Default Older Panel Concerns

Hey guys, will you give me a little help on this panel set-up. It's a 100 Amp Square D panel. The potential issues I see are:

  1. Double-tap on main
    1. The double-taps go to the panel on the right with a breaker for the AC. Since they go to a breaker is that okay?
  2. Double-taps on breakers
  3. Grounded conductor's (neutrals) on same fasteners?
  4. Grounded conductor from service panel is a bare copper conductor?
    1. Haven't seen that one before so wanted to make sure.
Anything else I'm missing?
Attached Thumbnails
older-panel-concerns-img_1257.jpg   older-panel-concerns-img_1260.jpg   older-panel-concerns-img_1259.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272

Last edited by krigler; 11/29/09 at 6:50 PM..
Reply With Quote
Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America)
  #2  
Old 11/29/09, 6:40 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Older Panel Concerns

The double tap on the main is wrong because its a double tap and the wire for the AC is that is double tapped is undersized now. Also, the neutrals and grounds should not be under the same terminal and the wires entering the panel should be in a protective chase.

I am not an electrical expert, but that's what I see. I am sure others will chime in. It looks like they need an electrcal upgrade.



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
  #3  
Old 11/29/09, 7:11 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Older Panel Concerns

Two-wire systems are indicative of older electrical systems. The electrical wiring systems that power the conveniences of modern life are hidden in walls and in panel boxes in basements. They are out of sight and out of mind. But that does not mean they are not overloaded and under severe stress.

Older electrical systems may show signs of deteriorating wire covering. Some systems may appear to be in good condition, may stress over the years may cause a weakness in the wiring that is not visible or noticeable.
Systems over 50 years old should be tested for safety by a licensed electrician.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #4  
Old 12/1/09, 8:02 PM
tmcsweeney tmcsweeney is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Buffalo, NY
Posts: 28
Default Re: Older Panel Concerns

The electrician took a short cut. While the wire is under sized for the ac from the double tap, it is protected. The double tap at that location is wrong. The electrician should have put in a sub panel wired correctly and would have been sufficient to move or add additional circuits. I agree with the other posts it should be written up.
Reply With Quote
  #5  
Old 12/1/09, 11:23 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Older Panel Concerns

The bare service neutral is a definite no-no. I saw a missing clamp fitting in the 3rd photo also. Lots of work for an electrician here.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Federal Pacific Question. lrollins Electrical Inspections 27 11/25/09 12:01 AM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
older homes with Mario Kyriacou, rcooke Canadian Inspectors 45 5/9/08 5:30 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:59 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts