Default Open Neutral ??

Did an H.I. on a condo today and on two outlets that both worked off of different switches, the outlets tested as having an open neutral with their corresonding switches in the off position. When in the on position, it tested okay. Haven't had this occur before. Can anyone offer an explanation as to why this occurred? Thanks!



Patrick Coulter
Cross County Inspection Services, LLC
(443) 266-7544
Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #2  
Old 8/12/09, 6:39 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Open Neutral ??

The switch improperly switches the Neutral (grounded) rather than the Hot (ungrounded) leg.
Quote:
2006 IRC E3901.8 Grounded conductors. Switches or circuit breakers shall not disconnect the grounded conductor of a circuit except where the switch or circuit breaker simultaneously disconnects all conductors of the circuit.

Commentary: Switching the grounded conductor of a two-wire circuit will turn the load on and off, but a safety hazard is created. When someone is working on the wiring in a lighting outlet or on a luminaire, the ungrounded or hot conductor must be de-energized when the switch is off.
Reply With Quote
  #3  
Old 8/12/09, 6:58 PM
Patrick Coulter Patrick Coulter is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Clarksville, MD
Posts: 186
Default Re: Open Neutral ??

Quote:
Originally Posted by mboyett View Post
The switch improperly switches the Neutral (grounded) rather than the Hot (ungrounded) leg.
Thanks for the info! Very helpful and much appreciated!



Patrick Coulter
Cross County Inspection Services, LLC
(443) 266-7544
Reply With Quote
  #4  
Old 8/12/09, 7:02 PM
Tom Horne Tom Horne is offline
New User
 
Join Date: Aug 2009
Posts: 12
Please Note: Tom Horne is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open Neutral ??

Installing the switch in the wrong side of the line is a common mistake with new electrical workers. I don't know if the use of contact testers is considered in scope in your industry But even a non contact tester should show voltage present at both terminals of the switch when the switch is in the on position. If the only time you detect voltage is when the switch is open then the switch is installed in the wrong side of the line.
Reply With Quote
  #5  
Old 8/12/09, 8:41 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Open Neutral ??

Sad to say that in most all cases with the HI. they are limited to visual inspection and can't technically remove the cover on the switches to get to the terminals. With that said many will argue that opening a panel enclosure is beyond their scope. however, the SOP used by HI's stipulates a visual inspection. When it comes to the panel they are too look inside and not insert anything into the panel and do a visual inspection.

Take a few minutes Tom and check out their SOP requirements on the left side of the screen. You will be surprised how they are limited in their allowances but are expected to see everything.....sad to say they are very restricted.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Hot on Neutral, With Hot Open jgromkoski Electrical Inspections 1 5/3/09 11:16 PM
Open Neutral & Open Hot fmagdefrau Electrical Inspections 12 9/18/08 6:04 PM
How do you write up an open neutral mnahrgang Electrical Inspections 7 8/4/08 8:08 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 9:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts