One junction box has # 2 AL for 100 amps and the other junction box # 2/0 AL for 150 amps. The boxes are undersized and overfilled.
Where does this fall under the NEC. thanks, Peter |
|
#2
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Article 370 deals with conductor fill.
|
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
HOLY CRAP!
![]() Nothing mazes me anymore. Art. 370 is Cablebus. Not applicable here. NEC 314.16, 300.34, 300.4(F) apply. The one looks to be close to legal. A collared 4-11/16" deep box maybe enough. |
|
#4
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
||||
|
||||
|
Brian,
No worries fella......this is why educators like myself hold 2002 NEC Update Classes..lol.....to learn the changes and relocations.....lol The connectors on these cables in the image on the right are also incorrect....they are for flexible AC , greenfield and so on Cable and not SER.... Also the SER is not supported within 12" from the box.....and for box fill....... I threw in a trick question...but I took it out.......lol......sorry Aw...what the hell.............the box on the right is a violation of Article 314.28(A)(2) as well......because the conductors are larger then # 4 AWG....and must meet the pull and angle requirement and that 4 x 1 1/2 box is not large enough......but who calls that out these days...lol......( dont say it does not apply to cables...read bottom line of that article...lol ) Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 11/6/06 at 9:59 AM.. |
|
#6
|
|||
|
|||
|
Thanks Paul
|
|
#7
|
||||
|
||||
|
Anytime my brother.........I am only a call away !
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |