Default One and Two Family Exemption from Flash Protection

1-82 Log #1651 NEC-P01


Action: Accept in Principle
(110.16)





__________________________________________________ _____________________________________________




Submitter:

Joe Tedesco Boston, MA





Panel Meeting Action: Accept in Principle




Revise text to read as follows:

110.16 Flash Protection. Switchboards, panelboards, industrial control panels, meter socket enclosures, and motor control centers that are in other than one- and two-family dwelling occupancies and are likely to require examination, adjustment, servicing, or maintenance while energized shall be field marked to warn qualified persons of potential electric arc flash hazards. The marking shall be located so as to be clearly visible to qualified persons before examination, adjustment, servicing, or maintenance of the equipment.


Panel Statement: The panel has revised the proposal to only include one- and two-family dwelling occupancies rather than all dwelling occupancies because one- and two-family dwellings provide a reasonable demarcation for occupancies where arc flash hazards may exist. The panel does not necessarily agree with all of the substantiation of the submitter.





Last edited by jtedesco1; 4/24/06 at 2:37 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 1:55 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts