Should the romex have run in conduit or is this ok ?
|
| Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Romex (NMC) does not belong inside conduit - except for short runs where it may need protection.
This lighting should have been installed using conduit such as EMT, not NMC. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
If that is NM-B it should not have been installed outside, regardless of conduit or not.
If it is UF cable it is approved for use outside. |
|
#4
|
||||
|
||||
|
thanks
|
|
#5
|
||||
|
||||
|
Section 334.10(A)(1) of the NEC states that Type NM cable shall be permitted for use in "normally dry locations." Article 100 of the NEC defines a dry location as:
Location, Dry. A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction. http://www.ul.com/global/eng/pages/o.../flooding/nmb/ http://www.unitedcopper.com/specs/wire/NMB_sheet.pdf |
|
#6
|
|||
|
|||
|
That's how I see it, too.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#7
|
||||
|
||||
|
I say it may or may not be approved for outdoor use and we cannot determine because the cable has been painted. It should be evaluated by an electrician.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#8
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Joe,
I do not know your SOP. UF cable is stiffer than NM-B. Often times you can roll the conductors inside the sheath of NM were as the UF has a solid fill and will not have any movement. |
|
#9
|
|||
|
|||
|
All technically correct, but I probably would not write it up because of the type of structure and the location (apparently out of reach) of the cable. After all, all they have to do is to put a piece of plywood over the bottom of the soffit and 'presto' the area is now enclosed just like any other wall or ceiling.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#10
|
||||
|
||||
|
Quote:
Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some coldstorage warehouses. So with that said it is a "Code" violation. now, understanding that code is code and safety is safety. We have to take into account just how unsafe is it to the condition of the dwelling. If the NM Cable is outside of reach that would technically put it outside of the rhelm of physical damage. The HI could recommend it be monitored on a regular basis for any exterior damage, future degrading effects and possibly simply note it and move on. The fix is simple. The HI who is observing the condition has to go with the feeling they have at the time of the inspection. As a municipal inspector I would fail it in a heartbeat so it would never make to the point the HI has to be concerned but alas this is probably a DIY installation so with that said...do you want to know what I would have put in my report? I would have noted it as a potential issue and if their are other things in the electrical rhelm that need to be addressed; i would most certainly put it on my report and let them choose to let it go or correct it with the other issues. The art of elevating something to a concern lies within the actual inspector doing the inspection. If you find many issues then this is simply another one that should be addressed, if it was the only concern in the entire inspection I would mention it and suggest they monitor it and move on with my inspection. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Make up air ducting question | jnelson | Inspecting HVAC Systems | 16 | 2/7/06 8:22 AM |
| Receptacles Mounted on Covers | jtedesco1 | Electrical Inspections | 1 | 2/5/06 1:13 PM |
| Answer to a common question about GFCI's | jtedesco1 | Electrical Inspections | 4 | 1/12/06 10:29 PM |