I can't see clearly enough to tell. As you know the bonding is normally done with a bond screw or strap between the neutral bar and the enclosure.
|
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Gary it's hard to tell from the photo what exactly we're looking at. Are you saying that the grounded conductor (neutral) is connected directly to the panel enclosure?
|
|
#4
|
||||
|
||||
|
Robert
Yes "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
If it's only connected to the enclosure then you might have a problem with section 200.2 from the 2008 NEC:
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Robert, I believe that section means that the enclosure cannot be used as a jumper between grounded conductors, ie so no current would be flowing on the enclosure.
|
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
|||
|
|||
|
Lets not forget that in that type of connection you would have to provide additional points of termination for other grounded conductors so it brings in not only the concern that is already posted...but does not afford additional terminal points for the additional grounded conductors in the entire system.
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Another bonding of service panel question? | mthiltgen | Electrical Inspections | 9 | 3/4/10 6:41 PM |
| Neutral bus bar failed inspection | Greg Moritz | Electrical Inspections | 18 | 1/19/08 1:53 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |