If the main disconnect is located in the garage and that is the only panel present, do the ground wires and neutral wires have to be separate? This panel looks very sloppy to me the way the ground and neutral wires are run to the buss. Some are sharing the same lug. How would you write this in the report?
|
|
#2
|
||||
|
||||
|
Grounds can be ganged,
Neutrals cannot; they must terminate under their own individual terminal lug. - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#3
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
If this is the main then the two can land on the same bar.
What is do see wrong is the grounded (neutral) and equipment grounding conductors under the same screw Does anyone see the main bonding jumper? I don’t see anything that is bonding the panel enclosure to the grounded (neutral) conductor. |
|
#4
|
||||
|
||||
|
There's a green bonding screw...top right of the buss.
|
|
#5
|
||||
|
||||
|
This'll help...
- Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#6
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is the screw I have pointed to here the bonding screw?
|
|
#7
|
||||
|
||||
|
Mike,
It's the one right above the one you've identified... - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#8
|
||||
|
||||
|
Quote:
|
|
#9
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is what you call very sloppy? At the rist of sounding narcissistic mine are a bit neater but that looks fine to me.
I have to say, here in NY that method of terminating grounds and neutrals of the same circuit is generally accepted by inspectors and MANY quality electricians do it that way. I did for many years, but do not any more. We do NOT follow the NEC and I have had high level inspectors tell me it's fine. Take that for what it's worth. |
|
#10
|
|||
|
|||
|
Thanks for the help. So, this is alright? As long as there are not two neutral wires to one lug?
|
|
#11
|
||||
|
||||
|
Quote:
Document it. http://www.nachi.org/forum/attachmen...2&d=1180638925 http://www.nachi.org/forum/f19/electrician-signs-off-ganged-neutrals-now-17471/ tom P.S. Does anyone see a GEC? If it's at the Disconnect, why is there bonding here? Last edited by tdietrich1; 7/31/07 at 9:09 PM.. |
|
#12
|
||||
|
||||
|
Quote:
- Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector Last edited by mgault; 7/31/07 at 9:53 PM.. |
|
#13
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#14
|
||||
|
||||
|
Quote:
Incorrectly spoken; 'Neutrals not terminating beneath their own terminal lug' is the call out. They are not double lugged... Petey is correct, double lugged is different. - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#15
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |