  #1  
Old 4/19/06, 12:15 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,605
Default ongoing AFCI debate

Inspected a home the other day, Master suite, AFCI turns off every outlet in the bedroom, all lights in the bedroom, closets, and bath. but the GFCI's at the sinks in the bath were still on. Any thoughts to this long standing debate.
Reply With Quote
  #2  
Old 4/19/06, 12:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: ongoing AFCI debate

Not a problem.

AFCI protection is required at outlets of bedrooms only. The bathroom has its own requirements including dedicated, GFCI protected circuits. Having AFCI protection on additional circuits is okay, although not required.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 4/19/06, 12:57 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,221
Default Re: ongoing AFCI debate

Outlets in bedroom include lights and smoke detector circuit but most houses are not wired this way.
Reply With Quote
  #4  
Old 4/19/06, 2:10 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: ongoing AFCI debate

Did a home (2 years old) in which the AFCI did not function either at panel or in bedroom with SureTest. When I pulled the panel here is what I found. Oops! How did I forget that?

Last edited by dedwards; 5/3/07 at 6:34 PM..
Reply With Quote
  #5  
Old 4/19/06, 2:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: ongoing AFCI debate

Does that pink tag say "faulty AFCI?"



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 4/19/06, 2:40 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ongoing AFCI debate

Be careful when testing AFCI circuit with the Suretest tester.
There are some complications with that unit and it is not 100% accurate, which really means " when is it accurate?"

The UL website says the best way to test the AFCI circuit breaker is to use the test button that is on the circuit breaker itself. Until further info from UL, that is how I would test AFCIs for now.
Reply With Quote
  #7  
Old 4/19/06, 2:47 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: ongoing AFCI debate

Jeff,
Yeah, I had put that on prior to opening up the panel. I often tag things and take a photo so I have a record of what items I found discrepancies with. I later removed it due to finding the reason it didn't work. I did not only test it with the SureTest, I always check it with the built in test as well. I have also heard there have some problems with the SureTest regarding AFCIs. I have never experienced it but I am aware of it.
Reply With Quote
  #8  
Old 4/19/06, 5:10 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,605
Default Re: ongoing AFCI debate

Jeff, this is one large room no doorway seperating the sleeping area from bath area, also only one way into this room.
Reply With Quote
  #9  
Old 4/19/06, 5:36 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: ongoing AFCI debate

It depends on where/how circuits were run. This has been posted before, but it makes things very clear.
Attached Thumbnails
ongoing-afci-debate-1014150850_2.gif  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 4/19/06, 6:21 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: ongoing AFCI debate

Question:

Smoke detectors are wired together (with battery backup) so if one goes off they all go off. Does this mean they are on their own AFCI circuit?

Okay I think that's true after looking at Jeff's picture again.
Reply With Quote
  #11  
Old 4/19/06, 6:32 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: ongoing AFCI debate

1) You really can't test AFCIs in an occupied house anyway unless you're prepared to turn off Granny's iron lung.

2) Unlike Doug's photo, I never stick my fingers inside a panel box for any reason. It's a rule I live by.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 4/19/06, 6:52 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: ongoing AFCI debate

Only on rare occasions do I venture my digits into a panel and this one was a very clean, neat and picture of professionalism with that one exception. I have been certified for Residential Electrical Wiring and take ordinary safety precautions. I had to touch the wire anyhow since once I removed the cover the bitter end of the wire popped out and was hanging over the bottom edge. I couldn't hardly leave it that way. By all means if you are not comfortable working around electricity then do not do anything that would compromise you. I respect it but I am also very comfortable around it.

Last edited by dedwards; 4/19/06 at 8:45 PM..
Reply With Quote
  #13  
Old 4/20/06, 6:38 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: ongoing AFCI debate

I don't test AFCI circuits for two reasons: (1) They are in the electric panel and I don't stick my fingers in the electric panel, (2) I'm not prepared to run around, first, to see what interesting items might be in all those the bedrooms, and second, to reset/reprogram those interesting items in all those bedrooms.

I simply include a lot of information about AFCIs in my report. Note that if you see an AFCI with a blue test button, you should report it as a possible recall. I believe that all recalled AFCI breakers have blue test buttons, but not all AFCIs with blue test buttons have been recalled.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 4/20/06, 9:19 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,605
Default Re: ongoing AFCI debate

for the record this was new construction,unoccupied, but my main point was that this a single room master suite, primarily the bedroom(no doors seperating the bath area). which goes back to the old debate, is a closet part of the bedroom, well if this suite is all one room then the outlets at the sink should have gone off with the AFCI.
Just a thought.
Reply With Quote
  #15  
Old 4/20/06, 11:51 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: ongoing AFCI debate

Quote:
Originally Posted by bgraham
well if this suite is all one room then the outlets at the sink should have gone off with the AFCI.
Even if you're thinking was right, they would require their own AFCI breaker as they must be dedicated to the bathroom(s) only.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Controversy rcooke Electrical 11 9/10/07 3:14 PM
AFCI's Explained by Mike Holt & Eaton Engineer pabernathy Electrical 19 2/15/07 1:05 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 12:46 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts