Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 515
Default Overloaded Junction Boxes and Fill

One junction box has # 2 AL for 100 amps and the other junction box # 2/0 AL for 150 amps. The boxes are undersized and overfilled.
Where does this fall under the NEC.
thanks,
Peter
Attached Thumbnails
overloaded-junction-boxes-and-fill-box-one.jpg   overloaded-junction-boxes-and-fill-box-two.jpg  
Reply With Quote
  #2  
Old 11/5/06, 10:55 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Overloaded Junction Boxes and Fill

Article 370 deals with conductor fill.
Reply With Quote
  #3  
Old 11/5/06, 11:01 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Overloaded Junction Boxes and Fill

HOLY CRAP!
Nothing mazes me anymore.

Art. 370 is Cablebus. Not applicable here.

NEC 314.16, 300.34, 300.4(F) apply.

The one looks to be close to legal. A collared 4-11/16" deep box maybe enough.
Reply With Quote
  #4  
Old 11/5/06, 11:19 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Overloaded Junction Boxes and Fill

Quote:
Originally Posted by Speedy Petey
HOLY CRAP!
Nothing mazes me anymore.

Art. 370 is Cablebus. Not applicable here.

NEC 314.16, 300.34, 300.4(F) apply.

The one looks to be close to legal. A collared 4-11/16" deep box maybe enough.
Well Sorry I was looking in my 99 codebook which is the only one I have inside the house...didn't know it was re located.
Reply With Quote
  #5  
Old 11/6/06, 9:29 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Overloaded Junction Boxes and Fill

Brian,

No worries fella......this is why educators like myself hold 2002 NEC Update Classes..lol.....to learn the changes and relocations.....lol

The connectors on these cables in the image on the right are also incorrect....they are for flexible AC , greenfield and so on Cable and not SER....

Also the SER is not supported within 12" from the box.....and for box fill.......

I threw in a trick question...but I took it out.......lol......sorry

Aw...what the hell.............the box on the right is a violation of Article 314.28(A)(2) as well......because the conductors are larger then # 4 AWG....and must meet the pull and angle requirement and that 4 x 1 1/2 box is not large enough......but who calls that out these days...lol......( dont say it does not apply to cables...read bottom line of that article...lol )



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 11/6/06 at 9:59 AM..
Reply With Quote
  #6  
Old 11/6/06, 5:12 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 515
Default Re: Overloaded Junction Boxes and Fill

Thanks Paul
Reply With Quote
  #7  
Old 11/6/06, 5:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Overloaded Junction Boxes and Fill

Anytime my brother.........I am only a call away !



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Calculating box fill of NM lfoster Electrical Inspections 14 7/1/07 12:02 PM


All times are GMT -4. The time now is 6:22 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts