Default Panel board I have not seen before

The breakers (OK one) had a hole for insertion perhaps of a cartridge fuse ? (not sure)
The one listed as 20 had a pull out with two mini cartridge fuses listed at 20 amp each.
Someone please tell me about these.
They were in a Condo (so they are in a sub)
Not looking for fun issues ,just facts on the breakers.

These are QF type and installed in 1970

Thanks in advance.
[ATTACH][ATTACH][ATTACH]panel-board-have-not-seen-before-qf-closeup-1024x768-.jpg[/ATTACH][/ATTACH][/ATTACH]
Attached Thumbnails
panel-board-have-not-seen-before-panel-1024x768-.jpg   panel-board-have-not-seen-before-panel-label-1024x768-.jpg   panel-board-have-not-seen-before-label-closeup-1024x768-.jpg  

Last edited by belliott; 5/3/10 at 2:48 PM..
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/3/10, 11:03 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Panel board I have not seen before

Bump
Reply With Quote
  #3  
Old 5/3/10, 11:46 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Panel board I have not seen before

Paul are you out there?
Reply With Quote
  #4  
Old 5/4/10, 11:45 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Panel board I have not seen before

I just swapped out a panel that was an older QO style. It was more than 50 years old but still worked like a charm for a main panel. I would imagine it's the same concept as the one I did. Each breaker had two handles to it as well as two lugs. They fit on the buss just like any other breaker. Two separate branch circuits would then connect to the two screws/lugs on the breaker. If you look at the panel diagram/label, you'll see each one listed with an R. That is labeled for the Rear terminal. I don't see why the cartridge fuse pull-outs would be any different. Instead of the breaker having two throws on it, you have two fuses inserted into the pull-out.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #5  
Old 5/4/10, 12:03 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Panel board I have not seen before

Quote:
Originally Posted by jwicklander View Post
I just swapped out a panel that was an older QO style. It was more than 50 years old but still worked like a charm for a main panel. I would imagine it's the same concept as the one I did. Each breaker had two handles to it as well as two lugs. They fit on the buss just like any other breaker. Two separate branch circuits would then connect to the two screws/lugs on the breaker. If you look at the panel diagram/label, you'll see each one listed with an R. That is labeled for the Rear terminal. I don't see why the cartridge fuse pull-outs would be any different. Instead of the breaker having two throws on it, you have two fuses inserted into the pull-out.

Jeff
Thanks Jeff.
I still do not understand the empty space on the far left breaker in the middle of it .
Apparently for a cartridge.
Never saw anything like it before.

Strange days, as I just finished three in a row with Ceil Heat.
Reply With Quote
  #6  
Old 5/4/10, 2:02 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Panel board I have not seen before

Quote:
Originally Posted by belliott View Post
Thanks Jeff.
I still do not understand the empty space on the far left breaker in the middle of it .
Apparently for a cartridge.
Never saw anything like it before.

Strange days, as I just finished three in a row with Ceil Heat.

That's most likely where the second pull-out fuse is located. Apparently missing.
I gotta get out of the suburbs and go into the city for some of the more interesting things you are discovering. I'm lucky if I come across a true crawlspace with an entrance from the outside.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #7  
Old 5/4/10, 2:22 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Panel board I have not seen before

The labels clearly say Square-D. Is that what you are asking?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 5/4/10, 2:46 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Panel board I have not seen before

Looks like cartridge fuse panel to me... perhaps an intermediate between edison fuses and IDE panels made by Siemens at one time. The cartridge is missing as you have pointed out. An antiquated unit and difficult to find replacement components




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
OAHI Out Of Control - Bylaws Breached - Documented Proof rwand1 Canadian Inspectors 423 2/25/08 6:20 PM
Arizona Bill would take inspectors out from under BTR. gromicko Legislation, Licensing & Legal Issues for Inspectors 62 2/9/08 10:33 PM
100 amp Service w/new 200 amp panel mlong Electrical Inspections 10 2/7/08 2:08 AM