Does a 200 amp main panel ever have more than 100 amps in each leg of a balanced feed?
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/1/11, 7:17 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Panel board capacity

How about 105A on each leg which should not trip the main



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 11/1/11 at 10:09 PM..
Reply With Quote
  #3  
Old 11/1/11, 7:25 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Panel board capacity

Quote:
Originally Posted by Ron Waller View Post
Does a 200 amp main panel ever have more than 100 amps in each leg of a balanced feed?
Yes could have over 200 amps per leg for a short period .
Constant load I think 160 amps . been out of the trade too many years but I think it is 80% . I expect some one might add to this thanks .. Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.




Last edited by rcooke; 11/1/11 at 8:01 PM..
Reply With Quote
  #4  
Old 11/1/11, 7:36 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Panel board capacity

Robert your response does not even make sense!

How about 105A on each leg which main not trip the main



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #5  
Old 11/1/11, 7:46 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Panel board capacity

I am not an electrician but I remember 75% but I am not sure. I hope that someone can clarify this, it would be nice to know if it has changed.
Roy I think you meant to say over 100/leg.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 11/1/11, 7:51 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Panel board capacity

Quote:
Originally Posted by kwood View Post
I am not an electrician but I remember 75% but I am not sure. I hope that someone can clarify this, it would be nice to know if it has changed.
Roy I think you meant to say over 100/leg.
He said 200 amp panel and they are 200 Amps on each leg of a 200 amp panel


( " Panel board capacity
Does a 200 amp main panel ever have more than 100 amps in each leg of a balanced feed? ")



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 11/1/11, 8:13 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Panel board capacity

OK we went from 100/leg to 200/leg so your last comment says 160 constant load. So I need more clarification if you can Roy.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 11/1/11, 8:21 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Panel board capacity

Quote:
Originally Posted by kwood View Post
OK we went from 100/leg to 200/leg so your last comment says 160 constant load. So I need more clarification if you can Roy.
The question was (" Panel board capacity
Does a 200 amp main panel ever have more than 100 amps in each leg of a balanced feed? ")

And the answer a 200 amp panel is 200 amps on each leg the Constant load is 80% , I was wrong at 70% .
You can over load a breaker for a short period like motor starting so yes it can exceed 200 amps per leg but a breaker should eventually dump at over 80% of rated load .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #9  
Old 11/1/11, 8:50 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel board capacity

At 240 volts a 200 amp panel will have a capacity of 200 amps of load. At 120 volts the same panel will have a capacity of 400 amps. A full 200 amp, 240 volt load might take a long time to trip the 200 amp OCPD if at all. A continuous load is one that will continue for 3 hours or more at maximum ampacity. Continuously loaded circuits and feeders must be sized at 125% of the connected load.
Reply With Quote
  #10  
Old 11/1/11, 9:12 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Panel board capacity

Thanks Robert M and Roy. I think that has now been cleared up.
Sized at 125% for motors
80% over rated 200 Amps/leg and it will trip the main.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #11  
Old 11/1/11, 9:16 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel board capacity

Quote:
Originally Posted by kwood View Post

80% over rated 200 Amps/leg and it will trip the main.
Not sure what you mean by this? Are you saying >160 amps will trip the 200 amp OCPD?
Reply With Quote
  #12  
Old 11/1/11, 9:32 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Panel board capacity

I made no comment about 160 amps that is Roys.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #13  
Old 11/1/11, 10:52 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Panel board capacity

He asked if there can be more than 100A per leg, and the simple answer is yes. An example is 105A per leg. Each leg of a typical 200A 120/240V panel should have a 200A capacity.

Circuits and feeders should only be loaded to about 80% of the rating (wire sized for 125% of the load), but that load would likely never trip a breaker. Loads need to be in the range of about 100% to 130% of breaker rating to trip a breaker.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 11/3/11 at 4:32 PM..
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/2/11, 7:42 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Panel board capacity

Unless of course if you are dealing with Federal Pacific but that is a whole new topic. LOL



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #15  
Old 11/2/11, 8:38 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Panel board capacity

Quote:
Originally Posted by kwood View Post
Unless of course if you are dealing with Federal Pacific but that is a whole new topic. LOL
I see nothing wrong with the Canadian FP panels .

Do you have any evidence to show that I am wrong .

I do have a FP in my home and see these in many homes .

They are still being installed in Canada. Thanks ... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Panel board I have not seen before belliott Electrical Inspections 7 5/4/10 2:46 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
NH licensing prussell Legislation, Licensing & Legal Issues for Inspectors 12 5/21/08 4:40 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Need help with main panel board buss bar smcintire Electrical Inspections 63 1/8/08 5:55 PM


All times are GMT -4. The time now is 9:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts