Default Overcurrent for AC - WRONG???

check out these pics.
house built in early 1960's
panels in bedroom closet

almost 100% that the small box is acting as the 30 amp overcurrent for the AC.

power supply to it is the double tap on the 50 amp breaker at the top right.

I understand the double tap is wrong.
I also understand that the white "hot" wires in the smaller box should be labeled black.
Single self-tapping machine screw was holding the front cover on.

Am I just looking at an issue of support/protection of the romex hanging outside the panels?
Am I missing anything else?
Attached Thumbnails
overcurrent-ac-wrong-100_0306.jpg   overcurrent-ac-wrong-100_0307.jpg   overcurrent-ac-wrong-100_0309.jpg  

Last edited by ccbrands1; 9/5/06 at 9:54 PM..
Reply With Quote
  #2  
Old 9/5/06, 10:30 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Overcurrent for AC - WRONG???

how about the clothes closet problem and the working space problem
Reply With Quote
  #3  
Old 9/5/06, 11:30 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Overcurrent for AC - WRONG???

Quote:
Originally Posted by Greg Fretwell
how about the clothes closet problem and the working space problem
that's exactly why i mentioned this.

the following was from an former post by joe tedesco.
__________________________________________________ _____
240.24(D) Not in Vicinity of Easily Ignitible Material

Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.

Examples of locations where combustible materials may be stored are linen closets, paper storage closets, and clothes closets.
__________________________________________________ _____

obviously my pic fits under this, but if it were original to the house (early 1960's) then what.

no city inspection in this town.

guess i'm on my own with documenting it as a fire hazard?
Reply With Quote
  #4  
Old 9/6/06, 12:23 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Overcurrent for AC - WRONG???

The clothes closet language showed up in the 80s but the easily ignited materials language was there for many years before that.
Reply With Quote
  #5  
Old 9/6/06, 9:31 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Overcurrent for AC - WRONG???

Quote:
Originally Posted by ccbrands1
Am I missing anything else?
Missing insulating bushings, red wire connected to neutral bus.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #6  
Old 9/6/06, 10:44 AM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Overcurrent for AC - WRONG???

Quote:
Originally Posted by Greg Fretwell
The clothes closet language showed up in the 80s but the easily ignited materials language was there for many years before that.
The reason the wording showed up later was because the clothes caught on fire (not a good thing). If it was unsafe in the 80's, then it was also unsafe in the 60's and should be reported as such. Recommend an electrician to evaluate. The buyer then determines what course of action to take.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #7  
Old 9/7/06, 5:53 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Overcurrent for AC - WRONG???

ACK!!

Double taps @ Main OCPD??
White (neutral) going to breakers
bunched Wires under One screw
Missing fittings (as pointed out already)
OLD cloth wire (scary)
Open OCPD Knock out See first pic with panel cover on...
Main panel bonding...Can't see it
Red wire going to neutral buss for ......???
Sub panel neutral and ground separated....Can't tell
Service panel legend marked or just hack job markings... See service panel
label...can't tell if properly marked...
Sloppy wiring job.. DIY'er

Oh ya the closet thing too..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thanks Nick I just hate it when I'm wrong cbottger Miscellaneous Discussion for Inspectors 0 6/9/07 2:01 PM
What's wrong here? wwarner Structural Inspections 15 9/12/06 7:47 PM
Messy work, but is it wrong? mtimpani Electrical Inspections 8 9/9/06 9:56 PM
is this really wrong brepanshek Plumbing Inspections 15 8/12/06 2:09 PM
What's Wrong Here? jtedesco1 Inspecting HVAC Systems 20 6/29/06 6:50 PM


All times are GMT -4. The time now is 9:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts