Default Old Fused Panel

Older Fused Panel.

Vintage panel within a Main Line Estate Home.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 5:35 PM..
Reply With Quote
  #2  
Old 11/5/06, 3:09 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Old Fused Panel

Pictures of the Home....

Built between 1900 and 1904

Interior of the home was original in almost every detail...



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 5:35 PM..
Reply With Quote
  #3  
Old 11/5/06, 3:37 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Old Fused Panel

Nice place Joe. Looks like they fused the neutrals. I did one last month with edison fuses, six of them. I thought they had six circuits at first, then I noticed three of the fuses were the neutrals. Three circuits for the whole house on #14 K&T, with 25 and 30 amp fuses.
Reply With Quote
  #4  
Old 11/5/06, 4:03 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Old Fused Panel

Quote:
Originally Posted by jhagarty
Pictures of the Home....
I'll take it! Send me the paperwork.
Reply With Quote
  #5  
Old 11/5/06, 4:04 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Old Fused Panel

Brian,

This was an Unusual Inspection.

Home is in excess of 8000 square feet. (!00 Amp Service / K&T Wire throughout).

I was on-site for the better part of the day with an Electrician, Roofer, Slater, HVAC Contractor, General Contractor, and several Carpenters.

Rewire of the home was Recommended.

Estimated costs will be in excess of $25,000 as part of the total renovation.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #6  
Old 11/5/06, 6:23 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Old Fused Panel

Quote:
Originally Posted by Speedy Petey
I'll take it! Send me the paperwork.
EWWWWW...I dont want no stinkin K & T home...thehehehe......I may know a few good electricians that can rewire it however...

NACHI project house...bring in ME,Greg,Brian and Peter and we shall REWIRE that sucker....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 11/5/06, 6:37 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Old Fused Panel

Quote:
Originally Posted by pabernathy

NACHI project house...bring in ME,Greg,Brian and Peter and we shall REWIRE that sucker....
Willing to do it at What Expense?



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #8  
Old 11/5/06, 6:57 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Old Fused Panel

Quote:
Originally Posted by jhagarty
Brian,

This was an Unusual Inspection.

Home is in excess of 8000 square feet. (!00 Amp Service / K&T Wire throughout).

I was on-site for the better part of the day with an Electrician, Roofer, Slater, HVAC Contractor, General Contractor, and several Carpenters.

Rewire of the home was Recommended.

Estimated costs will be in excess of $25,000 as part of the total renovation.
Joe, That is quite the panel, 100amps to a residence was a very big service back in that era, I love the panel, it is a work of art (OK so I have a twisted idea of art, but I love it).

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #9  
Old 11/5/06, 7:01 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Old Fused Panel

Quote:
Originally Posted by gbeaumont
Joe, That is quite the panel, 100amps to a residence was a very big service back in that era, I love the panel, it is a work of art (OK so I have a twisted idea of art, but I love it).

Regards

Gerry
That was my first reaction as well.

The architecture of this home was ahead of its time for the period.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #10  
Old 11/5/06, 7:04 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,254
Default Re: Old Fused Panel

Estimation for renovation is totaling $500,000 to $750,000 over the $1,000,000 price requested.

Considered a bargain in this area.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #11  
Old 11/6/06, 9:39 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Old Fused Panel

ahhhh...lol....( foot in mouth )...well I will come up for $ 46,000 and gutted.....not sure what the others want to get paid...thehehehe



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM