Default Open Neutral & Open Hot

Today was the first time my "Sure-Test" ever gave me these readings. Can someone please explain to me what they mean and give advice on how to report these findings. Also the Open Hot Sparked when I un-plugged the garbage disposal to test outlet. Thanks

Frank



Frank Magdefrau
DeSoto Home Inspection Services
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
Reply With Quote
  #2  
Old 9/17/08, 7:21 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open Neutral & Open Hot

Open hot at the disposal receptacle would make perfect sense if the switch was off.
Reply With Quote
  #3  
Old 9/17/08, 7:33 PM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 240
Default Re: Open Neutral & Open Hot

Basically open hot means the hot is not connected open neutral means the neutral is not connected. If there has been new receptacels installed recently the wires may have broke when they were stuffed back into the box. Pulling the outlet that tested bad you may find the problem or if the receptacles are wired in series it may be the one feeding it. There are other possibilities but those are the most common ones I've seen when doing repairs.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com

Last edited by mjones6; 9/17/08 at 7:42 PM..
Reply With Quote
  #4  
Old 9/17/08, 7:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Open Neutral & Open Hot

What kind of SureTest were you using that gave you these indications? An "open-hot" and an "open-neutral" will give the same reading on the 61-165 - nothing, or no reading on the display.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 9/17/08, 7:48 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open Neutral & Open Hot

Quote:
Originally Posted by mjones6 View Post
Basically open hot means the hot is not connected open neutral means the neutral is not connected. If there has been new receptacels installed recently the wires may have broke when they were stuffed back into the box. Pulling the outlet that tested bad you may find the problem or if the receptacles are wired in series it may be the one feeding it. There are other possibilities but those are the most common ones I've seen when doing repairs.

Bounce this one around
How about if they wired they neutral to the switch , instead of the hot.
Reply With Quote
  #6  
Old 9/17/08, 7:48 PM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 240
Default Re: Open Neutral & Open Hot

Ana to report 'em I would give a location and picture, State receptacel has a open hot. Recommend a qualifed electrician make repairs. Shock and fire hazard.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
  #7  
Old 9/17/08, 8:01 PM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 240
Default Re: Open Neutral & Open Hot

Quote:
Originally Posted by relliott View Post
Bounce this one around
How about if they wired they neutral to the switch , instead of the hot.
That's easy to fix, just turn the switch on.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
  #8  
Old 9/17/08, 8:05 PM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 240
Default Re: Open Neutral & Open Hot

When ever I have those type reading on an inspection I try to give the buyer 1 possibility of what might be the cause and write 'er up.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
  #9  
Old 9/17/08, 10:38 PM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 2,343
Default Re: Open Neutral & Open Hot

The upper socket at the disposal inspected correct wiring the lower socket sparked and tested open hot.



Frank Magdefrau
DeSoto Home Inspection Services
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
Reply With Quote
  #10  
Old 9/17/08, 10:39 PM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 2,343
Default Re: Open Neutral & Open Hot

Quote:
Originally Posted by jpope View Post
What kind of SureTest were you using that gave you these indications? An "open-hot" and an "open-neutral" will give the same reading on the 61-165 - nothing, or no reading on the display.
http://www.professionalequipment.com...rcuit-testers/



Frank Magdefrau
DeSoto Home Inspection Services
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
Reply With Quote
  #11  
Old 9/17/08, 10:47 PM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 2,343
Default Re: Open Neutral & Open Hot

Quote:
Originally Posted by Marc D. Shunk View Post
Open hot at the disposal receptacle would make perfect sense if the switch was off.
Not if it sparked and the other socket tested correct wiring.



Frank Magdefrau
DeSoto Home Inspection Services
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
Reply With Quote
  #12  
Old 9/18/08, 1:01 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open Neutral & Open Hot

Do Not Switch Neutrals see NEC 404.2 Switch Connections
Reply With Quote
  #13  
Old 9/18/08, 7:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Open Neutral & Open Hot

Quote:
Originally Posted by fmagdefrau View Post
Not if it sparked and the other socket tested correct wiring.
Certainly you're not trying to say that there are no other reasons why this would occur?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
How do you write up an open neutral mnahrgang Electrical 7 8/4/08 9:08 PM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
Metal Rigid or PVC Rigid what is code bpotts Electrical 5 12/4/06 3:40 PM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical 1 4/22/06 11:19 AM


All times are GMT -4. The time now is 4:02 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts