Default Re: Outlet tester

http://ecmweb.com/mag/electric_think_gfci/

GFCI testers. If you're from Missouri and simply don't believe the internal test circuit, then you need to exercise care in selecting the GFCI tester and in interpreting the results. It wasn't until the 1993 Edition of UL 1436, Safety Standard for Outlet Testers and Similar Devices, that the requirements for GFCI testers were coordinated with the requirements for GFCIs themselves. Testers that are not UL listed and UL-listed testers produced prior to 1993 may contain test circuits that do not properly test the GFCI. Indeed, they may indicate an unsatisfactory test when the GFCI is functioning fully in accordance with the UL GFCI standard.

Some testers not meeting UL 1436-1993 have timing circuits that limit the test current to a duration of 200 ms. If the GFCI takes more than 200 ms to trip (as permitted by UL), these testers may never trip some GFCIs that are in full compliance with UL requirements. Therefore, if you choose to use a GFCI tester, make sure it's listed to the 1993 Edition of UL 1436.

Some GFCI testers are relatively simple circuit testers with an additional test button. Others have milliammeters or dials that can be used to select various test currents. When using any of these more sophisticated testers, do not assume that it's accurately checking the calibration of the GFCI. There is very likely some capacitive leakage and possibly some harmless ground fault leakage "preloading" the GFCI. Consequently, a GFCI that is tripping within the UL time/current requirements may, according to the tester, be tripping at 3mA. In this case, the tester is simply giving a misleading reading.

Reverse polarity. Since testers establish a test circuit between hot and equipment ground, if the receptacle into which the tester is plugged is wired with reverse polarity, there will not be a voltage across the tester and test current will not flow. The GFCI will not trip and thus the GFCI might erroneously be considered defective.

Testing GFCIs on nongrounding circuits. Testers should not be used to test GFCIs installed as replacements for two-wire receptacles on nongrounding circuits. By design, GFCI testers will not test a GFCI protecting a 2-wire circuit and can expose the user to a potential shock.

The test button integral to the GFCI applies the test current between hot and neutral. This is not the case with GFCI testers; the test current in these devices is applied between hot and the equipment ground. Therefore, if there is no equipment ground, no test current will flow. If there are any exposed metal parts connected to the receptacle grounding contact (such as a metal face plate or a weatherproof cover), they will be energized by the test device. Since some of the test devices apply up to a 30mA test current; using such a tester on a 2-wire circuit while touching a metal cover plate could result in an uncomfortable shock.

Keys to testing GFCIs.

* Use the GFCI integral test button.

* Check for line-load reversal using the GFCI integral test button supplemented with a lamp or appliance.

* Be sure that any GFCI tester used is listed to the current UL standard.

* Do not use GFCI testers on two-wire nongrounding circuits.

Conclusion

The use of GFCIs, both required and otherwise, has mushroomed over the years, from just underwater swimming pool lights in 1968 to 33 references in the 1993 NEC, with even more to come. Now that GFCI installations number in the millions per year, repetitiveness can result in complacency. Not all GFCIs are alike. The installation layout needs to be evaluated and the most appropriate GFCI selected for the job, and you must adhere to all wiring instructions and markings.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 11/9/11, 1:10 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet tester

The newest GFIs will not reset if the line and load are reversed. They are also supposed to have an end-of-life component so that if they have failed the power is cut unlike the older ones that stayed on and made you think you had protection.
Reply With Quote
  #18  
Old 11/9/11, 2:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Outlet tester

Quote:
Originally Posted by Jim Port View Post
Jeff, could you expand on this? If UL and the device manufacturers tell you to use the test button, why would this not be sufficient?
I have often found (when using the built-in test button) that the mechanism will "trip," but will not open the circuit. So the simple push-button test is not definitive.

My protocol is to trip the circuit - either internally or by introducing a simulated ground fault - and then verifying with one of my instruments that the circuit has opened.

If the GFCI device is defective, an externally introduced ground-fault will not trip the internal circuit-tester, nor will it open the circuit, so I consider the external method to be more reliable.

A home owner relying on the internal test button without additional verification, may be lulled into a false sense of security believing the GFCI is operational when, in fact, it is not.

Additionally, many older GFCI devices will trip and open the circuit only when a large fault is introduced. My SureTest provides only a 7.4 ma load for a maximum of 6.5 seconds to determine proper operation.

I tested one this morning that would not trip at 7.4 ma, but tripped at 2.8 amps of impedance. The internal test button worked every time I tried it, but the load required to actually open the circuit was too great. Again, this gives a false impression that the device is functioning "properly."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dishwasher outlet tleahy Electrical Inspections 10 2/12/10 5:58 PM
Washing Machine Outlet < 6' from Utility Sink tdomingues Electrical Inspections 16 1/28/10 5:01 PM
What kind of Outlet tester do you use? jwatts1 Electrical Inspections 23 11/13/06 11:45 PM


All times are GMT -4. The time now is 9:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts