Default Outlets on branch circuits

Is there any restriction to the number of outlets that can be installed on a branch circuit? If not, what is the recommended number that can be used safely? Thanks in advance.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 9/6/07, 12:12 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlets on branch circuits

Quote:
Originally Posted by bsmith
Is there any restriction to the number of outlets that can be installed on a branch circuit?
In general, in a residence, in the US, barring local codes, NO...there is no limit.



Quote:
Originally Posted by bsmith
If not, what is the recommended number that can be used safely?
8-12 is typical. 12-15 is not unheard of, depending on the room.
Reply With Quote
  #3  
Old 9/6/07, 8:51 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,008
Default Re: Outlets on branch circuits

Thanks for the reply Speedy.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #4  
Old 9/6/07, 9:41 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Outlets on branch circuits

I've seen whole new home additions put on one breaker. "Breaker" should be a tool you use on the electrician's legs.

tom
Reply With Quote
  #5  
Old 9/6/07, 10:02 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlets on branch circuits

Quote:
Originally Posted by Speedy Petey
In general, in a residence, in the US, barring local codes, NO...there is no limit.

8-12 is typical. 12-15 is not unheard of, depending on the room.
!!!!!! couldn't believe my eyes at first. The Canadian Electrical Code limits the "outlets" (includes lights) on a circuit to a max of 12 in residential. We used to wire in 9-10 to leave room for another outlet or two at a future time if needed.
Reply With Quote
  #6  
Old 9/6/07, 12:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets on branch circuits

Just for FYI......Electricians ( good ones ) really understand that the amount of general use circuits as a minimum is important to the dwellings overall layout. Guess thats the lighting designer in me speaking....

If the dwelling is 2,400 sq. ft then we have to calculate the lighting and general appliance calculation....leaving off the small appliance and laundry circuit for this small specific calculation IF you want to know how many circuits should be in the house as a general rule...

So 2,100 sq ft x 3 VA/ft = 6,300 VA

ok.....so 6,300VA/120V = 52.5A ( and we know this rounds to 53A right )

So...you have 53A/15A Circuit = 3.53 (now you KNOW you can't have .53 of a curcuit...right...lol )

So the mimimum amount of circuits for general lighting and receptacless is 4 circuits.....as to the number of receptacles on each circuit the NEC simply says they should be proportional...( evenly balanced if you will )

So if you have 35 general use items - 45 items / 4 circuits = 11-12 items per circuit....

Now...that is some guidelines for how it is done...a good electrician will look at all the factors, and indeed we usually have well more than 4 circuits for general lighting and receptacle loads....but we keep it balanced to the point of in my companies case we dont put more than 10 items on a circuit...period...

Remember this has nothing to do with the required receptacles and so that is needed.....this was just to give you an idea of a method for determining the number of circuits needed in a dwelling based on the square footage.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 9/6/07, 12:56 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlets on branch circuits

Paul is right. The NEC really sets the number of circuits based on square footage. Receptacles are placed for convenience. You can handle up to 600 sq/ft with a single 15a circuit and still be "hold your nose legal". If this was one big room you could probably get away with 8 or 9 receptacles. If it was a chopped up floor plan with a couple rooms and lots of wall segments it could be a huge number.
Good "design" would have more circuits but that is not what the minimum code says.
One down side to the 2008 rule requiring AFCIs on general lighting is, I bet you will see more square footage on each breaker now. I have already seen bedrooms pushing the 600 sq/ft rule pretty hard
Reply With Quote
  #8  
Old 9/6/07, 12:58 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets on branch circuits

Greg I love that term..." hold your nose legal ".....excellent...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 9/6/07, 1:11 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlets on branch circuits

Let’s not forget that the receptacles in the kitchen and dinning room of this same 2100 square foot house will be on the small appliance circuits which greatly reduce the area covered by these four 15 amp circuits.
Reply With Quote
  #10  
Old 9/6/07, 1:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets on branch circuits

When giving a general lighting and receptacle calculation. The calculated (4) circuits do not include those required circuits. You would only apply those when doing the demand load calculation for the calculated load for sizing the service itself.

Us Instructors...you gotta love us



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 9/6/07, 1:16 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets on branch circuits

With that said.......what you say guys...do most of the homes you guys do have the minimum (2) Small Appliance Circuits and (1) Laundry...lol...

Seems like the last few houses we have done I have like (4) minimum Small Appliance Circuits lol...and (2) laundry circuits......Big Houses...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Article 240 : Overcurrent Protection Article pabernathy Electrical Inspections 0 5/23/07 12:40 PM
Testing Branch Circuits with SureTest pabernathy Electrical Inspections 4 2/12/07 7:30 AM


All times are GMT -4. The time now is 8:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts