The SEC main ground is connected directly to the panel, would this meet the bonding requirement?
panel-bonding-copy-p3270099.jpg



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
Need a home inspection in Colorado? Check out InterNACHI's listing of Colorado certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/28/10, 8:51 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel bonding?

I can't see clearly enough to tell. As you know the bonding is normally done with a bond screw or strap between the neutral bar and the enclosure.
Reply With Quote
  #3  
Old 3/28/10, 8:52 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel bonding?

Gary it's hard to tell from the photo what exactly we're looking at. Are you saying that the grounded conductor (neutral) is connected directly to the panel enclosure?
Reply With Quote
  #4  
Old 3/28/10, 8:57 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Panel bonding?

Robert
Yes



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #5  
Old 3/28/10, 9:01 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel bonding?

If it's only connected to the enclosure then you might have a problem with section 200.2 from the 2008 NEC:

Quote:
200.2 General.
All premises wiring systems, other than circuits and systems exempted or prohibited by 210.10, 215.7, 250.21, 250.22, 250.162, 503.155, 517.63, 668.11, 668.21, and 690.41, Exception, shall have a grounded conductor that is identified in accordance with 200.6. The grounded conductor shall comply with 200.2(A) and (B).
(A) Insulation. The grounded conductor, where insulated, shall have insulation that is (1) suitable, other than color, for any ungrounded conductor of the same circuit on circuits of less than 1000 volts or impedance grounded neutral systems of 1 kV and over, or (2) rated not less than 600 volts for solidly grounded neutral systems of 1 kV and over as described in 250.184(A).
(B) Continuity. The continuity of a grounded conductor shall not depend on a connection to a metallic enclosure, raceway, or cable armor.
Reply With Quote
  #6  
Old 3/28/10, 9:18 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel bonding?

Robert, I believe that section means that the enclosure cannot be used as a jumper between grounded conductors, ie so no current would be flowing on the enclosure.
Reply With Quote
  #7  
Old 3/28/10, 10:17 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel bonding?

Quote:
Originally Posted by Jim Port View Post
Robert, I believe that section means that the enclosure cannot be used as a jumper between grounded conductors, ie so no current would be flowing on the enclosure.
Yes you're correct, that why I said the only connection. If the neutral is only connected to the enclosure and the nuetral bus is bonded to the enclosure then the neutral current will flow on the enclosure. But I'm having a hard time deciphering the photo so based on the photo and what Gary posted I'm only guessing.
Reply With Quote
  #8  
Old 3/28/10, 12:16 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel bonding?

Lets not forget that in that type of connection you would have to provide additional points of termination for other grounded conductors so it brings in not only the concern that is already posted...but does not afford additional terminal points for the additional grounded conductors in the entire system.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Another bonding of service panel question? mthiltgen Electrical Inspections 9 3/4/10 6:41 PM
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts