Quote:
Originally Posted by jtedesco1
Thanks Paul for trying and Todd, fancy seeing you here?
Right back at ya Joe.
Reply With Quote
  #17  
Old 7/7/06, 11:50 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Online Code Check- Reference

Worth Reliving......For the NEWBIES !



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #18  
Old 7/7/06, 3:15 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Online Code Check- Reference

Good link Paul, that I reference occasionally too. Only down side is limited table values. Many (including me) highly recommend an HI at least have the basic CodeCheck reference with them on an inspection ... very handy ... http://www.taunton.com/store/pages/070680.asp

P.S. I also think Dan was right on the money, and should have asked the experts to put things in writing (assuming the one noted as a problem with 30 Amp wire and a 40 Amp Minimum Ampacity wasn't #10 Cu THHN in conduit which is good for 40A).



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #19  
Old 7/7/06, 5:09 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Online Code Check- Reference

Hey Paul, how current is that edition of Code Check? Are the referenced codes current?
Reply With Quote
  #20  
Old 7/8/06, 2:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Online Code Check- Reference

Not sure Brian.....I will look it over



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #21  
Old 7/8/06, 2:21 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Online Code Check- Reference

Quote:
Originally Posted by pabernathy
Not sure Brian.....I will look it over
Out of date, I know as I used to have that one.
Good reference but be careful.
Reply With Quote
  #22  
Old 7/8/06, 2:24 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Online Code Check- Reference

Code is not dependant upon which is current..........................

Code is dependent upon which is current in your market area....



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #23  
Old 7/8/06, 2:32 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Online Code Check- Reference

Quote:
Originally Posted by jhagarty
Code is not dependant upon which is current..........................

Code is dependent upon which is current in your market area....

Ok Joe then where is the aforementioned code check currently current?
Reply With Quote
  #24  
Old 7/8/06, 2:38 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Online Code Check- Reference

This may help your search
Reply With Quote
  #25  
Old 7/8/06, 9:39 AM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Online Code Check- Reference

30 amp wire:
I could put a #12awg on a 60 amp breaker using the below reference.
440.22

(A) Rating or Setting for Individual Motor-

Compressor.
The motor-compressor branch-circuit shortcircuit
and ground-fault protective device shall be capable
of carrying the starting current of the motor. A protective
device having a rating or setting not exceeding 175 percent
of the motor-compressor rated-load current or branchcircuit
selection current, whichever is greater, shall be permitted,
provided that, where the protection specified is not
sufficient for the starting current of the motor, the rating or
setting shall be permitted to be increased but shall not exceed
225 percent of the motor rated-load current or branchcircuit
selection current, whichever is greater.



Exception: The rating of the branch-circuit short-circuit

and ground-fault protective device shall not be required to
be less than 15 amperes.

Reply With Quote
  #26  
Old 7/8/06, 10:35 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Online Code Check- Reference

Was just information al reference for the usual HOME INSPECTOR...not for electricians...lol.....

Yep...Mike....somewhere in the boards I did a long explanation of that and gave some calcs samples as well......not sure where I stuck them now...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #27  
Old 7/8/06, 10:45 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Online Code Check- Reference

General Background Electric Shock(GFCI) Grounding Lightning Rough Wiring Fixtures/Appliances Circuit Breakers/Panels Alternate Energy Calculations Sizing Feeders Wiring Systems Earthquakes Hurricanes Environmental 2-3 Prong Grounding Aluminum Wire History of Wiring Swimming Pool Knob & Tube Q_A_Electric
Generators


BackgroundElectric ShocksGroundingBack to Table of Contents





Lightning




Rough Wiring


Fixtures, Appliances, EquipmentCircuit BreakersAlternative Energy Sources Calculations Wiring SystemsAluminum Conductors Electro Magnetic Fields and Health



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #28  
Old 7/8/06, 12:16 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Online Code Check- Reference

Quote:
Originally Posted by Mike Parks
30 amp wire:
I could put a #12awg on a 60 amp breaker using the below reference ... 440.22
The issue Dan posted that I commented on was an installation that did not appear to comply with the equipment label. He described it as a 30A wire when the listed minimum circuit ampacity on the nameplate was 40A.

Quote:
Originally Posted by dbowers
Minimum Ampacity 40 Amps & Maximum HVACR Breaker Size - 50 Amp
AND the wiring inside at the panel box was a 30 Amp wire.
Normally an HI will think of #10 = 30A ... but if it's typical #10 Cu wire fished through conduit (not a cable) for an AC circuit it would have an ampacity of 40A (temperature derating and voltage drop aside).

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #29  
Old 11/8/06, 7:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Online Code Check- Reference

Bump



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #30  
Old 11/8/06, 7:58 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Online Code Check- Reference

Thx for the bump.

I don't plan on using this too much, since it address 2000 IRC and at best 2002 NEC, but it's nice to have a simple to decide I like it. I might run out and get the book for some nice relaxing reading. Relaxing compared to the 2006 IRC I've been thumbing through for the last week.

What a geek!

tom
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
NFPA 70- 2005 National Electric Code Online homebild Electrical Inspections 1 6/27/07 8:24 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical Inspections 0 6/16/06 3:10 PM
Code Check books msaxton Inspection Hardware, Software & Publications 4 3/19/06 5:14 PM


All times are GMT -4. The time now is 3:46 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts