I found this in the Main Service Panel today. #8 stranded copper installed in 20 amp breakers. I know undersized wire is wrong , but I can't find anything that talks about oversized conductors. I would appreciate any input / education on this subject from you Sparkys out there. Thanks , Rick
Rick Slocum NACHI # 04072697 Elizabeth CO 80107 ABSOLUTE Home Inspection Service |
| Find an InterNACHI certified North Carolina Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Should I not be concerned with this ?
Rick Slocum NACHI # 04072697 Elizabeth CO 80107 ABSOLUTE Home Inspection Service |
|
#3
|
||||
|
||||
|
Richard, so long as the wire size is UL listed for the breaker there is no problem, code is " a minimum std" only. I would much prefer a conductor be oversized, than a breaker be undersized. The weakestlink is still the breaker, not the conductor.
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#4
|
||||
|
||||
|
Thats kinda what I was leaning towards . Thanks Jerry !
Rick Slocum NACHI # 04072697 Elizabeth CO 80107 ABSOLUTE Home Inspection Service |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| Oversized wire, reduced at Breaker | rross2 | Electrical Inspections | 10 | 2/16/09 6:59 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 10:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 1:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 4 | 3/25/07 11:41 PM |