Default Panel bond

I know this has been discussed many times and I guess i am not paying attention.

I see more times that not that the green screw is not bonded to the panel.
Once in a while I will see a bonding strap.

Should I be calling out the panel not being bonded.
The purpose of the bond is to direct ant stray current that may energize the cover to ground instead of a person correct!! Am I understand that.

Thanks

Is any one going to the Cleveland electrical seminar. I am planning on attending.
Attached Thumbnails
panel-bond-83506-lorain-015-small-.jpg.jpg
Views:	124
Size:	57.0 KB
ID:	6172  
Reply With Quote
  #2  
Old 10/14/06, 2:57 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Panel bond

David,

That "GREEN" screw is the bond between the panel and the buss as it should be on that panel shown. Notice the "grounded" (ie: Neutral ) conductors and grounding conductor are terminated on the same buss bar which would lead us to believe this is a main distribution panel.

Now....just remember.......any panel from this point to some other location i the dwelling would have to have (4) wires....(2) non-grounded conductors and (1) Grounded Conductor and (1) Grounding Conductor.....and at the remote panel...the (1) Grounded and the (1) Grounding conductor should not be tied together on the same buss bar.....the grounded ( neutral ) must be floating and not in contact with the grounding bar or the panel enclosure itself.

Hope that explains it.......if you see this taking place by all means call it out and if you are attending my seminar in Cleveland...we will go into it in much more detail...you will understand with even more at that time.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 10/18/06, 10:25 AM
nwagner's Avatar
nwagner nwagner is offline
InterNACHI Member
 
Join Date: May 2006
Location: Baraboo, WI
Posts: 2,973
Default Re: Panel bond

I've seen two panels that bonded to the water main with the conductor fastened in one of the common neutral bus lugs instead of to main grounding terminal. One of them lacked the main terminal all together. Is there some logic behind that or is that just a handyman "not getting it"?
Reply With Quote
  #4  
Old 10/18/06, 10:53 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Panel bond

Grounding and bonding are not the same Nick.

That ground may be okay if the panel is properly bonded.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 10/18/06, 3:23 PM
nwagner's Avatar
nwagner nwagner is offline
InterNACHI Member
 
Join Date: May 2006
Location: Baraboo, WI
Posts: 2,973
Default Re: Panel bond

In this set up is the water main grounded to the panel or is the panel grounded to the water main?
Reply With Quote
  #6  
Old 10/18/06, 7:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Panel bond

Neither is grounded TO the other.

The water main may - or may not - be the grounding electrode. You didn't give us enough information to know for sure. Assuming that it IS the grounding electrode, the panel would be grounded at the water main.

For kicks, lets say the water "main" is plastic, the house is piped with copper or steel, but the pipes are in the attic and walls (therefore, they are not the grounding electrode).

In this case, the panel and the water main are "bonded" to eachother, by way of the conductor you spoke of. Assuming the neutral bus is properly bonded to the enclosure (also assuming this is the service panel), both the "water main" and the panel should be "bonded" to the grounding electrode, which "grounds" the electrical system. Got it?

Bonding is simply "joining" components to make them one. Think of bonding in terms of "epoxy" used to glue things together - attaching them to one another.

Grounding is simply providing a conductive path to ground/earth.

The metal piping and electrical system components are bonded (attached together) and grounded (provided with a path to ground/earth).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 10/19/06, 8:59 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Panel bond

Still amazes me of Mr. Popes knowledge and ability to convey it in layman terms....Could I expand on it...sure....could I define the ACTUAL purpose of the grounded conductor...versus just a path to ground...yep....BUT for the HI...why expand it.....no need as Jeff's examples are great and well explained to make even a rookie understand..( P.s. Not call anyone a rookie...just an example )

I say Mr. Pope has a GREAT understanding of it.....guess he wont attend any of my Seminars...lol....nothing to teach that fella....

Great Job Jeff.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 10/19/06, 11:23 AM
nwagner's Avatar
nwagner nwagner is offline
InterNACHI Member
 
Join Date: May 2006
Location: Baraboo, WI
Posts: 2,973
Default Re: Panel bond

Yeah I gotta hand it to you Jeff. My problem is that I use electrical terms loosely, back to the books for me! I meant bonding like you defined but I left out the term grounding.

Let me attempt to better state my question. The subjects are a main service panel and a copper water main directing to the soil. The water main has a grounding electrode conductor bonded around the water meter with jumper cables. This grounding electrode conductor is bonded to the service panel in one of the common neutral bus bar lugs (the ones designated for branch neutral and ground conductors) and not to one of the larger lugs on the end of the bus which typically bond grounding electrodes (such as the SEC neutral). Will current needing grounding from this neutral bus ground to the water main?
Reply With Quote
  #9  
Old 10/19/06, 11:45 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Panel bond

Quote:
Originally Posted by nwagner
This grounding electrode conductor is bonded to the service panel in one of the common neutral bus bar lugs. . .

Will current needing grounding from this neutral bus ground to the water main?
Based on your statement, I would think so. The neutral bus would still need to be bonded to the enclosure as you said this is the service panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 10/19/06, 11:47 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Panel bond

Quote:
Originally Posted by pabernathy
.....guess he wont attend any of my Seminars...lol....nothing to teach that fella....
Paul, I wouldn't miss it if it were brought out here. I'll be in the front row.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 10/19/06, 11:56 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,465
Default Re: Panel bond

I plan on attending Paul's seminar in Cleveland in December. I have not yet registered but plan on doing in the next week.

I need to better understand electricity as JP & PA have spoken about.

Thank you both for all the help you provide to the message board.

Would you advise that I purchase the NEC 2005 book as a reference guide?

Thanks

Dave
Reply With Quote
  #12  
Old 10/19/06, 12:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Panel bond

Quote:
Originally Posted by dmacy
Would you advise that I purchase the NEC 2005 book as a reference guide?
I think it's important to have access to the codes. I have spent thousands of dollars on current code cycles for my particular area, plus the National model codes from which they were extracted. However, these books do very little with regards to educating or teaching.

If you're looking to "learn" the "why's and why not's," you should first purchase the commentary books and the NEC Handbook. Along with the code sections, these books explain the purpose and interpretation for the particular code.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 10/19/06, 11:19 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Panel bond

David,

I will recommend some good books at the seminar.......While I think Everyone should own the 2002 and 2005 NEC handbook....in regards to HI's....WHY.....not because of a HI having anything to do with CODE issues.....just think they are great references to help you understand and it explains many things very well.

As to Mr. Pope.......I am a FAN of yours fella.....you do some great posts...I would LOVE to have you in the FRONT ROW.......

I will be out your way next week.....in Seattle,WA and then in Sacramento,CA.....man I hate to fly.......;(

jeff.......again you have a GREAT grasp......and MUCH to give...keep up the GREAT work...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 10/19/06 at 11:22 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Does Anyone See A Panel Bond Here? pdickerson Electrical 14 10/24/07 12:40 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 5:24 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts