Default Outdoor spas, pools and the bonding of the deck.

I moved over here because we were hijacking another thread.

Paul, to answer the question about a spa on a patio (AKA lanai), Florida IAEA is leaning toward saying that if you drop a packaged spa on a paved surface it needs to have a bonding grid embedded in it. For something that has really been around for about 4 years I am not sure why they are just starting to look at it but that is sure how it reads.
I suppose if you built wood/plastic deck around the tub it would not need a bonding grid in the concrete but I haven't actually heard this.
The IAEI boys have also received a letter from NFPA that says the regular 6 or 8 ga steel welded wire is not "bars" so it can't be used for establishing the grid. There are some strange things coming from NFPA on this.
Reply With Quote
  #2  
Old 1/30/07, 2:34 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outdoor spas, pools and the bonding of the deck.

Paul I am taking you last question over here. In part II they are saying "permanent pool" as opposed to "storable pool". If the equipment in your spa was labelled "storable pool" I could see how you could duck part II.
Reply With Quote
  #3  
Old 1/30/07, 2:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

Greg,

Thanks for moving it.....see thats the thing with the NEC.

Personally I feel the GRID issue applies to "permanent" installed pools, outdoor spas and so on....not portable and usually WOOD cased self containted spa units.

Do you have any idea of any changes in verbage in the 2008 as I have not looked at it....

I agree 100% with the gradiant bonding as it pertains to 680.43 but I think we could have other issues when you tie a potential GRID of lets say a pool system and then have a patio where you install a portable spa which is GFCI protected for the most part ( we hope anyway )


Anyway take my SPA on my deck....it is all wood, wood bottom and all piping within is plastic except the motors which I bonded each together with a # 8 AWG to the control metal circuit case...bonding all parts together but I think it would be better served to stop their....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 1/30/07, 2:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

Quote:
Originally Posted by Greg Fretwell
Florida IAEA is leaning toward saying that if you drop a packaged spa on a paved surface it needs to have a bonding grid embedded in it. For something that has really been around for about 4 years I am not sure why they are just starting to look at it but that is sure how it reads.
My question is are they considering it permenant......as thats how I read the grid requirement and involving the rebar and so on associated with it, now i can see that on a poured built in hot tub or spa situation but feel it may simply not apply to a portable DROP down unit....atleast how it is written in the verbage I am reading.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 1/30/07, 3:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

Quote:
Originally Posted by Greg Fretwell
Paul I am taking you last question over here. In part II they are saying "permanent pool" as opposed to "storable pool". If the equipment in your spa was labelled "storable pool" I could see how you could duck part II.
i think part III refers to storage pools, I believe part II applies to the general requirement and in regards to the grid but I think this is where the problem lies.....most normal spas ( and I own a spa company : Virginia Water Systems..my brother runs it and business SUCKS....nice spas however...PDC Spa's are nice units ) and they are all wood cased and fiberglass inside with plastic plumbing pipes....

But I totally agree 100% if the spa is custom built and had steel within it...but i think it is not correct for florida to demand portable spa and hot tub units on a patio to have the grid under it..atleast how it is written to me.

hey fella...i am not saying I am right....just how i read it..but I also hear voices as well...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 1/30/07, 3:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

Ok...I am rambling on this one...but also lets take the concept of a portable spa placed on pavers as suggested.

Why would a Equipotential plane be needed here, what are you going to actually bond the proposed grid to....the EGC for the spa itself....i hope not..lol

So I think with most outdoor spas..unless BUILD in with rebar and so on like a pool it is probably a MOOT point to get into grids and so on.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 1/30/07, 7:30 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outdoor spas, pools and the bonding of the deck.

The problem is "portable spa" is not addressed in the NEC at all. There are indoor spas and outdoor spas. From a practical sense what they are really concerned with is a difference in potential between the water and the deck. A plastic tub in a wood case might actually make this worse. If you had one foot in the spa and one on the deck or you were standing on the wet deck, and reached back in the spa to get something or help someone get out, you can see the problem.

This came up a couple days ago when one of the BOs that hang out on the Fl IAEI BB pointed it out. The way it reads there is no relief for a portable spa.
This would get caught when they called for the inspection of the 50a receptacle. I suppose if you don't want to do this you should say it is a plug for a big pressure washer and hope you neighbor doesn't rat you out.
Reply With Quote
  #8  
Old 1/30/07, 11:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

I think in my view it is addressed. The issue with the bonding grid refers majority with steel rebar and permanant installed pools and spa's and not directly with portable spa's which I feel Part IV deals more with.

Now I am not saying portable in the sense of a cord in all cases.....A 50A disconnected hot tub is still not permanant in my opinion but again based on part 1 and 2...it is not a issue of steel rebar in the construction either.

Very hard in my mind to require a bonding grid under a hot tub on a patio unless it is within 5' of a pool lets say......and require it to have a bonding grid as a statement.

Like I said...I do quite a few spa installs around here as part of the company I own with my brother and as a EC and they are all wooden cased or simulated wood and plastic. The only bonding taking place is between the motors and to the metal enclosed control panel......strictly for bonding.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 1/31/07, 12:31 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outdoor spas, pools and the bonding of the deck.

The rebar in the pool has nothing to do with the grid. Until the TIA you had to put a copper grid under a fiberglass pool or vinyl liner pool. You still need to bond the paving.
This is really going to get confusing when they start trying to sort out all of the variables. In a concrete pool with a concrete deck it is easy to understand, pavers added a level of confusion but when plastic gets thrown into the mix it just gets silly. I understand the 2008 draft has us bonding DIRT!
I bumped the IAEI discussion about the portable spa again. They were still arguing about steel mesh when the spa thing came up and it went undisputed. These are CBOs in several florida jurisdictions speaking.
Reply With Quote
  #10  
Old 1/31/07, 12:41 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

I hear ya Greg.......one good thing about VA is by the time we ADOPT something it has been BEAT to all HELL before we have to observe it.

I agree but the intent of the GRID was to comply with actual bonding to the metal rebar in the construction of a permanent installed pool as the NEC tried to define it. Just not sure it really applies to typical stand alone spa's and hot tubs today...I see it is debated also over on Mike's site and they kinda jump back and forth....the issue of the pool or spa and so on being BUILT into the concrete and so on is seeming to take the lead on IF their needs to be a GRID for a spa......if stand alone unit chances are it would not be a bonding to the grid issue....the way I see it.....but alas you are right in who knows where it really will go.....Gotta love the CODE...

Most of the hot tubs we install have no metal parts on them at all....except for the case to the motors which are bonded according to the requirement but nothing else exposed that would need bonding. I find that article 680 in regards to part 1 and 2 more defined to BUILD in style units......probably a wrong way to look at it but based on the typical construction of a hot tub or spa unit it would be a decent statement.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 1/31/07 at 12:44 AM..
Reply With Quote
  #11  
Old 1/31/07, 1:01 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outdoor spas, pools and the bonding of the deck.

I suppose you don't agree that we should be bonding the water either then
That is also a proposal for any plastic pool. They want a .5 sq/meter metal bonding electrode in the water. That is what gets bonded to the deck in your scenario.
BTW even if the pump is double insulated I doubt the heater is. That is the real potential for energizing the water. They use an immersion element that is virtually identical to a water heater element. Better hope that GFCI is working.
Reply With Quote
  #12  
Old 1/31/07, 1:19 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

No I would not support that....lol.....just dont like the sound of it to be honest with you.

I guess I just dont see how any of that pertains to the 2005 NEC requirement for the bonding of a spa in how I know spa's....but I could see it in a built in spa that is designed with rebar and concrete like the pool...

Isn't the gradient for metal parts greg.....the heat itself in my spa which is metal cased is also tied to the motors via the # 8 AWG.....I would think that takes care of the bonding potential.

Personally...I think they are OVER "analysis" it to all hell...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 1/31/07, 1:20 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

Quote:
Originally Posted by Greg Fretwell
They use an immersion element that is virtually identical to a water heater element. Better hope that GFCI is working.
lol...watch it now fella....you are gonna have them wanting Water Heaters on GFCI's next with that statement...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 1/31/07, 12:56 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outdoor spas, pools and the bonding of the deck.

The equipotential grid is for everything conductive and the water is conductive. If you have a plastic tub the water or the deck can still be energized relative to each other. That is what they are trying to correct.
The heater and motor may be bonded but if that is not also bonded to the deck you can have the gradient.
The "bond the water" idea was in the ROP for the 2005 but it didn't make it to print. It is probably going to be in the 2008.
Reply With Quote
  #15  
Old 1/31/07, 3:57 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Outdoor spas, pools and the bonding of the deck.

if you ask me they have a BUNCH more to fix than just that to solve the problems in that Article...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:23 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts