Default Overhead 120VAC to Garage Clearance?

I was a home this morning and I ran into an unusual situation with a 4 conductor 120 VAC service supplying the garage. The height above grade was 8-1/2 to 9 feet. Since this a 4-conductor circuit, the neutrals and grounds are combined in the remote panel. My concern is the height above grade. I know the requirements for a service for the dwelling, but I have not run across anything for this situation regarding the height.

Looking for more definitive answer. I look at it being a safety concern not to mention the lack of drip loop at the dwelling.
Attached Thumbnails
overhead-120vac-garage-clearance-p1300363.jpg   overhead-120vac-garage-clearance-p1300364.jpg   overhead-120vac-garage-clearance-p1300365-1.jpg   overhead-120vac-garage-clearance-p1300411.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/21/11, 3:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Overhead 120VAC to Garage Clearance?

Same height requirements as a service drop.

I'm curious as to how it's a four-wire 120V circuit. Something isn't right.

Even if the egc's and neutrals were allowed to be bonded at that panel, they must also be bonded to the box. In addition, the garage should have its own GES.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 6/21/11, 3:36 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Overhead 120VAC to Garage Clearance?

There is a separate GEC at the garage. I thought it was unusual, too but it was there.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #4  
Old 6/21/11, 6:15 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Overhead 120VAC to Garage Clearance?

They need to be 12" above a driveway 10" areas accessible by pedestrians. I would call them the same as service entrance cables.
Reply With Quote
  #5  
Old 6/21/11, 10:55 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Overhead 120VAC to Garage Clearance?

Thanks,
I was unsure since there is protection of this service in the main distribution panel. I did end up calling it out as a safety concern in the report.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #6  
Old 6/22/11, 11:12 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Overhead 120VAC to Garage Clearance?

I also would have looked more closely at what type of splices those were. Even for barrel type, they seem awful thin and unprotected.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #7  
Old 6/22/11, 11:15 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Overhead 120VAC to Garage Clearance?

It was 12 gauge wire from the dwelling to the garage. The interesting thing, I found out the seller of the property is an electrician. Kind of goes with cobblers and their shoes...



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #8  
Old 6/25/11, 11:35 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Overhead 120VAC to Garage Clearance?

Quote:
Originally Posted by gliebig View Post
4 conductor 120 VAC service
I am curious about that too. Was it a 4-wire 120/240V feeder (H-H-N-G), and then only 3 of the wires were used for a 120V remote subpanel (H-N-G)?

Quote:
Originally Posted by gliebig View Post
Since this a 4-conductor circuit, the neutrals and grounds are combined in the remote panel.
The neutrals and grounds should not be connected if a ground wire is run with the feeder (or metal conduit is used that connect the two panels). Otherwise you could get current on that ground wire (parallel neutral path) ...

There are basically 2 ways to do a remote subpanel (NEC 250.32 ... see figures):
1. Connect the grounds between the service panel and remote subpanel (e.g. feeder ground wire or metal conduit connecting the panels). Then isolate the neutrals and grounds at the remote subpanel.
2. Do not connect the grounds between the service panel and remote subpanel (e.g. no feeder ground wire or metal conduit connecting the panels). Then the grounds and neutrals are connected at the remote subpanel.
And a separate earth ground (GES) is required for either remote subpanel option.

ECM has some good articles on Grounding & Bonding, including one for remote panels ... http://ecmweb.com/grounding/electric..._vs_bonding_5/

JMO & 2-Nickels ...
Attached Thumbnails
overhead-120vac-garage-clearance-remote-building-panel-option-1-grounds-connected.gif   overhead-120vac-garage-clearance-remote-building-panel-option-2-grounds-not-connected.gif   overhead-120vac-garage-clearance-remote-building-panel-4-wire.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #9  
Old 6/25/11, 11:55 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Overhead 120VAC to Garage Clearance?

Quote:
Originally Posted by roconnor View Post
I am curious about that too. Was it a 4-wire 120/240V feeder (H-H-N-G), and then only 3 of the wires were used for a 120V remote subpanel (H-N-G)?


The neutrals and grounds should not be connected if a ground wire is run with the feeder (or metal conduit is used that connect the two panels). Otherwise you could get current on that ground wire (parallel neutral path) ...

There are basically 2 ways to do a remote subpanel (NEC 250.32 ... see figures):
1. Connect the grounds between the service panel and remote subpanel (e.g. feeder ground wire or metal conduit connecting the panels). Then isolate the neutrals and grounds at the remote subpanel.
2. Do not connect the grounds between the service panel and remote subpanel (e.g. no feeder ground wire or metal conduit connecting the panels). Then the grounds and neutrals are connected at the remote subpanel.
And a separate earth ground (GES) is required for either remote subpanel option.

ECM has some good articles on Grounding & Bonding, including one for remote panels ... http://ecmweb.com/grounding/electric..._vs_bonding_5/

JMO & 2-Nickels ...
Nice post.

The second graphic (below) depicts an installation that is no longer permitted by the NEC but was permitted at one time.



Not sure what that green conductor is between the meter enclosure and the service panel in graphic #3?

Reply With Quote
  #10  
Old 6/25/11, 1:01 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Overhead 120VAC to Garage Clearance?

Quote:
Originally Posted by Robert Meier View Post
The second graphic (below) depicts an installation that is no longer permitted by the NEC but was permitted at one time.
Yes, I should have noted there are limitations now if the latest NEC has been adopted. The change applies to all new buildings on the 2008 NEC I believe, which many areas haven't even adopted yet. But even then there are still the two options for existing building systems where a remote building panel has been added. Home inspectors may find either option on inspections of existing buildings.

For an existing house I don't think the second option (no ground with the feeder) is really a safety issue an inspector needs to comment on, even though it wouldn't be permitted for all new construction under the latest NEC. My understanding is the change was made because you can have larger remote buildings where there is a remote subpanel without the ground on the feeder, and then another remote panel feeder is run with the ground ... and then the two systems are somehow connected (e.g. both are bonded to building steel or metal water lines).

http://www.ecmag.com/?fa=article&articleID=8837

And I don't know what that green wire is between the meter enclosure and the service panel is on the 3rd graphic. I didn't notice that ... . How about this revised one ...
Attached Thumbnails
overhead-120vac-garage-clearance-remote-building-panel-4-wire.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 6/29/11 at 11:46 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
attached garage ghelder General Inspection Discussion 5 2/23/10 5:40 PM
Garage door inspection procedure bgromicko General Inspection Discussion 5 8/7/09 12:47 PM
Unvented Overhead garage heaters bhartley Inspecting HVAC Systems 8 5/4/09 9:30 AM


All times are GMT -4. The time now is 9:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts