panel. Blacks to breakers, whites to buss bar lugs... Their ground wires, were snipped short, reversed, and fastened to the panel at the entrance nuts. The copper service ground was on the side of the panel, and more or less tucked behind it. This then ran to an old copper water pipe that was jammed up against the gas line.

Would you guys give me some suggestions on wording a comment? On the surface this looks horrible to me, but I don't want to make a mountain out of a mole hill. (Of course if it is a mountain, I want to document it accurately.)
Attached Thumbnails
odd-grounding-question-dscn6175.jpg   odd-grounding-question-dscn6174.jpg   odd-grounding-question-dscn6172.jpg  



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #2  
Old 8/25/09, 2:13 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,040
Default Re: Odd grounding question.

Jeez... it would have been easier to do it right
Reply With Quote
  #3  
Old 8/25/09, 3:04 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,117
Default Re: Odd grounding question.

Improper connections of EGC's and GEC to panelboard. Recommend licensed and qualified electrician to repair.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 3:00 PM
Question about metal Building grounding sparksnmore Electrical Inspections 16 11/19/07 1:19 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 11:43 PM


All times are GMT -4. The time now is 6:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts