  #1  
Old 9/8/07, 12:47 PM
David A. Nice's Avatar
David A. Nice David A. Nice is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Wauwatosa, WI
Posts: 1,678
Question Old panel configuration for comments

A home built in the 50's has a panel configuration like pictured. A main beaker panel with a breaker for a sub panel that houses fuses to a dryer outlet. Main breaker panel also feeds panel to the rest of the house. The feed in that panel has 2 black leads connected the the feed from the main breaker panel to a single breaker panel that goes to an outlet for the washer.

Obviously it is a pretty old system and it's not likely that replacement breakers can be found plus it is only 70 amp service.

Comments?
Attached Thumbnails
old-panel-configuration-comments-configuration-web.jpg   old-panel-configuration-comments-tapped-web.jpg  



David Nice
National Certified Inspection Services, Inc.
Wauwatosa, WI

http://www.nationalcertified.com
414-979-6900
President WiNACHI
http://www.winachi.org
Wisconsin InterNACHI Chapter
414-979-6053
Reply With Quote
  #2  
Old 9/8/07, 2:27 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Old panel configuration for comments

Wow, you've got a lot going on here to include double taps at the main. I've also never seen those type of breakers. Who's the manufacturer?

Are the sub grounds bonded and neutrals floating?

I'd simply recommend a licensed Electrician to evaluate and estimate repairs to numerous panels.
Reply With Quote
  #3  
Old 9/8/07, 3:01 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: Old panel configuration for comments

Quote:
Originally Posted by dvalley
I'd simply recommend a licensed Electrician to evaluate and estimate repairs to numerous panels.
Ditto... too much going on, likely several things to 'fix'...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #4  
Old 9/8/07, 3:11 PM
David A. Nice's Avatar
David A. Nice David A. Nice is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Wauwatosa, WI
Posts: 1,678
Default Re: Old panel configuration for comments

Quote:
Originally Posted by mgault
Ditto... too much going on, likely several things to 'fix'...
I agree. With 70 amp and and all that going on I am recommending an evaluation to upgrade to at leat 100 amp. Most of the home still has onder 2 prong outlets so they'll be needing an electrician soon enough.



David Nice
National Certified Inspection Services, Inc.
Wauwatosa, WI

http://www.nationalcertified.com
414-979-6900
President WiNACHI
http://www.winachi.org
Wisconsin InterNACHI Chapter
414-979-6053
Reply With Quote
  #5  
Old 9/8/07, 9:22 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Old panel configuration for comments

The panel in the middle looks like Square D "XO" and the one on the right looks like it might be Frank Adams. Did you happen to note the brands?
Reply With Quote
  #6  
Old 9/8/07, 11:29 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Old panel configuration for comments

"Frank Adams" How do you come up with these things. You must have seen everything ever built. I should go down to the Edison Home Lab and take some pictures. Maybe I can stump you

Seriously I wish you could have come along when I was inspecting the rehab of the John Ringling "CaDZan" mansion in Sarasota. I saw a lot of 1920s and 30 stuff they were restoring. The elevator had the same controller they used in the movie "Hotel" and the silver dollar sized contacts were in just about as bad of shape. When they were done it looked like brand new. They had an engineer from Otis overseeing the restoration (and I imagine he brought a big bag of parts)
I was actually amazed at how well the electrical system held up. I did Ecos testiing (early SureTest type of thing) on the raceways and virtually all of them were less than 1 ohm under load.
Reply With Quote
  #7  
Old 9/8/07, 11:32 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Old panel configuration for comments

Frank Adams panels were very popular around here in the 50's as well. Still a lot of them out there.
Reply With Quote
  #8  
Old 9/8/07, 11:39 PM
Rollie Meyers Rollie Meyers is offline
New User
 
Join Date: Jul 2007
Posts: 32
Please Note: Rollie Meyers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Old panel configuration for comments

Those are "Multi Breaker" panels, a number of manufactures made them and they predate the Cutler - Hammer / Square D XO breakers.
Reply With Quote
  #9  
Old 9/9/07, 2:35 AM
David A. Nice's Avatar
David A. Nice David A. Nice is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Wauwatosa, WI
Posts: 1,678
Default Re: Old panel configuration for comments

Quote:
Originally Posted by Rollie Meyers
Those are "Multi Breaker" panels, a number of manufactures made them and they predate the Cutler - Hammer / Square D XO breakers.
That far right panel is also a Square D panel, in fact they are all Square D panels.



David Nice
National Certified Inspection Services, Inc.
Wauwatosa, WI

http://www.nationalcertified.com
414-979-6900
President WiNACHI
http://www.winachi.org
Wisconsin InterNACHI Chapter
414-979-6053

Last edited by dnice; 9/9/07 at 3:12 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 1:10 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts