International Association of Certified Home Inspectors
|
|||||||
| Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera. |
![]() |
|
|
LinkBack | Thread Tools |
|
#1
|
|||
|
|||
|
I snapped this pic a couple of weeks ago and recommended the open j-box have a cover installed. The seller's response is "there are no splices, so it does not need a cover. The wires pass through the box into the conduit."
The red and white THHN/THWN wires need to be protected, right? So if there are no splices, than the box needs a cover, AND there needs to be conduit extended from the box to where the red and white wire terminate. Is that correct? |
|
#2
|
||||
|
||||
|
The box is a 4-11/16" square j-box. A blank cover might cost $1. The wires in question do need protection by a raceway of some sort.
|
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
You are correct. Any box or conduit body that contains individual conductors, splices or not, must have a cover. I can dig you up the code citation if you want that.
|
|
#4
|
|||
|
|||
|
Thanks guys,
I knew that I was right, but it is nice to get confirmation. Why the heck anyone would dicker over this is beyond me. |
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Someone added what looks like an 8/3NM cable to a conduit with TW(?) conductors already in it. Likely overfilling the conduit to boot. |
|
#7
|
||||
|
||||
|
Here is just one that marc was refering to: (C) Covers. All pull boxes, junction boxes, and conduit bodies shall be provided with covers compatible with the box or conduit body construction and suitable for the conditions of use. Where metal covers are used, they shall comply with the grounding requirements of 250.110. An extension from the cover of an exposed box shall comply with 314.22, Exception. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#8
|
||||
|
||||
|
I find open j-boxes all the time. I have a standard blurb for it (I think it came from RR's great collection).
Junction boxes with missing cover plates were observed ( ). Open junction boxes can be a fire hazard and could be lethal to small creatures (and large creatures, too) that may come in contact with the wiring. "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#9
|
|||
|
|||
|
BTW, could you establish the source of the moisture that's corroding that box? --- looks like it might be entering the box via the conduit.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| ? possible reasons for crawlspace mitigation | jeubank | General Inspection Discussion | 11 | 2/17/09 4:57 PM |
| Horizontal furnace in the foundation crawlspace | kswift | HVAC | 43 | 7/24/06 10:26 PM |
| Crawlspace questions?? | dmacy | Structural | 12 | 3/9/06 10:12 PM |