Question Outlet Under Sink

Hey can you guys tell me if this is properly installed under the sink.
It is for the garbage disposal, usually we see them mounted on the back side never below the plumbing with no GFCI.

Thanks
Attached Thumbnails
outlet-under-sink-img_6730_1.jpg  



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #2  
Old 3/20/08, 4:28 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

Troy my first concern is that the recepticale is face up.
Whats the black box?
is that a single or a duplex underneath?
I always call out lack of GFCI under the sink by the way.

Last edited by relliott; 3/20/08 at 4:33 PM..
Reply With Quote
  #3  
Old 3/20/08, 4:33 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

Quote:
Originally Posted by tfarmer
Hey can you guys tell me if this is properly installed under the sink.
It is for the garbage disposal, usually we see them mounted on the back side never below the plumbing with no GFCI.

Thanks
"422.16(B) Specific Appliances.

(1) Electrically Operated Kitchen Waste Disposers. Electrically operated kitchen waste disposers shall be permitted to be cord-and-plug-connected with a flexible cord identified as suitable for the purpose in the installation instructions of the appliance manufacturer, where all of the following conditions are met:

(1) The flexible cord shall be terminated with a grounding-type attachment plug.

Exception: A listed kitchen waste disposer distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.

(2) The length of the cord shall not be less than 450 mm (18 in.) and not over 900 mm (36 in.).

(3) Receptacles shall be located to avoid physical damage to the flexible cord.

(4) The receptacle shall be accessible."

DEFECT PER 3.
Reply With Quote
  #4  
Old 3/20/08, 4:35 PM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 604
Default Re: Outlet Under Sink

I have no clue, but it looks like it is attached to some kind of pump if you look closely. I have put a call into the builder to ask him what it was, thoughts



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #5  
Old 3/20/08, 4:36 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

Joe , with out the code , and you and me talking.
GFCI needed yes or no
recepticle facing up yes or no
Reply With Quote
  #6  
Old 3/20/08, 4:37 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

wow I missed that.
Shoulds have read better.
Still think recepticale is a problem , with that junction box facing up.
Water can enter easily
Reply With Quote
  #7  
Old 3/20/08, 4:46 PM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 604
Default Re: Outlet Under Sink

Without the code, can it be mounted up and w/out the GFCI?



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #8  
Old 3/20/08, 4:49 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

I say it is within 6 feet of water.
Why would that be an exception , with all the sink leaks.
Reply With Quote
  #9  
Old 3/20/08, 4:49 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

Quote:
Originally Posted by relliott
Joe , with out the code , and you and me talking.
GFCI needed yes or no
recepticle facing up yes or no
When the receptacles are facing up on kitchen counters, in a bathroom counter, or at a wet bar counter they are not allowed to face up, in the picture here this is not covered by the safety standard, and GFCI is not required, but may be added if desired.

I don't like to see the sharp edge of the plate this way because it presents a hazard when flesh is cut by it.

I saw a person get his arn cut bad when the metal plate was of this type.

The tall guy in the orange shirt should be around soon and will tell us of his experiences in the Chicago places he has inspected, we had lots of discussions in the past, search the archives for the piles of discussions.
Reply With Quote
  #10  
Old 3/20/08, 4:54 PM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 604
Default Re: Outlet Under Sink

Thanks Guys



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #11  
Old 3/20/08, 6:02 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

Thanks Joe
Thats why we do not operate under code, but under common sense.
Code is our guide.
Reply With Quote
  #12  
Old 3/20/08, 6:48 PM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 604
Default Re: Outlet Under Sink

Ditto



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #13  
Old 3/20/08, 9:58 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

As has been mentioned, this receptacle can be mounted in this fashion.


The real issue is box fill. The box shown is not listed for the number of conductors with a device in the box as well.
Reply With Quote
  #14  
Old 3/20/08, 10:40 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 2,927
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlet Under Sink

Quote:
Originally Posted by tfarmer
I have no clue, but it looks like it is attached to some kind of pump if you look closely. I have put a call into the builder to ask him what it was, thoughts
Air switch for the disposal
Reply With Quote
  #15  
Old 3/21/08, 12:00 AM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 604
Default Re: Outlet Under Sink

Thanks Brian thats what the builder said



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outlet position under kitchen sink jgollaher Electrical 9 4/20/07 6:46 PM
Outlet under kitchen sink adooley Electrical 3 2/13/07 3:50 PM
Sink Clog dirtydishes Plumbing 25 8/27/06 4:48 PM


All times are GMT -4. The time now is 10:01 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts