I ran into a situation today where the Air Handler w/heat strips was wired to a main panel 60 amp breaker with over sized #1 aluminum braided wire. Several of the aluminum braids were cut back (see attachment) to allow the wire to seat into the 60 amp breaker. Aside from the bare wires extending from the breaker, is this allowed?
Thank you, Richard Ross Accurate Home Inspections of America, LLC Cape Coral, FL 33914 239-271-8499 Office 239-271-8499 Mobile 407-358-5376 FAX
|
|
#2
|
|||
|
|||
|
No, it is not.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
||||
|
||||
|
No way!!!!
|
|
#4
|
||||
|
||||
|
Nope.
Ian Niquette Square One Home Inspection Markesan WI 53946 www.squareonehomeinspection.com Active Rain Network INACHI Awards Portal Want To Exchange Links? What we've got here is......failure......to communicate.....
|
|
#5
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Check this link. "NSI Polaris Bug" is what Marc Shunk calls them, and that's how I found this webpage.
http://www.tork.com/electrical/productdetail.aspx Used to connect large diam conductors or in this case, reduce the size to something that will fit the breaker correctly. John Kogel www.allsafehome.ca |
|
#6
|
||||
|
||||
|
Thanks for your responses
Richard Ross Accurate Home Inspections of America, LLC Cape Coral, FL 33914 239-271-8499 Office 239-271-8499 Mobile 407-358-5376 FAX
|
|
#7
|
||||
|
||||
![]() |
|
#8
|
||||
|
||||
|
Ian Niquette Square One Home Inspection Markesan WI 53946 www.squareonehomeinspection.com Active Rain Network INACHI Awards Portal Want To Exchange Links? What we've got here is......failure......to communicate.....
|
|
#9
|
||||
|
||||
|
Robert Newland Tyrone, GA 30290 NACHI05101290 http://www.CertifiedHI.com http://www.HomeInspectorTyroneGa.com Home Inspection Reports Powered by: HomeGauge eServices |
|
#10
|
|||
|
|||
|
Please Note:
Bob Electric is a non-member guest and is in no way affiliated with InterNACHI or its members.
No Haircuts?
|
|
#11
|
|||
|
|||
|
(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wirebinding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors. Terminals for more than one conductor and terminals used to connect aluminum shall be so identified. Also...Conductors need to be protected at their ampacity and once the fella cut them strands he has altered the ampacity rating of that conductor. So as everyone says...it's a no-no that you see alot-alot...so we fail-fail it alot-alot.... Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Ground wire in neutral bar, neutral to breaker, hot to ground? | rmc3inspection | Electrical Inspections | 4 | 8/1/06 9:44 AM |
| wire gauge / breaker rating | jweinberg | Electrical Inspections | 19 | 7/16/06 4:36 PM |