Default Outlet 'spacers'

Can someone please explain the requirements and use of 'spacers' at electrical outlet boxes? My understanding is that in certain instances a trim ring or extender of sorts may be needed at a j-box, that is recessed too much into the wall, to maintain the gap (1/4"??) caused by that recessing of the box and the cover plate. Now, certainly that would seem like it would be outside the scope of a typical home inspection to even think about something like that but, trust me, I have ulterior motives for understanding this concept better. If what I'm asking is not clear to you then that's OK, I probably don't need to know that (Bob), perhaps only the sparkies will now what I'm referring to and can explain it. Are there any sparkies left on the message board?

Note: I think I have subsequently found the answer to my question and would delete this post if it allowed me to.

From NEC:
Quote:
"In walls or ceilings with a surface of concrete, tile, gypsum, plaster, or other noncombustible material, boxes employing a flush-type cover or faceplate shall be installed so that the front edge of the box, plaster ring, extension ring, or listed extender will not be set back of the finished surface more than 6mm (1/4"). In walls and ceilings constructed of wood or other combustible surface material, boxes, plaster rings, extension rings, or listed extenders shall be flush with the finished surface or project therefrom."
Here's an example from the NEC Handbook.
"A wall constructed of wood but sheathed with an outer layer of gypsum board is permitted to contain boxes set back or recessed not more than 1/4". A wall constructed of metal studs but finished with wood panels requires that the outlet boxes be mounted flush with the combustible material."



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog

Last edited by mboyett; 2/12/09 at 8:31 AM..
Reply With Quote
  #2  
Old 2/12/09, 8:33 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Outlet 'spacers'

Quote:
Originally Posted by mboyett View Post
Can someone please explain the requirements and use of 'spacers' at electrical outlet boxes? My understanding is that in certain instances a trim ring of sorts may be needed at a j-box, that is recessed too much into the wall, to maintain the gap (1/4"??) caused by that recessing of the box and the cover plate. Now, certainly that would seem like it would be outside the scope of a typical home inspection to even think about something like that but, trust me, I have ulterior motives for understanding this concept better. If what I'm asking is not clear to you then that's OK, I probably don't need to know that (Bob), perhaps only the sparkies will now what I'm referring to and can explain it. Are there any sparkies left on the message board?
Michael, I can think of only 2 reasons for extending a J box, the first is to correct the relative depth of the box to the drywall, the second possibility is to increase the boxes fill capacity.

As an inspector I would make no note of them unless I felt there was something weired going on (such as a second layer of drywall installed over existing to hide something) I have seen that done. Having said that unless you are removing coverplates (which I sometimes do) you aren't going to find it.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 2/12/09, 8:47 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Outlet 'spacers'

Gerry,
Perhaps Michael has run into this scenario, as I find this quite often. A coverplate is missing on a wall (sheetrock) that is covered (overlayed) with wood paneling or T&G Pine, Cedar, BeadBoard, etc... resulting in an increased depth to the j-box of 1/8" to 1/4", occasionally more.
Jeff
Reply With Quote
  #4  
Old 2/12/09, 9:30 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Outlet 'spacers'

Yes, that is the scenario guys. As you may have heard on other threads Texas has recently adopted a new SOP and a Commentary is being written for that SOP to further explain it. One of the proposed paragraphs of the Commentary concerned this topic but it has been deleted for now. Obviously it would require the removal of all or at least a sample of cover plates or maybe those that are more likely to have this scenario. Anyway, thanks for the replies and look for my thread on the Commentary in the Texas section of the board and I'll explain this in more detail.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #5  
Old 2/12/09, 10:30 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet 'spacers'

It is not really to maintain the gap, but more to limit the gap to no more than 1/4" in non-combustible surfaces. This is to limit the chance for an arc or spark escaping into the wall cavity and starting a fire. It also provides a more secure mounting for the device instead of relying on the coverplate to hold it securely.

As a side note, the maximum gap around the sides of the box is limited to 1/8". The surface should be patched to correct this if larger than 1/8".
Reply With Quote
  #6  
Old 2/12/09, 10:42 AM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet 'spacers'

Hi Michael,

The main purposes of an extension ring on an a J box is to protect the insulation of the conductors from mechanical injury, provide protection for the receptacles terminals and to provide better electrical continuity for the ground. All of the aforementioned will help prevent igniting any combustible material surrounding the outlet.

An extension ring is required if the J box is recessed more than 6mm or .24 inches, approximately 1/4 inch.

Mike
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bathroom outlet near floor: GFCI mthomas2 Electrical Inspections 3 4/13/07 10:35 PM
Testing a dryer outlet acox Electrical Inspections 14 7/27/06 10:51 PM


All times are GMT -4. The time now is 9:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts