Default Painted over outlets and switches.

Is there anything in the NEC that prevents the switches and outlets from being painted over?

Thanks in advance

Russ



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/9/11, 11:58 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Painted over outlets and switches.

Here you go.

I would say that there is sufficient references to support a write up.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 2/9/11 at 12:08 PM..
Reply With Quote
  #3  
Old 2/9/11, 12:02 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Painted over outlets and switches.

Quote:
Originally Posted by rhensel View Post
Is there anything in the NEC that prevents the switches and outlets from being painted over?

Thanks in advance

Russ
Russell,just curious but what is the issue you are worried about over this ?
Reply With Quote
  #4  
Old 2/9/11, 12:10 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Painted over outlets and switches.

Quote:
Originally Posted by belliott View Post
Russell,just curious but what is the issue you are worried about over this ?
Of all the outlets I have seen painted, none were done with care. Usually just a paint brush and gobs of paint, much of which has filled in the slots who knows how far. I can just see someone trying to clean the paint out with a nail or something else.

If I see them painted, I just recommend replacement since outlets are so inexpensive.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #5  
Old 2/9/11, 12:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Painted over outlets and switches.

Quote:
Originally Posted by sstanczyk View Post
Of all the outlets I have seen painted, none were done with care. Usually just a paint brush and gobs of paint, much of which has filled in the slots who knows how far. I can just see someone trying to clean the paint out with a nail or something else.

If I see them painted, I just recommend replacement since outlets are so inexpensive.
I recommend replacement only if like you said,the slot was compromised.
Around here I hired tons of painters for rental units and they always loved panting over them for cost cutting.

Just lower quality work and will leave more hand prints .The real issue is removing them once they have a few coats on the old ones,just like the panels.
Reply With Quote
  #6  
Old 2/17/11, 11:48 PM
rneag rneag is offline
InterNACHI Member
 
Join Date: Jul 2009
Posts: 3
Default Re: Painted over outlets and switches.

It's wrong and improper. Paint can continually get pushed into the receptable openings a create a fire hazard. The receptacles should be replaced, a little less concern with the switches as they only control flow, not provide it. Too inexpensive not to replace IMO.
Reply With Quote
  #7  
Old 2/18/11, 1:32 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Painted over outlets and switches.

Quote:
Originally Posted by rneag View Post
It's wrong and improper. Paint can continually get pushed into the receptable openings a create a fire hazard. The receptacles should be replaced, a little less concern with the switches as they only control flow, not provide it. Too inexpensive not to replace IMO.
Ross can you explain the process involved that they become a fire hazard?

I know you can find words from sites about it but on a real level you can gob most paint in and have no real problems other than a tough time pushing in the darn plug.
Sure I write it up but do not do anymore than suggest it be replaced.I leave the scary wordage out of it.
The idea is that paint can be flammable right?
OK but for any type of spark to occur what is the process and when or what conditions would it occur under.
Someone provide proof from a investigation that a fire ever occurred over this .
Reply With Quote
  #8  
Old 2/18/11, 6:09 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Painted over outlets and switches.

If paint keeps getting jammed into the slots and you keep using it the blades will get Loose, Loose connections heat up . Thus a fire hazard .JMO Other being a stupid idea . A good painter should be able to miss it.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #9  
Old 2/18/11, 2:33 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Painted over outlets and switches.

Paint on receptacles as a cause for replacement if the receptacle is still functioning and usable...

You guys are kidding, right?
Reply With Quote
  #10  
Old 2/18/11, 2:40 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Painted over outlets and switches.

Quote:
Originally Posted by jfarsetta View Post
Paint on receptacles as a cause for replacement if the receptacle is still functioning and usable...

You guys are kidding, right?
You have to wonder sometimes Joe.

If it tests OK and the paint is not blocking the holes I could care less.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 2/18/11, 3:17 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Painted over outlets and switches.

Quote:
Originally Posted by jfarsetta View Post
Paint on receptacles as a cause for replacement if the receptacle is still functioning and usable...

You guys are kidding, right?
That is why i said in the slots BTW



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #12  
Old 2/21/11, 12:04 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Painted over outlets and switches.

Most receptacles that I run across were jammed with paint and/or sprayed over... I will use the 3 bulb tester to push through and verify correct ground and polarity, but I do recommend replacement when they've done this.

The other "neat" thing I've been running into on these flipped homes is the "lack of quality" for receptacle and fixture replacement. The 3 bulb tester will say most of it's fine.. the suretest will show me that they've used neutrals for grounds on a 3 wire system.. the connections are terrible at best and so on.

So sure... a neat and clean paint job on receptacles and switches, fine. How many times does that happen? My experience is that I need a chisel (insulated of course) to break the paint seal prior to testing.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #13  
Old 2/21/11, 3:24 PM
Jered Chandley Jered Chandley is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Orlando, Fl
Posts: 18
Default Re: Painted over outlets and switches.

Depends on the severity, I would make mention of it to protect yourself if something ever happened to the buyer because of it.




Central Florida's Premier Home Inspection
Orlando Home Inspection Florida Home Inspection

Jered Chandley
Vice President
1-888-511-SCAN
info@safescantech.com





Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Old style electrical outlets / switches lfoster Electrical Inspections 7 1/13/08 1:43 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Some good questions that always need answers jtedesco1 Electrical Inspections 5 6/16/06 9:10 PM


All times are GMT -4. The time now is 9:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts