I inspected a house yesteday that had a few GFCI outlets in the kitchen and all the rest of thle outlets in the house were labeled as GFCI with no ground for equipment being used. My tester showed open ground & would not trip any GFCI device.
Ther were also a couple of 2 prong outlets in one bedroom. Is this just a way of converting the house from 2 prong to 3 prong & is it safe or meet code.
The house was built in 1956

Roy Drangstveit
Reply With Quote
  #2  
Old 10/15/08, 10:34 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Outlets with a label

It meets code, and it is better than replacing two prong with three prong outlets, but not the best. Take a couple of hours and watch this http://www.nachi.tv/episode53, BTW, your tester won't trip the GFCI in this case because it uses the ground to create the short. You would have to test using the GFCI device buttons themselves (which is really the best way to test them anyway.)

Bad = replace 2 prong with 3 prong = violation and unsafe
Better = replace 2 prong with 3 prong GFCI/labels = acceptable by NEC and safer, but not great
Best = re-wire with appropriate romex = acceptable by NEC as well as appropriate.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.

Last edited by mnahrgang; 10/15/08 at 11:39 AM..
Reply With Quote
  #3  
Old 10/15/08, 10:43 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Outlets with a label

A GFCI should still trip without a ground.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #4  
Old 10/15/08, 10:58 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlets with a label

Quote:
Originally Posted by jbushart View Post
A GFCI should still trip without a ground.
Not with the "traffic light" tester, it won't, without a ground. Some guys plug the tester into an adaptor and run a seperate ground wire to something metallic and grounded when testing load side 3-prong receptacles that are served with a GFCI but not grounded.
Reply With Quote
  #5  
Old 10/16/08, 11:20 AM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlets with a label

From yesterday PM, this kitchen outlet, brand new 2007 construction, no ground, tester button useless, works with the built-in button. Somebody in sub-trades gets a slap to the head.
Also, the AFCI breaker in the panel does NOT trip with the test button. Is that a faulty unit?

John Kogel
www.allsafehome.ca
Attached Thumbnails
outlets-label-gfi1.jpg   outlets-label-afci.jpg  
Reply With Quote
  #6  
Old 10/16/08, 1:20 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Outlets with a label

Also kinda makes you wonder why they used all the mini's with plenty of space left.

Jeff
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
ungrounded outlets! gmaher Electrical Inspections 29 6/10/07 10:58 PM
Properly Testing GFCI Outlets tchristopher Electrical Inspections 17 3/17/07 11:19 AM
Miller AC (Blank Label) gkoehl Inspecting HVAC Systems 2 3/9/07 9:56 AM
Replacing 2-prong outlets with GFCI outlets kshepard Electrical Inspections 7 6/24/06 6:58 AM


All times are GMT -4. The time now is 9:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts