Default oversized main breaker

I inspected a home today with a 200 amp main breaker but the service conductors were undersized. This is an 800 sq ft lake cabin with electric heat, electric water heater, and electric stove. What all information shoud I give the client, outside of just deferring to an electrician.
Reply With Quote
  #2  
Old 4/15/07, 4:10 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: oversized main breaker

Can you share with us, what you mean by undersized? Could they have been copper when you expected Aluminum?

As for the client, explain how the over current protection is higher than the rating of the service entrance cables.

tom
Reply With Quote
  #3  
Old 4/15/07, 8:06 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: oversized main breaker

I am assuming from your post that the service disconnect was a separate box (mabye by the meter). Was there possibly another breaker at the inside panel that would serve as a disconnect for that box. And what was the disribution box rated for. Any pictures would help.
Reply With Quote
  #4  
Old 4/16/07, 10:48 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: oversized main breaker

With the lack of actual information I can only comment on this statement

Quote:
200 amp main breaker but the service conductors were undersized.
If indeed the SE Conductors are not sized to handle 200A based on 310.16 or even the allowance of 310.15(B)(6) of the NEC then it is wrong and should be defered.

Now....if you provide additional information like the size of the actual SE Conductors, If their was a service disconnect outside at the meter ( which I am not sure really matters..undersized is undersized ) then we can possibly go into more detail.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Arching Causes Main Breaker To Trip? msylvester Electrical Inspections 10 10/22/07 3:57 PM
Quiz: Main breaker panel box mounting dthomas2 Electrical Inspections 9 10/10/06 2:29 PM
double main breaker help pdoane Electrical Inspections 3 9/21/06 8:35 AM
Main Breaker Size cpennick Electrical Inspections 13 9/20/06 10:56 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts