Default Outlet Reading

On my tester all three lights lit up with no explanation on the tester. Can someone help with this kind of readout. what could be wrong with the outlet? Ground and neutrals reversed, etc.

Attachment 11417

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 8:42 AM..
Reply With Quote
  #2  
Old 5/9/07, 11:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Outlet Reading

This usually indicates a 240 volt circuit.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 5/10/07, 1:37 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Reading

You can also get this with a bad connection, either in the wiring or a loose connection to one prong of the tester. The tip off is 2 of the lights will be about half brightness.
Reply With Quote
  #4  
Old 5/10/07, 5:18 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Outlet Reading

All three lights where nice and bright. This outlet is in a kitchen, above the counter.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #5  
Old 5/10/07, 7:56 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Outlet Reading

Quote:
Originally Posted by nbhi
All three lights where nice and bright. This outlet is in a kitchen, above the counter.
I noticed it is by a counter, It should be a GFCI. All 3 lit up, might not be grounded. Is it an older house with with 2 wires, hot and neutral that someone has put in a 3 prong rec? And maybe grounded it to the box which would be a false ground.
Reply With Quote
  #6  
Old 5/10/07, 9:06 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Outlet Reading

You could confirm this with your SureTest, but as I said, it usually indicates an improperly wired, 240 volt circuit (if all lights were bright and equal).

A bad or false ground will not give this indication. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 5/10/07, 8:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlet Reading

Do you own a voltage non-contact ticker?

if you do.....ticker both slots and if it is 240V both sides will activate the ticker.....to rule out 240V or not.

If this is the only receptacle that caused this......then 1.) You call it out because something appears wrong, and 2.) if it reads 240V with the ticker then you know it is not a plug thats allows 240V to it.....

greg is right however in that usually if something is wrong in the unit it will have (2) lights not nearly as bright as one of them.....in the end call it out IF you tester does fine on all other plugs other than this one....needs to be looked at to be sure......either way that is not a plug designed for 240V so if that was the case...it needs to be addressed.



Paul W. Abernathy
Reply With Quote
  #8  
Old 5/10/07, 10:50 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Reading

Did you ask the owner/seller if there was anything funny with that receptacle? Have them plug in one of THEIR appliances and prove it to you.
If the blender or mixer sounds normal it is not 240v.

Probably not SOP huh?
Reply With Quote
  #9  
Old 5/10/07, 10:59 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Outlet Reading

Ok all

Just put a volt meter on it.

Radio shack under $20.00

Does anyone have a problem with this??

rlb
Reply With Quote
  #10  
Old 5/10/07, 11:51 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Reading

Paul, the volt tick will not prove 240. A receptacle on a circuit that has an open neutral upstream and a load downstream will show line voltage on both slots.
Reply With Quote
  #11  
Old 5/11/07, 10:14 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Outlet Reading

Are the neutral wires double tapped in the main panel?
Reply With Quote
  #12  
Old 5/11/07, 10:50 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Outlet Reading

Quote:
Originally Posted by dandersen
Are the neutral wires double tapped in the main panel?
Where are you going with this?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 5/11/07, 7:10 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Outlet Reading

Quote:
Originally Posted by jpope
This usually indicates a 240 volt circuit.
As you can see by the attached schematic.
Attached Thumbnails
outlet-reading-three-prong-tester-schematic.jpg  
Reply With Quote
  #14  
Old 5/12/07, 1:24 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlet Reading

Quote:
Originally Posted by brian winkle
Paul, the volt tick will not prove 240. A receptacle on a circuit that has an open neutral upstream and a load downstream will show line voltage on both slots.
Brian,
Keep it to HI basics...not diagnosis as they are not electricians so on a counter top that tests out all ok except a single receptacle on a counter.....and no others would not lead a person to that diagnosis....they can use the ticker to verify it just is not right and report as such.....

It will prove something is wrong...and if none other on the counter does it ahead and beyond i would stick with report it versus diagnostic theories.....now if other read the same i would then agree...but since it is isolated on a counter circuit i would think others would exist.... either way it is report worthy....as a loose neutral ahead could cause it BUT all factors need to apply.



Paul W. Abernathy
Reply With Quote
  #15  
Old 5/12/07, 3:27 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Reading

I still think this is a question you ask the seller. Let him plug in a blender (table lamp or something) to prove there isn't a problem. I bet the worst case is he has to jiggle the plug to make it work.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bathroom outlet near floor: GFCI mthomas2 Electrical Inspections 3 4/13/07 10:35 PM
Should there be an outlet here? lprinzi Electrical Inspections 3 3/23/07 3:12 PM
Testing a dryer outlet acox Electrical Inspections 14 7/27/06 10:51 PM


All times are GMT -4. The time now is 9:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts