Default Outlets under sink

Is this acceptable to have an outlet under a sink. I reported it as a safety hazard and should be relocated.
Reply With Quote
  #2  
Old 2/28/06, 10:03 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: Outlets under sink

Typically there are outlets (receptacles) under the sink. The dishwasher as well as the disposal is plugged into an outlet with an appliance cord. The vast majority of the homes I inspect have one or more outlets deliberately installed there just for those reasons. There are some caveats as to how the outlets are installed.

Last edited by dedwards; 2/28/06 at 10:07 PM..
Reply With Quote
  #3  
Old 2/28/06, 11:35 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outlets under sink

Mmmmm caveats..I love those little fish eggs

I don't think I've ever owned a home w/out a plug under the sink.....
Reply With Quote
  #4  
Old 2/28/06, 11:36 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Outlets under sink

If the recepticle protrudes (sticks out from the wall) and is not waterproof, I call it out.

Electricians say that under sink is not a wet area. How many of them have changed out a kitchen sink faucet?

I have gotten shocked many times changing a kitchen sink faucet.

I also like to see the wire (if directly connected) to the disposer be in waterproof cable.

I know that no codes recognize this, but I see it as a safety issue.

Laugh all you will. All it need sis some little kid playing hide and seek under the kitchen sink to get killed (or even shocked) for a lawsuit to ensue.




Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #5  
Old 3/1/06, 8:25 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets under sink

Quote:
Originally Posted by wdecker
If the recepticle protrudes (sticks out from the wall) and is not waterproof, I call it out.

Electricians say that under sink is not a wet area. How many of them have changed out a kitchen sink faucet?

I have gotten shocked many times changing a kitchen sink faucet.

I also like to see the wire (if directly connected) to the disposer be in waterproof cable.

I know that no codes recognize this, but I see it as a safety issue.

Laugh all you will. All it need sis some little kid playing hide and seek under the kitchen sink to get killed (or even shocked) for a lawsuit to ensue.

lol....Well again its receptacle...lol... and are you trying to say no electricians are handy...lol....hey fella...I am a HIC and CIC contractor...lol...I do remodels..lol....but yes the area below is not considered a wet area....net fact is if it is a commercial kitchen it would need to be GFCI protected....while in a dwelling if it is dedicated for a Disposal or DW...then it need not be....

But I agree with Will.......if their is a plug under the sink it should have a purpose...of no purpose it their......note it.

Hey....we are not laughing at ya Will....even Electricians have a heart

Also a few notes....and may only be seen in new construction in case you all do any....the receptacles under the sink are many times cut out incorrectly...either they sit back to far into the wall or the box is cut out too large.....these are also safety issues



Paul W. Abernathy

Last edited by pabernathy; 3/1/06 at 8:30 AM..
Reply With Quote
  #6  
Old 3/1/06, 8:30 AM
James M. Troth's Avatar
James M. Troth James M. Troth is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Mechanicsburg, Oh
Posts: 317
Default Re: Outlets under sink

I make a report comment that safety level would benefit from the outlet being GFCI protected.



Habitation Investigation LLC
http://www.homeinspectionsinohio.com
Reply With Quote
  #7  
Old 3/1/06, 8:34 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets under sink

James,

Most certainly will go along way in the safety of the client....most certainly adding that is advised....you just never know what a person will try to plug into it.....while they dont have to change anything...safety suggestions are always an added bonus...

While again not required......most certainly a great suggestion i hope most are using.



Paul W. Abernathy
Reply With Quote
  #8  
Old 3/1/06, 8:38 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Outlets under sink

I regularly see under sink recepticles where the whole box is not in the wall, is only connected by BX and is a regular box and the cover plate is the wrong type. Many times, one or more punchouts are missing and open.

Unsafe. May get laughed at by electricians (and I do), but, hey, I don't work for them. And, in Illinois at least, they don't have a state license.

I will go with the law (and common sense) thank you very much. Electricians rarely have to face non-laughing lawyers.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 3/1/06, 8:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets under sink

Dang.....their you go again fella...lol....what makes you think Electricians laugh at ya...



Paul W. Abernathy
Reply With Quote
  #10  
Old 3/1/06, 8:48 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets under sink

Those things you mentioned would make any electrical contractor agree....while we do use code....we DO understand the NEC is the minimum standard...we do not just adhear to the minimums simply because we have a license to do so.

I guess I am bias.....I do both but I call out just as many concerns...



Paul W. Abernathy
Reply With Quote
  #11  
Old 3/1/06, 9:11 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Outlets under sink

Paul;

1) Because I have had electricians, to my face and on the phone, laugh at me for calling out certain safety issues, when the installation met 'code'.

2) The NEC is not the minimum, the local code is the minimum. Some municipalities just accept the NEC, others amend it or write their own (Chicago, for example).

3) In many cases, around here, smaller towns and villages, seeking the bigger builders to develop land and provide the village with a bigger tax base, issue 'variances' to the builders. One such local village issued a builder a variance on 500 townhouse units that allowed them to not install GFCI and AFCI protection. I inspected and called it out, as my license requires me to do. The electrician (a good guy) explained the issued variance. He thought it was a joke and that the builder was stupid. But it was 'code'.

Many times, local AHJ codes are political and economic documents rather than technical or safety documents. They are under the authority of politicians and therefore, don't always have the best safety interests of the public in mind.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #12  
Old 3/1/06, 9:16 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets under sink

Very true Will........I find the answer to # 1 very sad....as an electrician I would NEVER laugh at the HI......I guess I just cant relate to that as I have never had a HI call me out and I laugh at them.....if they are concerned over something my job is to either give my opinion or put everyone at ease...

Not belittle the guy for doing his/her job......

Yes, very sad when local politics play a role...

This kinda also verfies what I was saying in the post about Panels in other locations and Supplemental overcurrent protection.....and remodels....all depends on the local AHJ......and as stated..sadly Politics.



Paul W. Abernathy
Reply With Quote
  #13  
Old 3/1/06, 9:21 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Outlets under sink

Glad we could reach and understanding, Paul.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #14  
Old 3/1/06, 9:23 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Outlets under sink

lol......did not think we didn't have an understanding...lol......I am only here to answer questions and learn myself.....Only giving you opinions...lol....I

I just like teasing...lol.......and its Receptacle...lol....



Paul W. Abernathy
Reply With Quote
  #15  
Old 3/1/06, 7:52 PM
ecox1's Avatar
ecox1 ecox1 is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Hampton, VA
Posts: 268
Send a message via Yahoo to ecox1
Default Re: Outlets under sink

I'm having problems posting the pic guys whenever I click the add image icon I get a page error
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
ungrounded outlets! gmaher Electrical Inspections 29 6/10/07 10:58 PM
Properly Testing GFCI Outlets tchristopher Electrical Inspections 17 3/17/07 11:19 AM
Sink Clog dirtydishes Plumbing Inspections 26 8/27/06 3:48 PM
Replacing 2-prong outlets with GFCI outlets kshepard Electrical Inspections 7 6/24/06 6:58 AM
Kitchen sink & outlets lprinzi Electrical Inspections 3 6/8/06 5:52 PM


All times are GMT -4. The time now is 3:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts