Default open ground on 3 garage receptacles

Out of all the receptacles in the house I Inspected,
I found 3 receptacles in the garage that my Tester said
were an open ground.....the home owner said that they
have been that way for 10years and they never had a problem.
they were three prong receptacles . Is this a big issue ?

David
Pyramid-Home-Inspections
Reply With Quote
  #2  
Old 10/27/06, 6:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,441
Default Re: open ground on 3 garage receptacles

Yes. It is.

Defer to a qualified electrician for evaluation and repair.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 10/27/06, 6:40 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 20,882
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by dnasser
.....the home owner said that they
have been that way for 10years and they never had a problem.
they were three prong receptacles . Is this a big issue ?......
Yes it's a big problem. Just report your findings and move on. Home owner's often claim to have had no problem with a reported issue. it's still an area of concern for the buyer. He's the one who has to decide how important it is and if it will affect his offer to purchase.

Last edited by mlarson; 10/28/06 at 6:28 PM..
Reply With Quote
  #4  
Old 10/27/06, 7:17 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by dnasser
the home owner said that they
have been that way for 10years and they never had a problem.
An absolutely classic reply to being told there is a problem.
I usually have some cute reply ready for them.
I will say something like, "Yeah, and your house hasn't burned down yet either, but it only has to happen once."
Reply With Quote
  #5  
Old 10/27/06, 7:19 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,346
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by dnasser
the home owner said that they
have been that way for 10years and they never had a problem.
Mount St. Helens was like that for a lot longer than 10 years and was never a problem...until it was a problem.

Yup, it's a problem.



____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #6  
Old 10/27/06, 8:00 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 14,025
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by lkage
Mount St. Helens was like that for a lot longer than 10 years and was never a problem...until it was a problem.

Yup, it's a problem.
Isn't that the God's honest truth?

Marcel



http://www.themainehomeinspector.com/
Serving all of Kennebec County and Central Maine
Cyr Home and Commercial Property Inspections

IAC2 Certified
http://co.nachi.org/inachiawards
Inachi 2009 US Member of the Year




Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #7  
Old 10/27/06, 9:05 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 3,106
Send a message via AIM to sstanczyk
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by dnasser
Out of all the receptacles in the house I Inspected,
I found 3 receptacles in the garage that my Tester said
were an open ground.....the home owner said that they
have been that way for 10years and they never had a problem.
they were three prong receptacles . Is this a big issue ?

David
Pyramid-Home-Inspections
Is the main panel in the garage?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #8  
Old 10/27/06, 9:14 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: open ground on 3 garage receptacles

Being a garage I ask this.... are they GFCI protected and is the house old?

Meaning, that the electrical codes allow for three prong outlets 'downstream' of GFCI protection(either a breaker or a GFCI receptacle). If so, then the 'issue' I would have is, why aren't those receptacles identified "GFCI protected" and "No Equipment Ground Present".

Just thinking out loud...

tom
Reply With Quote
  #9  
Old 10/28/06, 12:25 AM
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 320
Default Re: open ground on 3 garage receptacles

no....its the rear of house
Reply With Quote
  #10  
Old 10/28/06, 5:47 AM
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,570
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by tdietrich1
Being a garage I ask this.... are they GFCI protected and is the house old?

Meaning, that the electrical codes allow for three prong outlets 'downstream' of GFCI protection(either a breaker or a GFCI receptacle). If so, then the 'issue' I would have is, why aren't those receptacles identified "GFCI protected" and "No Equipment Ground Present".

Just thinking out loud...

tom
Not my job identify the fault write it up and move on. Read the SOP .
I only have about 3 hours to do inspection write report and be gone.
Roy Cooke



Roy Cooke.RHI.
http://royshomeinspection.com/
Questions 613-475-1144
Roycooke@sympatico.ca

" A life spent making mistakes is not only more honorable but more useful
than a life spent doing nothing." George Bernard Shaw
Reply With Quote
  #11  
Old 10/28/06, 9:46 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by rcooke
Not my job identify the fault write it up and move on. Read the SOP .
I only have about 3 hours to do inspection write report and be gone.
Roy Cooke
Understood, I didn't think there was a fault, just a simple 'issue' that effects the expectation of what should and shouldn't be in a garage. There might be an open ground for a good valid reason.

tom
Reply With Quote
  #12  
Old 10/28/06, 9:57 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,441
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by sstanczyk
Is the main panel in the garage?
I'm curious as to why you asked this Stephen.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 10/28/06, 12:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: open ground on 3 garage receptacles

ANY ungrounded plug with a 3 hole receptacle should be in your report and defered. Regardless of the debate that even (2 hole plugs are grounded in many eyes )......the EGC is used in a different way......

Lack of those having a EGC that shows up needs review.....the EC will look inside and determine the problems...might be as simple as a EGC that came loose at the receptacle BEFORE those 3.....you never know but the EC will find it....I ALWAYS find it....

so........as Jeff stated correctly ( yet again... ) defer it and have it looked at......

I love what Speedy said.....MOST EXCELLENT.....man i wish I had a $1 for everytime I have heard that statement.....about been that way since the house was built and so on......classic home owners and RE's response...lol....Nice Speedy.........you nailed it !



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #14  
Old 10/30/06, 4:17 PM
Michael Martin Michael Martin is offline
New User
 
Join Date: May 2005
Location: Cleveland, Ohio
Posts: 24
Please Note: Michael Martin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: open ground on 3 garage receptacles

Quote:
Originally Posted by pabernathy
ANY ungrounded plug with a 3 hole receptacle should be in your report and defered.
Even if it's marked both "GFCI protected" and "no equipment ground"? If so, why?
Reply With Quote
  #15  
Old 10/30/06, 5:53 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: open ground on 3 garage receptacles

oh stop..lol............we are talking generals here...not a system that has been protected by GFCI.....we are speaking to HI's on finding 3 hole plugs in a 2 wire system ( ungrounded ).......they know about the GFCI Protected and No Equipment Ground... ( that info is on the basic electrical intro exam )

He stated they were not labeled as such

Quote:
Meaning, that the electrical codes allow for three prong outlets 'downstream' of GFCI protection(either a breaker or a GFCI receptacle). If so, then the 'issue' I would have is, why aren't those receptacles identified "GFCI protected" and "No Equipment Ground Present
So since the LACK of 2 prong plugs........or statement about a ungrounded systems.......then any 3 hole plug NOT LABELED....and not working in a grounded system house ( excluding the argument the neutral " grounded" conductors is considered grounding )....it should be defered....

Would you NOT defer them....hell any 3 prong receptacle in a dwelling that gives a reading of No Ground that is NOT labeled should be defered and let the CHIPS go where they may....I would not be worried about an electricians comments on this...safety first should be the HI's concern.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 7:57 AM
Installing GFCI in garage with no ground cyezza Electrical 53 11/30/07 5:05 PM
Bedroom Door leading to garage jberthiaume Interior 10 4/21/07 6:17 AM
Open attic access from garage jveivia Interior 13 7/26/06 12:01 PM
Open Ground tneumann Electrical 6 3/11/06 5:11 AM


All times are GMT -4. The time now is 4:29 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts