#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
If you haven't started yet you could put 20' or more of #4 (or larger) rebar in the footer. Use a concrete listed clamp to attach a 250.66 sized conductor as your GEC. (typically a #4 solid). Attach this with a lug to building steel and a listed clamp to the piping system to complete the system
|
|
#3
|
|||
|
|||
|
(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (½ in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means. Just some additional code verbage for ya.... Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Texas Atty. General Renders Opinion about Liability Insurance | bthompson1 | Legislation, Licensing & Legal Issues for Inspectors | 45 | 12/20/07 11:57 PM |
| Bath exhaust fan opinion | rgiglio | Plumbing Inspections | 6 | 3/16/07 3:06 PM |
| Your opinion needed | jonofrey | Exterior Inspections | 24 | 2/1/07 12:10 AM |
| Volunteer home inspectors needed to help elderly/disabled. | gromicko | Miscellaneous Discussion for Inspectors | 1 | 11/13/06 7:33 AM |