Does a 200 amp main panel ever have more than 100 amps in each leg of a balanced feed?
|
| Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
How about 105A on each leg which should not trip the main
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 11/1/11 at 10:09 PM.. |
|
#3
|
||||
|
||||
|
Quote:
Constant load I think 160 amps . been out of the trade too many years but I think it is 80% . I expect some one might add to this thanks .. Roy Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. Last edited by rcooke; 11/1/11 at 8:01 PM.. |
|
#4
|
||||
|
||||
|
Robert your response does not even make sense!
How about 105A on each leg which main not trip the main THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#5
|
||||
|
||||
|
I am not an electrician but I remember 75% but I am not sure. I hope that someone can clarify this, it would be nice to know if it has changed.
Roy I think you meant to say over 100/leg. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#6
|
||||
|
||||
|
Quote:
( " Panel board capacity Does a 200 amp main panel ever have more than 100 amps in each leg of a balanced feed? ") Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#7
|
||||
|
||||
|
OK we went from 100/leg to 200/leg so your last comment says 160 constant load. So I need more clarification if you can Roy.
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#8
|
||||
|
||||
|
Quote:
Does a 200 amp main panel ever have more than 100 amps in each leg of a balanced feed? ") And the answer a 200 amp panel is 200 amps on each leg the Constant load is 80% , I was wrong at 70% . You can over load a breaker for a short period like motor starting so yes it can exceed 200 amps per leg but a breaker should eventually dump at over 80% of rated load . Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
At 240 volts a 200 amp panel will have a capacity of 200 amps of load. At 120 volts the same panel will have a capacity of 400 amps. A full 200 amp, 240 volt load might take a long time to trip the 200 amp OCPD if at all. A continuous load is one that will continue for 3 hours or more at maximum ampacity. Continuously loaded circuits and feeders must be sized at 125% of the connected load.
|
|
#10
|
||||
|
||||
|
Thanks Robert M and Roy. I think that has now been cleared up.
Sized at 125% for motors 80% over rated 200 Amps/leg and it will trip the main. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#11
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not sure what you mean by this? Are you saying >160 amps will trip the 200 amp OCPD?
|
|
#12
|
||||
|
||||
|
I made no comment about 160 amps that is Roys.
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#13
|
||||
|
||||
|
He asked if there can be more than 100A per leg, and the simple answer is yes. An example is 105A per leg. Each leg of a typical 200A 120/240V panel should have a 200A capacity.
Circuits and feeders should only be loaded to about 80% of the rating (wire sized for 125% of the load), but that load would likely never trip a breaker. Loads need to be in the range of about 100% to 130% of breaker rating to trip a breaker. Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 11/3/11 at 4:32 PM.. |
| Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Unless of course if you are dealing with Federal Pacific but that is a whole new topic. LOL
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#15
|
||||
|
||||
|
Quote:
Do you have any evidence to show that I am wrong . I do have a FP in my home and see these in many homes . They are still being installed in Canada. Thanks ... Roy Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Panel board I have not seen before | belliott | Electrical Inspections | 7 | 5/4/10 2:46 PM |
| Main panel...recommendation ? | dnasser | Electrical Inspections | 6 | 11/22/09 9:55 PM |
| NH licensing | prussell | Legislation, Licensing & Legal Issues for Inspectors | 12 | 5/21/08 4:40 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Need help with main panel board buss bar | smcintire | Electrical Inspections | 63 | 1/8/08 5:55 PM |